    Hi All

    I have just purchased a new 2.5 hp single phase electric motor to put on my dust extraction fan only to realise that it is running in the wrong direction.

    I have swapped the wires running from the capacitor into the motor and this changes the direction of rotation but the motor does not spin as fast.

    will i stuff the motor if i run it reversed ? or have i swapped the wrong wires around?

    Any help would be greatly welcomed as the closest electritian is 2 hours drive away

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Apr 2004
    Location
    United States
    Posts
    317

    Default

    There should be a schematic where you connect your wires that show how to reverse the rotation of the motor. If there isn't one then you probably cannot change the motor's rotation.

    Paul

  4. #3
    Join Date
    Nov 2000
    Location
    Cle Elum, Washington, USA
    Posts
    117

    Default reverse

    If the motor doesn't reverse by rewiring you can turn it around 180 degrees and mount it the other direction. You may need to build a new bracket, but that is generally pretty simple. Good luck.
    "Always cutting corners...!"

  5. #4
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    I am no electrician, but the only motor I thought you could change the direction of rotation on was a DC motor.
    CHRIS

  6. #5
    Join Date
    Jan 2007
    Location
    Adelaide
    Posts
    2,794

    Default

    Wattie, I might talk rubbish, so take it with a lot of salt. I grew up with electric motors (dad's factory) but what I knew is mostly forgotten.
    My advice is to restore the original connection to the capacitor immediately while you find out how to change the motor's wiring if it's possible. Piece of cake with 3phase, can't remember how to do it in 1phase. If the motor is still running slower after you have changed back, you need to check that one section of the motor's wiring is not a) burnt already or b) disconnected, for example because overheating has melted a weak soldered connection. If this is the case, further use will just result in complete burning, while you might be able to save the motor if it is case b).

    If all returns to normal, the reason of the slowing is that you messed up the earth connection and the motor was running at reduced voltage. No immediate damage done, but don't risk blowing everything up next time.

    Cheers
    Frank

  7. #6
    Join Date
    Apr 2005
    Location
    South Australia
    Age
    81
    Posts
    131

    Default

    I would suggest a 2 hour drive to get it done by an electrician makes far more sense than a similar ride in an ambulance or heaven forbid a hearse. Jon.
    Quote Originally Posted by Wattie View Post
    Hi All

    I have just purchased a new 2.5 hp single phase electric motor to put on my dust extraction fan only to realise that it is running in the wrong direction.

    I have swapped the wires running from the capacitor into the motor and this changes the direction of rotation but the motor does not spin as fast.

    will i stuff the motor if i run it reversed ? or have i swapped the wrong wires around?

    Any help would be greatly welcomed as the closest electritian is 2 hours drive away
    Jon.

  8. #7
    Join Date
    Jun 1999
    Location
    Westleigh, Sydney
    Age
    77
    Posts
    9,550

    Default

    Little boy,
    Electric wires.
    Blue flashes,
    Boy's ashes.
    Visit my website
    Website
    Facebook

  9. #8
    Join Date
    Mar 2007
    Location
    Central NSW
    Posts
    4

    Default

    thanks for your input every one, I think the safest and probably best solution will be to build a new mount for the motor and forget about rewiring it. Will get to it through the week.

    Another question about the motor though, what revs should the fan run at? the motor runs at 2800 rpm
    current set up is 3 1/2 inch pully on motor and 1 1/2 inch pully on fan.

    by my calculation the fan should run at approx 6500 rpm with that setup. would that be fast enough?

    By way of explanation the fan is one i picked up second hand and used to have a 3 phase motor on it. I only have single phase

    The motor was missing though (thats why i dont know what speed the fan should run at)

    The fan is 12 inch diameter with 6 inch out let and inlet

    I just happened to have a 3 1/2 inch pully in the shed thats why i am using it.

    The fan came with the 1 1/2 pully already on it. The belt guard looks like it was made to accomodate a fairly large pully on the motor maybe up to 8 inch.

    Any ideas?

  10. #9
    Join Date
    Nov 2004
    Location
    Port Pirie SA
    Age
    52
    Posts
    6,908

    Default

    Most spin at 2850rpm, the old motor may have been a slow speed one.
    ....................................................................

  11. #10
    Join Date
    Dec 2005
    Location
    South Australia
    Posts
    4,475

    Default

    Take note Some motors are reversable some are not ALL CAPACITORS ARE NON REVERSABLE put back how it was or the capacitor may explode

  12. #11
    Join Date
    Jul 2004
    Location
    Singleton NSW
    Age
    69
    Posts
    355

    Default

    Wattie,

    There are several types of motors using capacitors.
    1. Capacitor start / Induction run
    2. Capacitor start/ Capacitor run a
    3. Capacitor Start/Run

    The difference between 1 and 2 as opposed to 3 is that 3 does not have a centrifugal switch to switch out the start winding. This gives smoother torque in the motor.

    All have 2 windings a start and a run winding. Reversing the ends of either the start or run windings will reverse a single phase motor.

    As for speed, the speed of a motor is determined by 120 * frequency / number of poles.
    So for a 2 pole machine ( which is the fastest, as a motor dont work with one pole) is 3000rpm (synchronous speed). For a motor to develop torque there must be a difference between synchronous speed and actual speed.

    Most 2 pole motors run at 2800 to 2850 rpm. The difference is called 'slip'

    What was the HP of the motor that came off? If it is the same as your single phase motor you will require the same size pulleys or risk running out of horsepower.

    woodcutta

  13. #12
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    What sort of fan is it? Photo?
    CHRIS

  14. #13
    Join Date
    Mar 2007
    Location
    Central NSW
    Posts
    4

    Default

    Not sure who made the fan. I was told the original 3 phase motor was probably 3 hp.

    will post some photos as soon as i work out how

  15. #14
    Join Date
    Jan 2007
    Location
    Adelaide
    Posts
    2,794

    Default

    Quote Originally Posted by woodcutta View Post

    What was the HP of the motor that came off? If it is the same as your single phase motor you will require the same size pulleys or risk running out of horsepower.
    Provided that the motor's speed is also the same. It is quite likely that the old motor was 4 pole => 1400 rpm for better torque, as you said yourself. The pulleys' ratio in this case would have been double to achieve the same fan speed.

Similar Threads

  1. gender view of oil change
    By John Saxton in forum WOODIES JOKES
    Replies: 1
    Last Post: 13th February 2007, 01:36 PM
  2. Why can you reverse the direction of rotation of metal lathes?
    By Billy Bignutz in forum METALWORK FORUM
    Replies: 25
    Last Post: 25th November 2006, 09:05 AM
  3. Bushing a elec motor shaft.
    By Harry72 in forum METALWORK FORUM
    Replies: 11
    Last Post: 23rd October 2005, 11:41 PM
  4. Cyclone blower motor advice
    By Moo73 in forum DUST EXTRACTION
    Replies: 12
    Last Post: 19th August 2005, 07:13 PM
  5. Oil change
    By Iain in forum WOODIES JOKES
    Replies: 1
    Last Post: 1st November 2001, 06:56 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •