    The following is a link to a post from a sparky in the SHED forum regarding 15A GPOs.
    Workshop Layout Any Ideas Suggestions

    This has significant implications for dust extraction because up until that post every sparky I had spoken to had insisted on every15A machines be on their own circuit with their own breaker.
    For DIY this meant the expense of running new cable and adding a breaker and a GPO.

    Turns out this isn't so and you can have as many 10A, 20A and 15A GPO's as you like even on the same circuit/breaker with the following proviso.
    The circuit/breaker has to be able to handle the highest current device and you obviously cannot use more than the cable/breaker capacity on that circuit.
    But please don't take my word for it, read the above post and get official sparky approval/permission etc.

    Thus a 15A GPO could be wired into an existing single 20A circuit and breaker, or 2 x15A GPOs could be even be wired into a circuit that has a 16A breaker.

    Just because your shed had only 10A GPOs doesn't mean much - you have to check the circuit and see what it is.
    For example, the cable and breaker might be capable of significantly more than 10A.
    The critical thing is the cable because if it is up for more current than its existing breaker, the breaker can easily/cheaply be replaced for a bigger breaker that matches the cable.
    Many circuits with 10A only GPOs are connected to 16A breakers but the cable may be rated for 20A.

    On a 20A circuit there is enough capacity to run one 3HP and one 2HP machines plus some power left over for lighting and a radio - if you switch to LED lighting even better.
    3HP DCs actually only draw around 9A and 2HP machines at around 7.5A.
    (technically you could run 2 x 3HP machines but that would be pushing it)

    There are several provisos.
    The first thing is convincing your sparky. The 3 sparkies I had quote on my shed wiring would only provide 1 x 15A GPOs on its own circuit and breaker
    The other obvious thing is there should not be anything else on that circuit which for lone DIY is usually not a problem, but watch out for automated devices like compressors etc sitting on the same circuit that can kick in automatically - if these are 15A or greater then they are best placed on their own circuit.

    So the folks that have only 10A GPOs in their shed and wishing to get into 15A gear may be able to officially get into 3HP machinery for relatively little cost.

    ADDED BY ADMIN

    DISCLAIMER

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.

    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Dec 2015
    Location
    Perth
    Age
    42
    Posts
    90

    Default

    Quote Originally Posted by BobL View Post
    The following is a link to a post from a sparky in the SHED forum regarding 15A GPOs.
    Sorry but I'm not a sparky. I'm a structural engineer and deal with Australian Standards on a daily basis, including expert witness reports and statements. I have always been interested in electrical work (my dad was a sparky) and hence have absorbed AS3000 Wiring Rules, but I hold no electrical qualifications. I do have a lot more experience than the average sparky in the interpretation of Australian Standards though - it's my bread and butter.

    The way to address this issue with a sparky who states that they're limited to 1x 15A outlet per 16A circuit is to ask the following questions:


    1. Are they basing this off the calculation method of maximum demand per Appendix C and specifically Table C8?
    2. If so, why can't they use the limitation method of determining maximum demand per Section 2.2.2 of the Code?
    3. If the limitation method is used and the breaker rating determines maximum demand, what is stopping them putting multiple 15A outlets on a 16A circuit given that (a) you don't intend using more than one outlet at a time, so nuisance tripping won't be an issue and (b) if you do use more than one outlet, the breaker will trip and limit maximum demand as permitted by the Code?


    In all likelihood you'll be met with blank stares and bluster, in which case move on to the next sparky. I would suggest asking them when you initially make contact (first phone call) whether they're comfortable using maximum demand by limitation rather than the calculation method guidelines in Appendix C. If they're not, keep phoning around.

    Note that AS3000 Appendix C itself contains the following that supports my reasoning:



    Of particular import is clause (b) which is directly applicable to a final subcircuit installation in a shed. The maximum demand of that subcircuit can be taken, by limitation, to be the current rating of the breaker protecting that circuit. Section C5 'Number of points connected to circuits' further states inter alia that "where more than one item of equipment is to be connected to a circuit, consideration needs to be given to- (b) the operating characteristics of the different items of equipment, including seasonal or daily variations; and (c) the circuit current under expected operating conditions..." Blind compliance with the informative Table C8 does not give due consideration to either of those aspects.

  4. #3
    Join Date
    Aug 2010
    Location
    Horsham Victoria
    Posts
    5,713

    Default

    Ive got to commit that to memory.

    DaveTTC

    Turning Wood into Art

  5. #4
    Join Date
    Dec 2015
    Location
    Perth
    Age
    42
    Posts
    90

    Default

    Quote Originally Posted by DaveTTC View Post
    Ive got to commit that to memory.
    You're building sheds for others though, correct? If so you'd really need to have an electrical layout agreed and signed off by the client before you could consider relying on the limitation method of maximum demand for subcircuits; otherwise the sparky would run a significant risk of the client being unhappy when they start up multiple machines on one circuit and trip the breaker. Different kettle of fish to your own personal shed.

    On another note, I have a little giggle every time I read your name. On the baby forums that wifey frequents, the abbreviation 'TTC' means Trying To Conceive. Not sure what yours means?


  6. #5
    Join Date
    Feb 2016
    Location
    Canberra
    Posts
    5,125

    Default

    This is interesting, for my sparky (a professional who is also a friend) knew of this and did exactly this in my studio. He enquired as to what machines I had, the draws (he looked at all the motors) and asked when and how they were used, plus likely upgrades (be enthusiastic!).

    He then told me that I needed only 1/3rd the cabling and why. He was more than happy to do the whole "more than one 15A point per" thing.... He suggested it. It looks neat and I've far more options than initially hoped, plus gobs of room for upgrade.

    I don't think there is a $$$ conspiracy. They just know that people can be complete tools when it comes to electricity.

    Perhaps the admins will permanently pin this thread?

  7. #6
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by woodPixel View Post
    This is interesting, for my sparky (a professional who is also a friend) knew of this and did exactly this in my studio. He enquired as to what machines I had, the draws (he looked at all the motors) and asked when and how they were used, plus likely upgrades (be enthusiastic!).

    He then told me that I needed only 1/3rd the cabling and why. He was more than happy to do the whole "more than one 15A point per" thing.... He suggested it. It looks neat and I've far more options than initially hoped, plus gobs of room for upgrade.
    Well that is really good to hear that there is a sparky prepared to do it.

    The bizarre thing with the sparky that ended up wiring my shed was he was OK with using double point 15A GPOs but not with putting 2 single 15A GPOs on the one circuit.

  8. #7
    Join Date
    Aug 2010
    Location
    Horsham Victoria
    Posts
    5,713

    Default

    TTC The Turning Cowboy
    Im on Bubhub and found out what it meant there. Yes i had a chuckle too

    DaveTTC

    Turning Wood into Art

  9. #8
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    The sparky who wired my shed 35 years ago used exactly that thinking. He was also the one who advised me to put all lights on three pin outlets and that has proved to be the best thing I did and I have advised many others to do the same since.
    CHRIS

  10. #9
    Join Date
    Jan 2014
    Location
    Sydney Upper North Shore
    Posts
    4,470

    Default

    With my recent shed subboard and wiring, I was having two 15 A GPOs wired up. On a whim, I asked the sparky to fit another 15A GPO on the same board as the sub board enclosure (400 mm away) so I had a 15A at each end of the shed and one in the middle. The sparky asked whether there would a chance that the front and middle would be used at the same time and I said no, so he put two single 15A GPOs on the one breaker.

    In reality though, it only saved me ~$30 - the cost of a RCBO as both were wired into the one RCBO.

  11. #10
    Join Date
    Dec 2015
    Location
    Perth
    Age
    42
    Posts
    90

    Default

    Quote Originally Posted by BobL View Post
    The bizarre thing with the sparky that ended up wiring my shed was he was OK with using double point 15A GPOs but not with putting 2 single 15A GPOs on the one circuit.
    That is indeed bizarre as the notes to Table C8 state "For the purposes of determining the number of points, a multiple combination of socket-outlets is regarded as the same number of points as the number of integral socket-outlets in the combination." In simple terms, a double outlet GPO is two points for the purposes of Table C8.

    Just another example of misunderstanding of the Code, unfortunately.

  12. #11
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by Chris Parks View Post
    The sparky who wired my shed 35 years ago used exactly that thinking. He was also the one who advised me to put all lights on three pin outlets and that has proved to be the best thing I did and I have advised many others to do the same since.
    That's what I wanted as well. One of the sparkies who quoted for the wiring refused to do this and said lights had to be hardwired. The sparky that eventually did mine did put in 3 pin plugs but I have them on a separate circuit. Losing lighting at night in a cluttered shed is a bit disconcerting.

    The 3 pin idea turned out to be useful when I changed the lighting to LED tubes. As well as changing all the existing tubes to LED I was able to add 4 extra doubles just by piggybacking onto the 3 pin outlets.

  13. #12
    Join Date
    Oct 2009
    Location
    South Africa
    Posts
    950

    Default

    Just as a point of interest, in South Africa, the standard domestic socket is 16A, and they are wired with 2.5mm wire (in the past 4mm was more common), usually on a 20A (sometimes a 30A) breaker per circuit. AFAIK there is no legal limit to the number of sockets on a circuit, but typically an average house will have two, maybe three, circuits for plug sockets, so often half of the sockets in the house will share a single breaker. Obviously it is possible to get nuisance trips, especially in winter when there are a couple of heaters running, but it does mean that you are free to hook up enough sockets to connect all your toys, and if you turn too many on, you might have to reset the breaker, which is less inconvenient than burning the house down.

    Additionally we're big users of multi-plug adapters, and each adapter should have an over-current breaker built in, which allows you to draw 16A in total. I have a double 16A socket in my garage, and I run my lathe, bandsaw and dust extractor off one of those sockets, using a multi-plug adapter. The lathe and bandsaw don't usually run at the same time, but my 3hp dust extractor and either lathe or bandsaw run at the same time with no issues.

  14. #13
    Join Date
    Oct 2013
    Location
    Perth, Australia
    Posts
    1,813

    Default

    This thread is perfect timing, I've been wondering about this stuff lately. My old man has a 15a outlet in his shed but he wasn't sure if we could run more than one machine off it. So if I understand things correctly I should be able to check the rating on the breaker it's wired to and that will tell me the total capacity?

    Edit: never mind, just thought about it and it looks like I'd need another point wired up anyway. No double adaptors for 15a from what I can tell.

  15. #14
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by bueller View Post
    This thread is perfect timing, I've been wondering about this stuff lately. My old man has a 15a outlet in his shed but he wasn't sure if we could run more than one machine off it. So if I understand things correctly I should be able to check the rating on the breaker it's wired to and that will tell me the total capacity?

    Edit: never mind, just thought about it and it looks like I'd need another point wired up anyway. No double adaptors for 15a from what I can tell.
    You can replace the single 15A GPO by a double like this https://www.bunnings.com.au/deta-15a...point_p4430422 but you may not be able to run 2 x 15A machines at the same time from this outlet. Well you can try but it will probably trip the breaker.

    If the cable is 2.5mm (preferably 4mm^2) and there is a 20 A breaker on it you could safely run a single 15A rated machine and a 10A rated machine on that circuit.

    This is no different than plugging in multiple 10A rated machines into a single circuit protected by a 16A circuit breaker. the assumption is that none of the machine are drawing their full power under load.

    It's even more subtle than this because even 15A machines don't use anywhere near 15A when free running so its not just about them being on but the load they are under.
    My BS, belt sander and DC are all 3HP 15A rated machines
    The BS uses 1.8A when free running while the Belt sander uses 3A free running and the 3HP DC uses ~7-9.5 A constantly.

    I don't know why I would do this but it means I could connect all 3 machines to my 20A breaker circuit and leave all three machines on, the DC, and the BS and Belt sander free running (13.8A total).
    Then I could move between using the BS and Belt sander.
    Under load he BS rarely goes above 5A in 150 mm wide cuts - it just doesn't seem to need the juice to cut.
    The total current would then go up to 17A.

    The Belt sander seems to max out at about 6A so when using that the total current would be about the same as using the BS under load.

    What this highlights is knowing what the actual current drawn by each machine is, is instructive and useful.

    The only 3HP (15A rated) WW machine in my shed that uses 15A is the TS and I have to be really hard on it to do that.

  16. #15
    Join Date
    Oct 2013
    Location
    Perth, Australia
    Posts
    1,813

    Default

    Cheers for the advice. I've also been pointed to an Arlec 15A power centre which could do the trick. I'm happy to muck around with electronics and motors etc but I draw the line at touching mains power. Parents place is out bush too so sparkies charge like a wounded bull for callout.

    https://www.bunnings.com.au/arlec-15...block_p7050064

    Realistically I'll probably only need it for a dust collector and table saw so hopefully that shouldn't be too much.

Page 1 of 3 123 LastLast

Similar Threads

  1. Blackwood is over rated.
    By tea lady in forum WOODTURNING - GENERAL
    Replies: 47
    Last Post: 11th May 2009, 03:35 PM
  2. Walnut - Seriously over-rated
    By TTIT in forum WOODTURNING - GENERAL
    Replies: 26
    Last Post: 2nd February 2007, 04:56 PM
  3. CE rated machines
    By IanA in forum BANDSAWS
    Replies: 4
    Last Post: 17th September 2003, 04:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •