    Default Table Saw keeps tripping the breaker

    Hello just wondering if anyone has any ideas why my table saw keeps tripping the breaker.

    It is a new Harvey HE110LGE-30. It has a 15amp plug and is plugged into a 15amp power point. The breaker is 20amp (should it be more?). It is the only thing plugged in to that circuit.

    It trips soon as I start it. The saw blade moves a little bit.

    I have only had the saw for a couple of weeks and finally got round to trying it out.

    The wiring in the shed is only 12 months old and I did tell the electrician what I was planning to run in there.


    Thank you in advance.

    Baz

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    That sounds like a short somewhere.

    If it's a "too high a starting current" issue remove the belt and see if it starts.

    Also are you sure that that there nothing else running on the same circuit?
    Ideally 15A GPOs should be on its own circuit i.e. no other GPOS on that circuit.

  4. #3
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    I would immediately get in touch with the supplier re warranty claim for a faulty motor.

  5. #4
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    I presume that you have properly unpacked the saw and ensured that the blade turns freely by hand?

  6. #5
    Join Date
    Aug 2013
    Location
    Montmorency Victoria
    Posts
    554

    Default

    Hi Baz.

    You have a SERIOUS electrical problem .... there is a short somewhere .... maybe the saw motor.... maybe in the saw wiring ... or the building wiring.

    You could test the 15amp circuit on a known piece of equipment ... if it works OK then it is the saw ...

    You did remove the red bracket ... ?

    Regards

    Rob

  7. #6
    Join Date
    Jan 2016
    Location
    Townsville
    Age
    43
    Posts
    22

    Default

    I presume that you have properly unpacked the saw and ensured that the blade turns freely by hand?
    Yep moves freely. Saw setup correctly.

    I will try starting with out belt tomorrow arvo and see what happens.

    Thanks for the suggestion Bob and David

  8. #7
    Join Date
    Jan 2016
    Location
    Townsville
    Age
    43
    Posts
    22

    Default

    Yep red bracket removed.

    I tried the circuit with the DC7 Dusty and no issues.

    Hope I can get sorted it by the xmas break.

  9. #8
    Join Date
    Mar 2013
    Location
    Jervis Bay South Coast NSW
    Posts
    354

    Default

    Hi I had a saw that would throw the breaker, had everything tested on the saw and circuit no issues. Electrician suggested replacing the breaker with a new one and theproblem went away. It would work fine with the band saw and dust collector etc but the saw would trip it.

    Sent from my SM-T530 using Tapatalk

  10. #9
    Join Date
    Apr 2014
    Location
    Little River
    Age
    78
    Posts
    1,205

    Default

    The cause of the tripping is the fact that on start up the saw draws way more than its rated current. To accommodate this the breaker is designed to pass this current for a short time. How much extra current and for how long varies with the breaker's design curve. If you have a breaker that is designed for normal domestic use it will not handle a large excessive current. To find out how much current your breaker is designed to handle you need to know what its design curve is.

    An example of the various curve ratings for Schneider breakers is

    "Applies to the ac rated C60 Multi-9 devices
    B curve: 3.2 - 4.8 times amp rating for UL489 and UL1077 (3 - 5 times amp rating for IEC)
    C curve: 7 - 10 times amp rating
    D curve: 10 - 14 times amp rating
    K curve: 10 - 14 times amp rating
    Z curve: 2.4 to 3.6 times amp rating"

    You can fix your problem by having the sparky replace the breaker with one that has a more appropriate curve.

  11. #10
    Join Date
    Jan 2016
    Location
    Townsville
    Age
    43
    Posts
    22

    Default

    The breaker is a Hager ADC320T C20.

    I really hope it is as simple as a different breaker.

    If it is a warranty issue hopefully it is straight forward process.


    I have a 12" Woodman combo thicknesser due to arrive before xmas too and am looking forward to getting a project or two underway.


    Thank you for your replies.

  12. #11
    Join Date
    Apr 2014
    Location
    Little River
    Age
    78
    Posts
    1,205

    Default

    Quote Originally Posted by basil55 View Post
    The breaker is a Hager ADC320T C20.
    That is a C curve breaker. It looks like a D curve might solve your problem.

  13. #12
    Join Date
    Jul 2015
    Location
    Hunter Valley
    Age
    56
    Posts
    1,342

    Default

    Quote Originally Posted by code4pay View Post
    Hi I had a saw that would throw the breaker, had everything tested on the saw and circuit no issues. Electrician suggested replacing the breaker with a new one and theproblem went away. It would work fine with the band saw and dust collector etc but the saw would trip it.
    Similarly, we had a situation in a new house we moved into - one of the power circuits in the house would trip once in a while for no discernible reason every few days. Sparky changed the breaker over, and it has never happened since - there was absolutely no change in any electrical item or habit in usage between the times.

    Hopeing it turns out to be this simple!

  14. #13
    Join Date
    Jan 2016
    Location
    Townsville
    Age
    43
    Posts
    22

    Default

    Update.

    I have just spoken to the bloke form the shop I brought
    it from and he said this is a fairly common thing.
    He said the circuit breakers are very sensitive and something about
    earth leakage in the bigger electrical motors.
    It could be a very small amount of moisture in the motor ( quiet humid at the moment)
    I did get a little lost with the explanation.

    So aside from that I have organised my electrician to check it out. Hopefully this arvo
    or if he can’t get here today it will be Monday.

    Machine supplier suggested bypassing the breaker
    and seeing if it starts. I’m not sure about that one.

    If sparky not here until Monday I will take belt off to see if that allows it to start up.
    Other than that I will just have to wait and see for now.

    Thanks

    Baz

  15. #14
    Join Date
    Dec 2014
    Location
    Willunga, Australia
    Posts
    735

    Default

    If it trips the RCD then it is earth leakage. If it is the breaker then it is the over current. (There are RCD breaker combos which does not help but these are rare).

    Most likely over current as Bohdan said, the electrician can sort it out pretty easily

  16. #15
    Join Date
    Feb 2016
    Location
    Canberra
    Posts
    5,125

    Default

    Didnt know about curves on breakers. Good to know.

    Shame the breakers don't have a small display to show a small diagnostic code.

Page 1 of 4 1234 LastLast

Similar Threads

  1. 3HP 1P motor tripping RCD tripping
    By BobL in forum ELECTRONICS
    Replies: 5
    Last Post: 20th January 2015, 08:33 PM
  2. MJ2325B table saw tripping circuit breaker
    By munruben in forum GENERAL & SMALL MACHINERY
    Replies: 8
    Last Post: 3rd September 2012, 12:35 AM
  3. My New Table Saw is tripping circut breaker
    By Arry in forum WOODWORK - GENERAL
    Replies: 15
    Last Post: 7th July 2011, 09:53 PM
  4. Table Saw tripping circuit breaker
    By Sam in forum TABLE SAWS & COMBINATIONS
    Replies: 19
    Last Post: 22nd October 2010, 07:48 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •