    I understand the theroy Bob but here is a back of the envelope quick maximum demand calculation with some obvious assumptions:
    Hot plates on 32A breaker - load must be greater than 25A or 25A breaker would be used - Add %50 rated load so 14A
    Wall oven 25A so as above - Add 10A
    Air CB - 75% connected load - 32A ~ add 21A
    AC CB - as above ~ add 12A

    So far 57A without adding Spa, HWS and lights.
    The only way that is legal is maximum demand by limitation.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Feb 2003
    Location
    back in Alberta for a while
    Age
    68
    Posts
    12,006

    Default

    could there be two 63 Amp inputs? i.e. the OP's house has a 2 phase supply?
    regards from Alberta, Canada

    ian

  4. #18
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    Quote Originally Posted by maxxsinner View Post
    I understand the theroy Bob but here is a back of the envelope quick maximum demand calculation with some obvious assumptions:
    Hot plates on 32A breaker - load must be greater than 25A or 25A breaker would be used - Add %50 rated load so 14A
    Wall oven 25A so as above - Add 10A
    Air CB - 75% connected load - 32A ~ add 21A
    AC CB - as above ~ add 12A

    So far 57A without adding Spa, HWS and lights.
    The only way that is legal is maximum demand by limitation.
    I'm not saying its right - I'm just saying that our place was done by 3 licensed sparkies.

  5. #19
    Join Date
    Jan 2015
    Location
    Latrobe Valley
    Posts
    160

    Default

    Was actually referring to the OP's switchboard with that calculation above.
    Yours sounds like it would scrape in depending on the KW of your AC's Bob. Circuit breaker for a main switch which is mandatory these days sets the maximum demand by limitation but still need to comply to 2.5.7 of AS3000 reliability of supply.
    Ian - it appears as the main switch is single pole, assuming that this is the main switchboard which I think it is.
    Looks like the meter panel in the bottom of the pic.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. How much extractor do we need?
    By elanjacobs in forum DUST EXTRACTION
    Replies: 58
    Last Post: 2nd March 2018, 12:36 PM
  2. Woodman CT-60 Dust extractor, A compact yet powerful extractor.
    By sicd_steve in forum WOODWORK - Tools & Machinery
    Replies: 0
    Last Post: 19th April 2017, 10:29 AM
  3. my new extractor
    By fubar in forum DUST EXTRACTION
    Replies: 1
    Last Post: 23rd August 2016, 08:52 PM
  4. What Extractor should I go for
    By Stewy in forum DUST EXTRACTION
    Replies: 10
    Last Post: 5th October 2012, 08:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •