    Default Table Saw tripping circuit breaker

    I bought an old MBT combination table saw and buzzer from another forum member last week. All went well, usual great people you meet from the forum !!!

    Finally got a chance to fire it up yesterday and after it runs for about 5 seconds one of the circuit breakers in the meterbox trips. Assuming the saw is electrically ok, does this mean I need to have a new circuit breaker installed just for the saw/garage similar to a separate air conditioner one ? I didnt have anything else running off the same power point at the time and throughout the house only the fridge and TV would have been going. My house is 3 years old and dont plan on buying any other stationary machinery in the future.

    While I sort the problem out is there any risk plugging the saw into the air conditioner power point and running an extension lead into the garage ? I intend to have a newer style on/off switch installed too, any recommendations for which one and also where to get it wired up in Northern Melbourne ?

    The saw motor info is as follows;
    G & C brand AC capacitor start
    Single Phase: 50 cycless
    HP: 1
    Rating: Conts
    Volts: 220/250
    Amps: 8
    RPM:1440
    Capacitor Unit MFD 110

    Also does anyone else out there have an MBT combination woodworker ? The only internet references I've found are a website where a bloke restored one in 2000 and a one line mention in a 1954 newspaper.

    Cheers,

    Sam

    PS - I'm electrically challenged so if I'm using the wrong terminology forgive me !

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    Changing the breaker is not the answer.

    Is it the RCD breaker that is tripping?

    If yes, then the saw is leaking (electrically speaking) which is lucky you have a new house with an RCD breaker otherwise you might not have made your post.

    Either way I'd be getting the saw tested by an electrician before you turn it on again. This happens occasionally when machinery is moved, something gets knocked or bumped resulting in something connecting where it shouldn't.

  4. #3
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    Also, can you tell us what the rating is on the breaker that is popping?
    I may be under rated for the start current that the saw is dragging.
    Have you tried it on another circuit?
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  5. #4
    Join Date
    Mar 2008
    Location
    Townsville, Nth Qld
    Posts
    4,236

    Default

    What Cliff said is the starting point, but any c/b should be able to carry 8 amps. It is less than the rating of a normal 10A GPO (power point).

    you have two possible problems:

    1. An electrical fault. If your earth leakage circuit breaker ( or residual c/b) has tripped , then you have a fault. Don't use the saw until you locate the fault !

    2. Most likely the starting current of the motor is too much for the circuit breaker, especially if you have other applicances on that circuit. Typically it can be 5 to 6 times the rated current of the motor, and can last for quite a few seconds. In this case you will need to get the c/b changed to one that will handle motor starting currents. Not necessarily a higher rated one, but one that has a bit less sensitive tripping characteristics for overloads

    If your earth leakage circuit breaker ( or residucal c/b) has not tripped , you could try it on the air con circuit which will have a higher rating, and provided the circuit is not already heavily loaded, and see how that goes. Remember that the air con may have very high starting currents too, so the circuit could trip if both your woodworker and the aircon are going
    Last edited by Dengue; 10th October 2010 at 12:30 PM. Reason: typos, lots
    regards,

    Dengy

  6. #5
    Join Date
    Nov 2007
    Location
    Victoria
    Posts
    733

    Default

    Thanks for the quick replies. Before I read Bob's post I tried it again and about 2 inches into cutting a piece of wood it stopped, sort of as the motor would have been under a bit of load.

    Bob,
    I've attached a pic of which one is tripping, not sure which one is the RCD breaker sorry.

    Cliff,
    The info on the switch says 4.5kpa C16, 240v-16A, Power N/L.....

  7. #6
    Join Date
    Mar 2008
    Location
    Townsville, Nth Qld
    Posts
    4,236

    Default

    You are going to need an electrician to change the C/b or even put in a new circuit for your shed. Get him/her to measure the currents on the circuit before and after operating the saw. My guess is that you have a fair bit of load on that circuit already, as you have only two power circuits for the whole house, and the saw starting up or when under load with cutting just pushes it over the tripping edge.
    Last edited by Dengue; 10th October 2010 at 12:40 PM. Reason: typos
    regards,

    Dengy

  8. #7
    Join Date
    Mar 2008
    Location
    Townsville, Nth Qld
    Posts
    4,236

    Default

    RCD Residual current device = Safety Switch = ELCB Earth leakage circuit breaker, are all the same, designed to trip the circuit instantly the live mains touches earth, either through a wiring fault, or through a person. They trip at about 30milliamps flowing, and trip quickly, to prevent electrocution. Needs a good earthing connection at your switchboard, ands at the point of the fault, to operate properly.

    Usually all houses are required to have one monitoring their power circuits.

    Every building site is required to have one.

    They should be tested each month by pushing the test button on them.
    regards,

    Dengy

  9. #8
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    Quote Originally Posted by Sam View Post
    Thanks for the quick replies. Before I read Bob's post I tried it again and about 2 inches into cutting a piece of wood it stopped, sort of as the motor would have been under a bit of load.

    Bob,
    I've attached a pic of which one is tripping, not sure which one is the RCD breaker sorry.

    Cliff,
    The info on the switch says 4.5kpa C16, 240v-16A, Power N/L.....
    Your RCD is the big breaker that says 40A on it - the fact that it is not tripping is a good sign.

    When you say the saw stopped - did it trip the breaker or was it just the saw itself stopping?

    If the latter then the saw's internal temperature overload switch has kicked in - another sign to get it looked at.

    if it's still the 20A breaker tripping it concerns me that it trips at just 2" into the wood. I would turn off everything else on that circuit and try again - if it works, as jill said you need a dedicated circuit.

    The next question is now what size was the piece of wood (What depth of cut) and what's the blade look like - perhaps a close up picture of both would answer those questions. Is the blade on teh correct way around - don't laugh it's happened many times.

    I can get my TS to trip my 20A breaker if I push it too hard while ripping bone dry Aussie hardwood with a depth of cut greater than about 3". I also have a current meter that allows me to monitors what is going on and when 3" deep ripping in dry aussie hardwood the saw is pulling 12A. If I start pushing the wood too hard the current jumps up to 17-18 A and can trip the breaker.

    If I keep ripping even slowly at those depths for some time eg 10 continuous minute the saw itself can overheat and trip out. I then have to wait for it to cool down before I can cut some more. A critical thing here is blade sharpness and correct blade profile for the task - ripping, cross cutting etc.

  10. #9
    Join Date
    Mar 2008
    Location
    Townsville, Nth Qld
    Posts
    4,236

    Default

    BobL, I think it is the 16 Amp c/b that is tripping
    regards,

    Dengy

  11. #10
    Join Date
    Aug 2009
    Location
    Caversham WA
    Posts
    193

    Default

    If that's the one that's tripping it's not the RCD, it's the circiut breaker. This means you are drawing too much current from that particular circiut which could be for one of two reasons, 1) you have too many other appliances operating the same time as you're using the saw, 2) the saw motor is faulty and is drawing too much current.

    It's a 16A breaker and an 8A motor so it shouldn't trip if nothing else is running off the circiut.

  12. #11
    Join Date
    Nov 2007
    Location
    Victoria
    Posts
    733

    Default

    Jill,
    We built with a volume builder so I'm not surprised that you say only two power circuits, 2 must be the absolute minimum allowed !! That said it is only a small house.

    Bob,
    Not sure which one goes off first. I was only ripping a 19 thick piece of pine very slowly. When I bought the saw the seller ripped a 50 thick bit of hardwood easily so before I moved it the motor and blade were ok.

    Sounds like I need to get the meterbox AND the saw looked at ! Either way I'm still happy with the purchase, the fence is unmoveable and the cast-iron top is deadflat.

    Thanks heaps,

    Sam

  13. #12
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    Yeah - sorry its a 16A circuit breaker that breaking.

    Quote Originally Posted by nihilism View Post
    It's a 16A breaker and an 8A motor so it shouldn't trip if nothing else is running off the circiut.
    An 8A rating for a motor means very little. The motor will pull much more current than this when it's under high loads. If the saw is pushed it could even pull 16A. The fact that it first tripped the breaker when turned on and then eventually started (probably some other device was turned off on the same line) and that it barely cuts pine for 2" suggests the breaker is too lowly rated.

    Sam - when they change the breaker make sure the electrician checks the wiring coming out of the breaker box is up to spec - if the lower rated wiring has been used then the wiring may overheat - it's unlikely but worth asking about.

  14. #13
    Join Date
    Sep 2005
    Location
    Leithfield, New Zealand
    Posts
    915

    Default

    My 3HP compressor (and 3HP saw) both blew 10 Amp fuses at the wall. I replaced it (with professional advice) with a 15 Amp slow-burn motor fuse. But by way of further information, the saw also had a 13Amp fuse in the plug and that would blow regularly on startup. It seems it pulls about 14 Amps on startup but once that weakpoint was eliminated it runs forever without a hiccup.
    1st in Woodwork (1961)

  15. #14
    Join Date
    Aug 2010
    Location
    ACT
    Age
    84
    Posts
    2,580

    Default

    Hi Sam,
    Things are a lot more complicated than just putting in a bigger breaker. As there are only 2 breakers it means it is on a house circuit The regs say at least one third of the GPOs must be on the lesser circuit. Each circuit is usually protected by a 16A Fuse or 20A Breaker but as yours are only 16A they have probably been de-rated because of insulation covering some of the wiring.
    Switch off the breaker then run round your dwelling and find out which GPOs are live and which dead then you will know which ones share the shed circuit.
    Your ultimate answer will be to have an electrician install a dedicated circuit to the shed bearing in mind you will eventually want to run a dusty etc at the same time.
    Of course there could just be something wrong with saw.
    Hugh

    Enough is enough, more than enough is too much.

  16. #15
    Join Date
    Nov 2007
    Location
    Victoria
    Posts
    733

    Default

    Thanks for all the replies and suggestions. I've got an electrician coming in the next few weeks to look at the house and also the saw just incase. As I said we built with a volume builder so no doubt the house wiring will be the bare minimum. I'll report back with what the electrician says.

    I'd like to publicly acknowledge and thank the seller for his concern and offer of a refund. While it was certainly not required I really appreciate it.

    Cheers,
    Sam