    I have a Powtran PI8100a 004G1 VFD which is to be connected to a 15 amp single phase supply & then this will run a 3 phase 3kw Monarch Induction motor from Teco Aust on my Dust collector. The plate on the motor states
    Delta 240v 10 amp
    Star 415V 5.8 amp

    When testing the output terminals from the VFD (without the motor connected at this stage), I get 240v.
    ie test terminal A & B = 240 volt
    A & C = 240 volt
    B & C = 240 volt
    Obviously I am a total novice when it comes to electricity, but I was under the impression that the VFD would produce 415v when tested across those terminals.

    So, if I am getting 240v three pahse, can I get the motor configured to delta configuration & it will then work?
    Or am I missing something in the setup here, or is the VFD not producing correctly?

    Any help & clarification would be much appreciated thanks

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    Quote Originally Posted by lesterz View Post
    I have a Powtran PI8100a 004G1 VFD which is to be connected to a 15 amp single phase supply & then this will run a 3 phase 3kw Monarch Induction motor from Teco Aust on my Dust collector. The plate on the motor states
    Delta 240v 10 amp
    Star 415V 5.8 amp

    When testing the output terminals from the VFD (without the motor connected at this stage), I get 240v.
    ie test terminal A & B = 240 volt
    A & C = 240 volt
    B & C = 240 volt
    Obviously I am a total novice when it comes to electricity, but I was under the impression that the VFD would produce 415v when tested across those terminals.
    There are very few VFDs that will do this and expect to pay 2 - 4 times more to get this capability

    So, if I am getting 240v three pahse, can I get the motor configured to delta configuration & it will then work? s
    Correct and it will produce the same power as when powered by 415V.

    If you leave the motor in star config the motor will only run at half power so it will be overloaded by the impeller size /air volume which will damage the motor.

  4. #3
    Join Date
    Aug 2008
    Location
    Toowoomba
    Posts
    21

    Default

    Thanks BobL. That is just the clarification I was looking for.

Similar Threads

  1. fitting single phase motor to old 3 phase lathe
    By Sebastiaan76 in forum WOODWORK - GENERAL
    Replies: 15
    Last Post: 11th February 2016, 11:39 PM
  2. 240v single phase to 415v 3 phase conversion
    By Oldneweng in forum METALWORK FORUM
    Replies: 81
    Last Post: 12th July 2012, 05:58 PM
  3. Replies: 14
    Last Post: 4th May 2012, 08:48 AM
  4. Hercus 3 phase lathe, single phase supply
    By Pete F in forum THE HERCUS AREA
    Replies: 51
    Last Post: 16th January 2009, 10:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •