    An interesting array of opinions some that I had not considered. I will look at how much more it will cost to go a little bit thicker. What if any extra reinforcement is required.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Jan 2015
    Location
    Latrobe Valley
    Posts
    160

    Default

    Quote Originally Posted by Pat View Post
    Christos, get the slab at 125mm, then cover it with yellow tongue flooring, your back will appreciate it, especially in the colder months.
    Do you find the yellow tongue flooring slippery with a bit of saw dust on it Pat, or have you put a textured sealant on it? Do you happen to have pics of it on here?

    I am very curious as I have been looking at getting my shed floor epoxied but the $$$$ have made me hold off. That and I am not sure it's the best solution. Putting down YT flooring is something I never considered but sounds like it has merit.

  4. #18
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    I too would do a slab + yellow tongue. The floor in my shed is done in the first generation yellow tongue on steel beams and it is over 30 years old. it used to be a garage but converted to my work shop so has had a variety of uses over the years. I put a two part epoxy on it when new and I would recommend the same or similar. Is this going to be a generic steel shed? You could do a raised floor on piers and no slab which is basically what mine is in some ways. With the cost of laminated beams and the ease of getting holes bored using a bobcat that might not be a bad way to go. Doing that would allow for underfloor dust extraction as well which might appeal to you...or not.
    CHRIS

  5. #19
    Join Date
    Jul 2015
    Location
    New Zealand
    Posts
    69

    Default

    I would second the comment re underfloor dust extraction. If I were going to build a shed from scratch I would probably run some 150mm pipe under the base from the centre of the shed to my intended dusty location. So long as you can do this without comprising the strength of the foundation and in a way that doesn't interfere with vehicles driving over it.

  6. #20
    FenceFurniture's Avatar
    FenceFurniture is offline The prize lies beneath - hidden in full view
    Join Date
    Oct 2010
    Location
    1017m up in Katoomba, NSW
    Posts
    10,662

    Default

    Quote Originally Posted by maxxsinner View Post
    Do you find the yellow tongue flooring slippery with a bit of saw dust on it Pat, or have you put a textured sealant on it? Do you happen to have pics of it on here?

    I am very curious as I have been looking at getting my shed floor epoxied but the $$$$ have made me hold off. That and I am not sure it's the best solution. Putting down YT flooring is something I never considered but sounds like it has merit.
    I have YT (not on concrete), and I coated it with water based Polyurethane. It can be slippery with dust, but not so much that I want to change it.

    There is an up side to that - it encourages regular sweeping or vaccing although I'm not sure how Chistos feels about that.....

    Certainly YT is easier on the feet/knees/back than epoxy would be. (if laid on battens).
    Regards, FenceFurniture

    COLT DRILLS GROUP BUY
    Jan-Feb 2019 Click to send me an email

  7. #21
    Join Date
    Aug 2011
    Location
    bilpin
    Posts
    3,559

    Default

    [QUOTE=Beardy;2087473]Doesnt really make sense to pay an engineer to design the footings without giving the infill detail as well.
    It is usually more cost effective and practical to pour the whole slab in one go as well but yes technically you are correct[/QU
    A shed design usually comes with a footing design. It wouldnt be an extra cost. When submitting plans to council, the fee is calculated on the cost of the project. As the concrete slab will usually represent 50% of the project cost, it is a considerable saving to delete from spec. There is also a considerable labour saving as no formwork is required as the slab is poured inside the wall cladding. Best to seal the cladding to prevent concrete burn. This method also gives a vermin free finish between wall and floor.

  8. #22
    Join Date
    Feb 2018
    Location
    Shepparton
    Posts
    508

    Default

    same same I have worked on slabs that will crack before your eyes so controlling where you might get cracks only works where you expect pressure will occur such as where pipes are in place.I still say no matter how good you are at prep of slab if you can stop cracks from occurring you will be a rich man.

  9. #23
    Join Date
    May 2012
    Location
    Woodstock (Cowra)
    Age
    74
    Posts
    3,381

    Default

    Step 1 Geotech report for soil classification (council will require this)
    Step 2 Engineer designs slab but you have to tell him what type of activity /concentrated load points the slab will have imposed on it (referred to as dead floor load and live floor load)

    General accepted practice for generic shed (domestic, double garage style) min 100mm slab with thickened edge beams and internal beam) 100mm 20mpa F82 mesh for a class M slab, class H usually has extra deformed steel in the beams and 25mpa concrete, H1 and above depends on geotech report and the reaction summaries as to what thickness, steel and mpa concrete required.

    If you want to do under floor dust extraction, put ducting on top of slab, use appropriate joists and screw your sheet flooring down so if in the future if you change ducting configuration it is easy to get to.

    As for the shed people that told you 75mm slab ok....BS !!!!
    The person who never made a mistake never made anything

    Cheers
    Ray

  10. #24
    Join Date
    Jan 2004
    Location
    Towradgi
    Posts
    4,839

    Default

    As with both Brett and Chris, yes the YT can be slippery when wet or dusty, good housekeeping is required. I'm a turner so very fine dust is present every day, so the dc and vax is used at the end of the day . . . normally with a beer in the other hand to balance myself
    Pat
    Work is a necessary evil to be avoided. Mark Twain

  11. #25
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Quote Originally Posted by rwbuild View Post
    Step 1 Geotech report for soil classification (council will require this)
    Step 2 Engineer designs slab but you have to tell him what type of activity /concentrated load points the slab will have imposed on it (referred to as dead floor load and live floor load)

    General accepted practice for generic shed (domestic, double garage style) min 100mm slab with thickened edge beams and internal beam) 100mm 20mpa F82 mesh for a class M slab, class H usually has extra deformed steel in the beams and 25mpa concrete, H1 and above depends on geotech report and the reaction summaries as to what thickness, steel and mpa concrete required.

    If you want to do under floor dust extraction, put ducting on top of slab, use appropriate joists and screw your sheet flooring down so if in the future if you change ducting configuration it is easy to get to.

    As for the shed people that told you 75mm slab ok....BS !!!!
    Ray, why not a pier and beam floor/bearers/joists construction. Doing a slab, a good one not something just formed up and poured and then putting a floor on top with at least 200mm deep joists seems an expensive way to do it.
    CHRIS

  12. #26
    Join Date
    Aug 2011
    Location
    bilpin
    Posts
    3,559

    Default

    Gees, sounds more like a factory than a shed. But hey, its only money.

  13. #27
    Join Date
    Apr 2018
    Location
    Nsw
    Age
    64
    Posts
    1,364

    Default

    [QUOTE=rustynail;2087571]
    Quote Originally Posted by Beardy View Post
    Doesnt really make sense to pay an engineer to design the footings without giving the infill detail as well.
    It is usually more cost effective and practical to pour the whole slab in one go as well but yes technically you are correct[/QU
    A shed design usually comes with a footing design. It wouldnt be an extra cost. When submitting plans to council, the fee is calculated on the cost of the project. As the concrete slab will usually represent 50% of the project cost, it is a considerable saving to delete from spec. There is also a considerable labour saving as no formwork is required as the slab is poured inside the wall cladding. Best to seal the cladding to prevent concrete burn. This method also gives a vermin free finish between wall and floor.
    The shed design comes with two options, one on pad footings for an earth floor and an alternate detail for a full slab with thickenings to support the structure
    When you do the method you suggest without formwork what do you do the the back of your wall sheeting where it meets the concrete and what do you do with the base of your frame standard, do you frame them up on pedestals or concrete them in?
    The hundred odd dollars in additional council fees would be insignificant to having two concrete pours and the additional work and concrete in having pad footings

  14. #28
    Join Date
    Nov 2012
    Location
    Brisbane
    Posts
    1,809

    Default

    I have a 100 mm slab and it has a 750 kg machine on it with no issues. The soil structure and type of soil does make a difference though - an active soil (like a cracking clay) needs a stronger floor. A soils engineer could advise but your local council will know if you need to worry about that.

    If I were building a new shed for my workshop I would have an elevated floor so I could run my 150 mm dust collection ducting under it. That way it is easy to rearrange your ducting if you rearrange the workshop.

    One of my machines has its main DC outlet low down and I end up with flex hose on the floor in one place (overhead everywhere else). It is very dangerous as a trip hazard. Alternatively, if you know where your machines are going to go you could dig 150 mm sewer quality PVC pipe into the ground before laying the slab and bring it up through the floor where needed.

  15. #29
    Join Date
    May 2012
    Location
    Woodstock (Cowra)
    Age
    74
    Posts
    3,381

    Default

    Its a shed yes, cheaper insurance, no problems where you are going to put any machinery, uses and needs change over time, no restrictions if a slab, no rodent or termite problems, resale value is substantially more, nothing wrong with an infill slab either same result as integrated slab which still needs 100mm minimum and if the soil classification is H or above will move substantially more than an integrated slab. Not a lot of difference in cost between integrated slab (monolithic) and pier and infill slab.

    You will also note that it is planed to use 1/2 for vehicle / trailer parking so no sense in 1/2 concrete 1/2 bearers and joists given the minimum legal requirement for clearance under bearers is 400mm which equates to 500 step from slab to floor. A total bearers and joist floor excludes vehicle access unless substantial increase in timber specification which would be 3 times cost of concrete.

    The timber floor over slab is ONLY if doing under floor ducting for dust removal.
    The person who never made a mistake never made anything

    Cheers
    Ray

  16. #30
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Quote Originally Posted by rwbuild View Post
    A total bearers and joist floor excludes vehicle access unless substantial increase in timber specification which would be 3 times cost of concrete.

    The timber floor over slab is ONLY if doing under floor ducting for dust removal.
    My yellow tongue floor was engineered as a four car garage, the loaded wheel weight of a normal car is not that heavy. Some woodworking machines would weigh more.
    CHRIS

Page 2 of 6 FirstFirst 123456 LastLast

Similar Threads

  1. Log Cabin mail box build questions
    By Uncle Henry in forum WOODWORK - GENERAL
    Replies: 9
    Last Post: 17th February 2017, 06:29 PM
  2. Replies: 5
    Last Post: 5th January 2015, 09:09 AM
  3. Bed build questions . . . and maybe a WIP!?
    By TTIT in forum FURNITURE, JOINERY, CABINETMAKING - formerly BIG STUFF
    Replies: 61
    Last Post: 9th January 2014, 12:27 AM
  4. Quick Canoe build questions
    By JJMc in forum Michael Storer Wooden Boat Plans
    Replies: 3
    Last Post: 4th November 2011, 04:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •