    Default Huanyang VFD 220v 2.2KW ? getting 190 v output

    Hi all,
    This is my 1st post. I have a Bridgeport mill, 220v 3 phase and using a Huanyang 2.2KW VFD. I got it to work my mill ok with a pot. But I cant get the motor to turn 1730 rpm. the fastest I get is 1530rpm?
    The other thing I want to run my 3 phase lathe 3hp. But only measure 190 volts at the lathe input. The contactor will not stay engaged, like too low of voltage. Any ideas on parameter change to increase my voltage and rpm on the mill?
    My parameters :
    PD000-0
    PD001-0
    PD002-1
    PD003-90
    PD004-90
    PD005-90
    PD006-2.5
    PD007-.5
    PD008-220V
    PD009-13.0 A
    PD010-6.5
    PD011-12
    PD012-NULL
    PD013-0
    PD014-3
    PD015-3
    PD016-20
    PD017-20
    PD041-08
    PD-042-5
    PD043-5
    PD044-2
    PD070-4
    PD071-20
    PD072-90
    PD142-11
    PD143-04
    PD144-1730 RPM

    Thanks for any help.

    Dave

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    When you say contractor - do you have switching gear between the VFD and the motor? If so any of contactor / switches should be removed and you should be using the VFD or remote switches connected to the VFD to control the motor.
    Failure to do this may damage the VFD.

  4. #3
    Join Date
    May 2016
    Location
    pittsburgh Pa. USA.
    Age
    73
    Posts
    4

    Default

    The contactor is part of the machine, Pulls in when you hit the start button on the machine. The motor runs continuous, until you move the lever on the carriage. Are you saying to bypass the contactor and go direct to the motor?

  5. #4
    Join Date
    Feb 2003
    Location
    back in Alberta for a while
    Age
    68
    Posts
    12,006

    Default

    Is "ago" describing a star--delta switching device?
    regards from Alberta, Canada

    ian

  6. #5
    Join Date
    May 2016
    Location
    pittsburgh Pa. USA.
    Age
    73
    Posts
    4

    Default

    Dont know what you mean by star-delta switching device. The lathe is a Graziano Sag 12. has 3 hp motor and oil pump motor also. Im staring to believe this Huanyang VFD will not work with this Lathe. The lathe motor runs continuous and has Electro mechanical clutches to change speeds and reverse. and a safety switch on the electric oil pump. If the pump doesn't run the motor won't start. I believe this lathe is too complicated for this Chinease VFD. I might have to use a conventional phase convertor.

  7. #6
    Join Date
    Feb 2003
    Location
    back in Alberta for a while
    Age
    68
    Posts
    12,006

    Default

    Hi Dave

    Many 3 Phase motors have a three position switch OFF - START - RUN
    the star-delta is the switch wiring behind the START - RUN positions.
    the star configuration is used to reduce the amps drawn by the motor when starting with the delta position being used to once the motor is close to operating speed. In a typical 3 phase motor, the starting amps under the star wiring connection are about 30% of what the starting amps would be if you tried to start the motor in delta.


    If I've understood the data in your question, you're attempting to run a 3 Hp motor (=2.24kW) plus the oil pump, with a 2.2KW VFD.
    That might be your problem right there.
    Hopefully someone familiar with VFD's will chime in, but my understanding is that the power rating of a VFD should be around 25% higher than that of the motor it's connected to.
    regards from Alberta, Canada

    ian

  8. #7
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by ago View Post
    Dont know what you mean by star-delta switching device. The lathe is a Graziano Sag 12. has 3 hp motor and oil pump motor also. Im staring to believe this Huanyang VFD will not work with this Lathe. The lathe motor runs continuous and has Electro mechanical clutches to change speeds and reverse. and a safety switch on the electric oil pump. If the pump doesn't run the motor won't start. I believe this lathe is too complicated for this Chinease VFD. I might have to use a conventional phase convertor.
    There absolutely be any Motor start and stop switches in between the VFD and the motor.

    It is possible to have a switch that switches the VFD output between two or more motors.
    PROVIDED
    The motors MUST have their power switched on/off first BY THE VFD before switching.
    I have this setup on a pair of 3Ph grinders.

    More than one motor can be simultaneously driven by one VFD provided the motors are connected in Parallel to the VFD.
    I have this on my WW Bandsaw where one motor drives the band and a smaller motor drives the fan motor at double the speed of the band motor.

    I think using a VFD on a Graziano has been discussed over in the Metal workers forum Metal Work Forums
    I think the solution was a Phase converter.

  9. #8
    Join Date
    May 2016
    Location
    pittsburgh Pa. USA.
    Age
    73
    Posts
    4

    Default

    I think I will use a rotary phase convertor

  10. #9
    Join Date
    May 2016
    Location
    Gosford
    Posts
    11

    Default

    Dave, hope this is not a dumb thought, but is the motor set-up for 50hz in lieu of the 60Hz? I think this motor is sold in countries (such as UK and Australia) that operate on 50Hz. This may may explain the difference in maximum rpm. Regards, Tim

  11. #10
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,774

    Default

    Disable the pot and use the key pad speed control. Reset PD02 = 0
    Do you have a manual for the VFD?
    PD03, PD04 and PD072 should be reset to 60.
    To use the pot PD070 should be set to 0 not 4. This may be causing the problem but I don't know what type the pot is. For a Huanyang it should be a 10k ohm linear pot.
    All this is assuming that you have the same VFD model as my manual.
    Ignore the voltage readings you get from the VFD output terminals. Multimeters are set up to read sign wave RMS values. What the VFD is sending out will probably read differently to a standard power outlet and the VFD also varies the voltage at the output depending on the operating mode and the applied load.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

Similar Threads

  1. Where to buy 220v momentary foot switch?
    By Woodwould in forum HAND TOOLS - POWERED
    Replies: 17
    Last Post: 14th March 2013, 09:14 PM
  2. Replies: 14
    Last Post: 4th May 2012, 08:48 AM
  3. 220v / 240v Help??
    By John0 in forum GENERAL & SMALL MACHINERY
    Replies: 4
    Last Post: 9th September 2008, 08:32 AM
  4. 220v remote switch for 3hp Dusties
    By Groggy in forum ANNOUNCEMENTS
    Replies: 19
    Last Post: 15th November 2007, 03:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •