Thread: New Sawstop PCS tripping breaker
-
12th August 2018, 04:58 PM #1Intermediate Member
- Join Date
- Jun 2017
- Location
- New Zealand
- Age
- 52
- Posts
- 46
New Sawstop PCS tripping breaker
So had it a few weeks. Not really used it until today other than checking alignment etc. On the odd startup it will trip the breaker. Did it once this morning. Not at all this afternoon - maybe 12 to 15 starts. Then 3 out of 9 starts early this evening.
Seems to be working fine when running. Normal NZ Voltage - 230/240V Single Phase. On its own dedicated circuit with a 16A breaker. Prior to chasing down the supplier I'm thinking this is to do with the initial inrush of current at startup.
All lights are doing what they should. Solid Green light after it's gone through initialization etc.
I noted when I purchased my Hammer A31 Jointer / Planer they told me to install a D curve breaker for startup but the Sawstop is on a new Hagar 16A C Breaker and is an RCBO - so it provides overcurrent as well as earth leakage. Guessing one of them is happening !
Any ideas ? Do I need a D curve on this circuit as well ? Will also speak to the sparky who installed it.
Thanks for the thoughts
GedLast edited by Gedc; 12th August 2018 at 05:19 PM. Reason: Tidied up some info
-
12th August 2018 04:58 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Age
- 2010
- Posts
- Many
-
12th August 2018, 06:12 PM #2
Talk to your sparky.
It might be more a current leakage than over current. It might even be due to moisture in the air and motor/wiring.
-
12th August 2018, 11:39 PM #3
We've seen this in these forums before.
From memory, you need a type "D" circuit breaker when this is happening, and again from memory, these usually aren't fitted by default because most sparkies don't know you're about to use this type of kit with a certain peak load at startup that is enough to trip a normal breaker.
Let me see if I can find the thread...
EDIT: Found, as I'd bookmarked it when I read it in case mine produced the same issue: SAWSTOP PCS Circuit requirements for installation, what are they?
EDIT 2: My memory served correctly, it's a D Type circuit breaker you need (post 3 in the linked thread).
-
13th August 2018, 05:58 AM #4Intermediate Member
- Join Date
- Jun 2017
- Location
- New Zealand
- Age
- 52
- Posts
- 46
Hi Midnight Man. Thankyou for that. I did search but couldn't find anything like that. I will chat to the sparky and see about changing it for the D curve breaker. Funny enough we did chat about it at the time but given there wasn't anything specific from the supplier ( i checked) and in the documentation we thought the C typo would suffice. Just goes to show. Will get him to check for any other issues re earth leakage but fingers crossed another $100 will sort the issue.
-
21st September 2018, 02:54 PM #5Senior Member
- Join Date
- Feb 2018
- Location
- Ipswich
- Posts
- 103
Hi all,
I've recently moved into a rental house and I'm having a similar problem but it's the 40 amp safety switch that is tripping. I'ts intermittent, happening 2 or 3 times a day when I have a full day in the shop. It has only tripped the 20 amp breaker once and the safety switch went at the same time. Is this most likely a faulty safety switch or will I have to spring for the sparky to fit an upgraded fitting?
Thanks for any and all advice
Craig
-
21st September 2018, 03:44 PM #6.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,787
-
21st September 2018, 05:55 PM #7wood butcher
- Join Date
- Dec 2008
- Location
- East Bentleigh
- Posts
- 200
I've got a sawstop and it's not the breaker size I'm my case but the voltage drop. The mains coming in is a bit thin and the workshop is up the other end of the block. The d-curve may help but sometimes lower voltage for startup and the electronics on the saw upset the rcd. I had to go to an industrial sized one 100mA instead of the 30mA.
On the question of the sawstop that you didn't ask, it saved my pinky last week when using the finger joint 2 blade set. $300 for a new stack and brake but just a scratch on the pinky.
Cheers Bryan
Sent from my SM-G955F using Tapatalk
-
21st September 2018, 06:28 PM #8
-
21st September 2018, 07:01 PM #9Senior Member
- Join Date
- Feb 2018
- Location
- Ipswich
- Posts
- 103
BobL it's always the sawstop. I have a 1.75 hp contractors saw. Never had a problem at my last place, would just occasionally trip the power board.
-
21st September 2018, 07:20 PM #10.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,787
Similar Threads
-
Table Saw keeps tripping the breaker
By basil55 in forum TABLE SAWS & COMBINATIONSReplies: 50Last Post: 2nd May 2018, 11:24 PM -
3HP 1P motor tripping RCD tripping
By BobL in forum ELECTRONICSReplies: 5Last Post: 20th January 2015, 08:33 PM -
MJ2325B table saw tripping circuit breaker
By munruben in forum GENERAL & SMALL MACHINERYReplies: 8Last Post: 3rd September 2012, 12:35 AM -
My New Table Saw is tripping circut breaker
By Arry in forum WOODWORK - GENERALReplies: 15Last Post: 7th July 2011, 09:53 PM -
Table Saw tripping circuit breaker
By Sam in forum TABLE SAWS & COMBINATIONSReplies: 19Last Post: 22nd October 2010, 07:48 AM