    If it happens again the the first thing you should do is check the "insulation resistance". I always check just after the breaker. If there is a problem then you know its either the cable or motor. Then you disconnect the motor to determine if its the motor or cable. If this is an overload protected RCD then it may trip on either over current or leakage current.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #47
    Join Date
    Aug 2010
    Location
    ACT
    Age
    84
    Posts
    2,579

    Default

    Hi,
    RCDs are set at 30 Milli amps in 20 Milli seconds, any more than that may not be life saving. 10ma are available for use in operating rooms and higher ones up to 1 amp and longer delay for farther up the line to protect the installation and not trip the mains when a sub circuit has a trip.
    FYI
    Regards
    Hugh

    Enough is enough, more than enough is too much.

  4. #48
    Join Date
    Jan 2014
    Location
    Sydney Upper North Shore
    Posts
    4,464

    Default

    The question still remains as to why it is tripping -earth leakage or overcurrent?. See NCArchers previous relevant post re switch position if the breaker handles both.
    Re checking insulation resistance - not everyone has an insulation resistance tester/megaohmmeter available and it should be done by someone in the know as the test conditions and result interpretation are critical.

    As the equipment in question is new, I personally would be getting someone qualified in to check to see if the problem is the circuitry, current limit of breaker etc or the machine.

    JMHO

  5. #49
    Join Date
    Feb 2016
    Location
    Perth WA Australia
    Posts
    828

    Default

    Heres my two cents...

    If everything is fine in your meter box I wouldn't rule out your equipment being the cause. If its happening even irregularly I'd get it checked out even if its for your own sanity. It may not be a big deal but when you're mighty frustrated with a project the last thing you want is a electrical problem to distract you to what is already a dangerous activity.

    I had a table saw once that would trip the circuit breaker every now and then couldn't figure out why but noticed that it'll only do it when nothing else was drawing power, so my solution was to turn on everything in the shed before turning on the saw eg dust collector, lights etc. Got rid of the table saw and nothing has tripped since then. So as Lappa says if its a new saw I'd get it looked at, as electrical issues are one of those things that don't generally resolve themselves.

  6. #50
    Join Date
    Jan 2016
    Location
    Townsville
    Age
    43
    Posts
    22

    Default

    Hi All

    A little bit of an update.

    So after having the saw for a while this is the story so far.

    After the initial tripping of the breaker and it ‘going away’ well the issue came back. (No real surprise)

    It wasn’t all the time sometimes start first shot, sometimes throw the breaker a few times before it would go.
    After not getting much of a chance to get any real shed time for the early part of the year, I have been recently.
    And after sort of just putting up with it I finally got an electrician out to check it out. He tested the breaker and it was ok. Checked the motor and it was ok. A bit of head scratching and a call to his boss he had a couple of suggestions. One is to put in a different breaker that he called a ‘motor rated ‘ breaker. And the other is to put in another circuit with heavier cable and a bigger breaker. (Existing wire is 2.5). He is going to get a bit of advice and get back to me.

    Any feed back and suggestions welcome.

    Thank you

    Baz

  7. #51
    Join Date
    Jan 2014
    Location
    Sydney Upper North Shore
    Posts
    4,464

    Default

    Link to info on different breaker ratings.

    https://thegrid.rexel.com/en-us/prod...-breakers/6030

Page 4 of 4 FirstFirst 1234

Similar Threads

  1. 3HP 1P motor tripping RCD tripping
    By BobL in forum ELECTRONICS
    Replies: 5
    Last Post: 20th January 2015, 08:33 PM
  2. MJ2325B table saw tripping circuit breaker
    By munruben in forum GENERAL & SMALL MACHINERY
    Replies: 8
    Last Post: 3rd September 2012, 12:35 AM
  3. My New Table Saw is tripping circut breaker
    By Arry in forum WOODWORK - GENERAL
    Replies: 15
    Last Post: 7th July 2011, 09:53 PM
  4. Table Saw tripping circuit breaker
    By Sam in forum TABLE SAWS & COMBINATIONS
    Replies: 19
    Last Post: 22nd October 2010, 07:48 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •