  1. #16
    Join Date
    Jun 2003
    Location
    Brisbane, Qld
    Posts
    942

    Default

    Looks like he is in the US? That gives me pause... But I have queued up his videos on VFDs, they will definitely be helpful by the looks!

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Jan 2015
    Location
    Latrobe Valley
    Posts
    160

    Default

    Quote Originally Posted by rtyuiop View Post
    Deciding factor might be if I can find a sparky who knows something about VFDs and will work for a reasonable rate.
    Any sparky will be able to do wiring and connections for your VFD when they are installing the 15A outlet. The programming and understanding the requirements of the motor windings needing to be in a delta config as Bob has stated is where I reckon most residential sparkies may be found lacking due to little or no experience with motor control.
    If you can program and configure the unit yourself, you will save yourself some dollars and once you get the motor, post a pic of the internals of the terminal box.

  4. #18
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,787

    Default

    Quote Originally Posted by maxxsinner View Post
    Any sparky will be able to do wiring and connections for your VFD when they are installing the 15A outlet.
    Unfortunately that has not been my experience.
    There's no doubt some sparkles already know how or are more than savvy enough to read the manuals and work it out for themselves.
    However,
    The young (30ish) sparky I bought my used 3P compressor from had not even heard of VFDs.
    When the next door neighbour sparky came for a shed tour he said he had heard of VFDs but he would not know how to wire one up. When I offered to show him how, he said don't bother as he would just call in a more experienced sparky to do it.
    At my mens shed I had to show our very experienced (50 years) shed sparky how to wire up a VFD.
    When I recommend men's sheds get a 3Phase motor and VFD for their dust extractors I often get a call from their sparky asking questions about VFD that tells me they know little or nothing about them. Most work it out but I have still had to go and show a couple of sheds how to program their VFD.

  5. #19
    Join Date
    Sep 2008
    Location
    Petone, NZ
    Age
    68
    Posts
    2,816

    Default

    Quote Originally Posted by rtyuiop View Post
    Looks like he is in the US? That gives me pause...
    Jack's a carpenter/joiner in Canada. He decided to equip his workshop(s) with mostly older British machinery (mostly Wadkin) and jokingly calls one shop the "Wadkin Temple". He's well known for having done the the greatest Wadkin PK (dimension saw) upgrade ever. He's a member here. Each year he holds an open day - the Rustfest:

    Rustfest 2019 at the Wadkin Temple Canada

    Cheers, Vann.
    Gatherer of rusty planes tools...
    Proud member of the Wadkin Blockhead Club .

  6. #20
    Join Date
    Feb 2009
    Location
    moonbi nsw Aus
    Age
    69
    Posts
    2,065

    Default

    You are right Bob. Seven or so years ago when I wanted to have a 3Ph Rotary Converter I found most sparkies did not have a clue even with as much information as I had gathered. A Forumite 70 miles away volunteered to put all the bits together for me. One fellow I asked, told me it would not last very long and would probably result in a fire. His answer was to buy a petrol powered generator to get 3Ph.

    My set up with the rotary is running trouble free and can deliver enough grunt when the machine is loaded up and working hard.
    Just do it!

    Kind regards Rod

  7. #21
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,787

    Default

    There are no doubt many sparkies in OZ that know all about VFDs but it's unlikely you will find them undertaking domestic wiring . The most likely places sparkies with VFD knowledge will be working are in industry but they are unlikely to be interested in wiring up a VFD for a single customer.. One of my relatives is a mechanical engineer specialising in mining equipment and he knows about them (on paper) as he stipulates them in many mining designs and apps. He's never had to wire one up but would be savvy enough to follow a VFD manual. He has an extensive home workshop but has never had any interest in installing one for himself.

    Despite this sparkies are very useful (even essential in any electrical install) because the usually should the regs and therefore what can or cannot be done, so what they say does need to be taken very seriously

  8. #22
    Join Date
    Jun 2003
    Location
    Brisbane, Qld
    Posts
    942

    Default

    Question for the brains trust - talking to a sparky today who says he works with VFDs a lot (and he didn't say anything that was so obviously wrong that I could detect it!)... He says that motor is 415v only (unusual according to him) and won't run off the 3 phase 240v which is output from a single-to-3-phase VFD. Any thoughts?

    Not a complete disaster if he is correct, I can just connect to 3 phase - I'll just lose the ability to move it around the shop between GPOs.

  9. #23
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,787

    Default

    Quote Originally Posted by rtyuiop View Post
    Question for the brains trust - talking to a sparky today who says he works with VFDs a lot (and he didn't say anything that was so obviously wrong that I could detect it!)... He says that motor is 415v only (unusual according to him) and won't run off the 3 phase 240v which is output from a single-to-3-phase VFD. Any thoughts?

    Not a complete disaster if he is correct, I can just connect to 3 phase - I'll just lose the ability to move it around the shop between GPOs.
    In that case its probably a 3Phase 415V ∆, one of those that cannot be converted without a complete motor rewind. It would be interesting to see the name plate on the motor to confirm this.

  10. #24
    Join Date
    Jun 2003
    Location
    Brisbane, Qld
    Posts
    942

    Default

    I'll take some photos (and open up the connection box) tonight.

    Thanks Bob!

  11. #25
    Join Date
    Sep 2008
    Location
    Petone, NZ
    Age
    68
    Posts
    2,816

    Default

    Quote Originally Posted by rtyuiop View Post
    ...He says that motor is 415v only (unusual according to him) and won't run off the 3 phase 240v which is output from a single-to-3-phase VFD. Any thoughts?...
    You can get VFDs that transform 240v to 400v and convert to 3-phase - but they're more expensive (considerably more I believe).

    Quote Originally Posted by rtyuiop View Post
    ...I'll just lose the ability to move it around the shop between GPOs.
    Why not get more 3-phase outlets installed (or like me, run a 3-phase extension cord)?

    Cheers, Vann.
    Gatherer of rusty planes tools...
    Proud member of the Wadkin Blockhead Club .

  12. #26
    Join Date
    Jun 2003
    Location
    Brisbane, Qld
    Posts
    942

    Default

    Quote Originally Posted by Vann View Post
    You can get VFDs that transform 240v to 400v and convert to 3-phase - but they're more expensive (considerably more I believe).

    Why not get more 3-phase outlets installed (or like me, run a 3-phase extension cord)?

    Cheers, Vann.
    The sander and my dust extractor are the only three phase machines I have - and the dusty is outside and doesn't move! And 3 phase outlets and gear aren't all that cheap...

  13. #27
    Join Date
    Jun 2003
    Location
    Brisbane, Qld
    Posts
    942

    Default

    Photos:




  14. #28
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,787

    Default

    Either your sparky doesn't want to get involved or doesn't know much about VFDs but that is definitely a convertible motor (I have a similar WEG 3kW motor on my DC but mine isa 2850 rpm - 2 pole motor).
    Your motor is wired as a Y and it's just a matter of rearranging the brass connections between the terminals to convert it toe 240V ∆.

    It's a matter of rearranging the brass strips (there will be 3 of them) marked by the red marks and connecting them .
    Please don't attempt this yourself and get your sparky to do it.
    VFDMotor.jpg

    These WEG motors are very common and widely used on water Pumps and fans with VFDs.

    I also notice your motor is 1430 rpm motor. In that case a VFD is really worth having so the speed can be boosted to 150 or 175% for belt work.
    Does the machine have a disc as well as a belt?
    Although you will have to be a bit more careful about not overheating the wood you'll find its MUCH faster with a fresh sanding belt than running at 1430.

    For shaping work I sometime run my 3HP sander up to 3200 rpm using zirconia belts - makes a lot of dust but fair rips things into shape.

  15. #29
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Quote Originally Posted by rtyuiop View Post
    The sander and my dust extractor are the only three phase machines I have - and the dusty is outside and doesn't move! And 3 phase outlets and gear aren't all that cheap...
    Check on Ebay, I think you will be surprised at how cheap they can be even for known brands such as Clipsal.
    CHRIS

  16. #30
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.
    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk


Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Am I an idiot ?
    By Phil Spencer in forum NOTHING AT ALL TO DO WITH WOODWORK
    Replies: 48
    Last Post: 29th September 2009, 08:18 AM
  2. Electrical Engineer allowed to do Electrical work?
    By ubeaut in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 0
    Last Post: 16th November 2008, 07:10 AM
  3. HELP ! I'm an idiot!
    By TheBigBJ in forum WOODTURNING - GENERAL
    Replies: 4
    Last Post: 23rd August 2003, 04:29 PM
  4. I'm an idiot........... HELP!
    By Neil in forum ANNOUNCEMENTS
    Replies: 0
    Last Post: 7th March 2003, 12:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •