    Default Power - Lighting Fitout help

    Hi all,
    I am hoping to get some help with the electrical fitout in my shed. I am asking as i want to save some money by roughing in the cable (im not conecting anything) and currently cannot get an electrician around or cant even get an answer out of one (without them looking). The electrician who ran the power to my shed is going to have a look mid december and by the tone of his voice and past experience I wont be seeing him till next year sometime.
    I have attached th plan of my layout. power circuits will be 2.5mm and the lighting circuit is 1.5mm. Is 25mm conduit enough to handle the power and lighting running on the c channel, probably about a 6 and a half meter run or do i need to go 32mm conduit and increase the cable sizes due to having it in conduit.
    Thanks in advance for any help

    Added by ADMIN

    DISCLAIMER

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.

    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Put all the light points in using 3 pin unswitched roses (power points) instead of hard wiring them. The lights have a 3 pin plug on the end of the lead and you plug them in as you would a power point. The advantage is you can add lights using double adaptors, move lights using short extension cords etc. You can put extra outlets in and not put lights on them as I did and later on as I became older I added lights. It is the best single thing I did when wiring my workshop.
    CHRIS

  4. #3
    Join Date
    Aug 2010
    Location
    Australia
    Posts
    10

    Default

    Thanks for the advice, I had planned to use plugbases for the hanging power points and the light fittings as I think it is required here in the standards, but also to make things easy down the track.
    I have had good news. After whining to the right people and losing a bet for $50 my current electrician has approved the plan telling me exactley how the wireing should go, loop in and out to each connection and he will be getting his offsider to do the connections and everything will be approved. I did forget the circuit he pointyed out for a second hand 10kw air conditioner i picked up for next to nothing that is allso getting installed so fingers crossed the power is on by the end of this weekend.
    Just goes to show if you push the right buttons and with the lure of cash at the right person magic can happen
    Now to get onto my bro for that air con by xmas....

  5. #4
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    Quote Originally Posted by hellspice View Post
    .... power circuits will be 2.5mm and the lighting circuit is 1.5mm. Is 25mm conduit enough to handle the power and lighting running on the c channel, probably about a 6 and a half meter run or do i need to go 32mm conduit and increase the cable sizes due to having it in conduit....
    The good book says that you can only put one run of 2.5mm in a 25mm conduit.
    You can have 2 runs of 1.5mm in a 25mm conduit.
    Since you have a 1.5mm & a 2.5mm in it, you will need to use 32mm conduit.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  6. #5
    Join Date
    Aug 2010
    Location
    Australia
    Posts
    10

    Default

    Quote Originally Posted by Cliff Rogers View Post
    The good book says that you can only put one run of 2.5mm in a 25mm conduit.
    You can have 2 runs of 1.5mm in a 25mm conduit.
    Since you have a 1.5mm & a 2.5mm in it, you will need to use 32mm conduit.
    In the conduit run to the lights with the hanging powerpoints some of it has 2 runs of 1.5 and 2 runs of 2.5 in a 25mm size conduit (extreamly tight), although on one side this only goes for maybe 60cm the other side goes for 2 meter's. all the runs to the powerpoints have 2.5 cables in them. Sparky said it was ok and and is putting in the aproval in for job.

    Im no electrician, than again every electrician i have asked has given a different story and price. The jobs nearly done and going to be approved and so far has set me back $400 in materials so im pretty happy.
    Happy days

  7. #6
    Join Date
    Jan 2009
    Location
    Brisbane
    Posts
    1,766

    Default

    OH dear!!! Here we go again. I hope you got a tax invoice with his license number on it. You might need it for your insurer one day.
    There ain't no devil, it's just god when he's drunk!!

    Tom Waits

  8. #7
    Join Date
    Aug 2010
    Location
    Australia
    Posts
    10

    Default

    Quote Originally Posted by Enfield Guy View Post
    OH dear!!! Here we go again. I hope you got a tax invoice with his license number on it. You might need it for your insurer one day.
    One step ahead there, I have asked for that and a copy of the aproval papers as previous he ran the power to shed upgraded the switchboard in the house and did the switchboard board in the shed. He said no problems and will have it all together when the aircon gets hooked up and the jobs all done.

  9. #8
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    I wouldn't worry too much, I am sure that the 2m length isn't going to melt down & catch fire & they are only running lights.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

Similar Threads

  1. How do Fitout-Chippies order Skirting?
    By Reno RSS Feed in forum DOORS, WINDOWS, ARCHITRAVES & SKIRTS ETC
    Replies: 0
    Last Post: 10th June 2009, 10:20 AM
  2. Framing and trim for internal caravan/campervan fitout
    By Bazza12345 in forum WOODWORK - GENERAL
    Replies: 11
    Last Post: 31st August 2008, 09:10 AM
  3. Basement workshop lining and fitout
    By numbat in forum WOODWORK - GENERAL
    Replies: 23
    Last Post: 20th March 2005, 01:49 PM
  4. Work Bench area fitout
    By MajorPanic in forum THE WORK BENCH
    Replies: 8
    Last Post: 14th March 2004, 07:06 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •