Thread: 2 Phase Power

  1. #1
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    3,277

    Default 2 Phase Power

    Next year at the end of April ill be moving to a place with a shed. When I asked if it had single or 3 phase power. I was told all his equipment was 240v but the shed has 2 phase.

    What is 2 phase or was it a typo for 3 phase????
    …..Live a Quiet Life & Work with your Hands

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Jun 2010
    Location
    Canberra
    Posts
    769

    Default

    It's the Yanks who have 2-phase or "split-phase" power - most of the outlets are 110V but you can also have 220V outlets for dryers etc.

    The other instance is rural properties that are supplied with a SWER line - the transformer supplies 2 x 240v phases.

    There's a couple of other possibilities - the shed could have 2 circuits which the person is mixing up with phases. The property could have 3 phase power, but the shed circuits are supplied with circuits that use 2 of the 3 phases. However, if the shed has a range of gear in it, it should be fed with a 3 phases with at least 3 circuits in the shed so the total load can be balanced across the 3 phases.

  4. #3
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    3,277

    Default

    Quote Originally Posted by RustyArc View Post
    It's the Yanks who have 2-phase or "split-phase" power - most of the outlets are 110V but you can also have 220V outlets for dryers etc.

    The other instance is rural properties that are supplied with a SWER line - the transformer supplies 2 x 240v phases.

    There's a couple of other possibilities - the shed could have 2 circuits which the person is mixing up with phases. The property could have 3 phase power, but the shed circuits are supplied with circuits that use 2 of the 3 phases. However, if the shed has a range of gear in it, it should be fed with a 3 phases with at least 3 circuits in the shed so the total load can be balanced across the 3 phases.


    The property is in Mt Evelyn, VIC.

    I have a 3 Phase lathe so I'm guessing I will either need to have a sparky set up for 3phase then? or get one of those VFR?? things?
    …..Live a Quiet Life & Work with your Hands

  5. #4
    Join Date
    Aug 2010
    Location
    Horsham Victoria
    Posts
    5,713

    Default

    I am in a country town Ns have 2 phase. 2 x 240 or 480v

    It cN be split apparently for extra circuits but useless for 3 phase.


    Dave

    The Turning Cowboy

  6. #5
    Join Date
    Oct 2009
    Location
    Springfield NSW
    Age
    70
    Posts
    1,007

    Default

    Look at the power lines coming in from the street. If there are 2 then it is single phase, if there are 4 then it is three phase. Some older houses were supplied by 3 wires - 2 phases plus neutral. This was usually done to supply the kitchen appliances with one phase and the rest of the house on the other phase. The advantage of having 2 phases supplied is that you can run twice as many single phase circuits.

    My house has 3 wires coming in. It is an old house. The meter box has been replaced at some time in thedistant past . Now i have one phase supplying all light and power circuits, the other is for the off peak hot water - pretty useless.
    ____________________________________________________________
    there are only 10 types of people in the world. Those that understand binary arithmetic and those that don't.

  7. #6
    Join Date
    Feb 2003
    Location
    back in Alberta for a while
    Age
    68
    Posts
    12,006

    Default

    Quote Originally Posted by DSEL74 View Post
    The property is in Mt Evelyn, VIC.

    I have a 3 Phase lathe so I'm guessing I will either need to have a sparky set up for 3phase then? or get one of those VFR?? things?
    Quote Originally Posted by Avery View Post
    Look at the power lines coming in from the street. If there are 2 then it is single phase, if there are 4 then it is three phase. Some older houses were supplied by 3 wires - 2 phases plus neutral. This was usually done to supply the kitchen appliances with one phase and the rest of the house on the other phase. The advantage of having 2 phases supplied is that you can run twice as many single phase circuits.

    My house has 3 wires coming in. It is an old house. The meter box has been replaced at some time in the distant past . Now i have one phase supplying all light and power circuits, the other is for the off peak hot water - pretty useless.
    Avery is pretty close

    nearly every street has 3 phases running down it -- the 4 wires on the cross arms of each power pole

    In the old days, if you had a gas oven / gas hot water, the house would be supplied with a single phase essentially for lighting. If your oven /hot water was electric the house would be supplied with 2 phases, one for the lights the other for the oven -- which was typically on a separate 25 or 30 amp circuit.

    From memory, the current supply standard is 70 amps per phase, so 2 phases equal a 140 amp supply.

    Even if, as in Avery's case, the 2nd phase is only connected to the hot water, a sparky can tap into it before the meter - route the new wire via the other meter and you can enjoy the extra amps.
    (off peak hot water is turned on when the supply authority passes a special code down the wire)
    regards from Alberta, Canada

    ian

  8. #7
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    3,277

    Default

    What is the benefit of having 2x 240V circuits? Is there a limit to how many machines etc you can run per circuit or does it mean if you blow a fuse on one the other still runs?

    So from what is being said there aren't special motors etc for 2phase it is just an additional circuit of 240V. Is it better to get a VFD or have proper 3phase?

    I really have no knowledge when it come to electricity other than flip a switch and it makes things go, don't stick things in power points and don't mix electricity with water.
    …..Live a Quiet Life & Work with your Hands

  9. #8
    Join Date
    Aug 2010
    Location
    Horsham Victoria
    Posts
    5,713

    Default

    Again - not a professional but I do believe you can get 480 volt motors but I don't think there is any real advantage over 240


    Dave

    The Turning Cowboy

  10. #9
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    What DaveTTC says.

    It is a rural area thing.

    A single phase runs into an area & is then feed through a transformer with a centre tapped 480V secondary winding.

    This gives 2 x 240V outputs that are 180° out of phase.

    This is then run into the property switch board as 2 phases to give extra current carrying capability.

    It is used like 2 separate 240V circuits, each is fed through its own power metre.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  11. #10
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    5,773

    Default

    Appart from the SWR line stuff right up the country we do not have anything that could be considerd "two phase" in this country.

    There are houses that have two phases connected.....but they are generally considered as two seperate single phases.

    In those SWR installations, they generally function as two seperate 240v single phases....there may be a few pump motors and the odd grain elevator that run off the 480V pair of phases, but that is a ruraly specific thing.

    As has been said in the past it was far from uncommon to have two phases run into a house...but as has been said they pretty well always run as two seperate single 240V phases.

    These days, there are heavier single phase submains available or they run all 3 phases into the house.

    They ( electrical authorities) will expect you to justify the need for 3 phase power, but that is as easy as saying the word "airconditioners".
    Saying you want to run a workshop with 3 phase machines...may...um...not be wise.....tell em you want to install air conditioners and lots of em.

    It is possible to run a 415 volt single phase motor across two of 3 phases......but its not a favoured thing to do these days.

    The electricity authorities are concerned about balancing their loads across the phases....so they want any heavy demand split across all 3 phases.

    cheers
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

  12. #11
    Join Date
    Feb 2004
    Location
    Oxley, Brisbane
    Age
    79
    Posts
    3,041

    Default

    Quote Originally Posted by soundman View Post
    Saying you want to run a workshop with 3 phase machines...may...um...not be wise.

    Why not soundman?
    Bob Willson
    The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.

  13. #12
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    5,773

    Default

    Because for some it brings up the concept of industrial processes in residential areas and puts it on record.

    A friend of mine, was interested in getting 3 phase connected to his house, primarily to service his shed....that he was running a business from at the time.

    Being a former public servant..he has a way of speking to people and asking the right questions.

    He was informed that the electrical authority "may not look on his application with favour" if it stated the purpose was to run machinery...he was told in no uncertain terms....."tell em you are installing airconditioning"...and "don't mention the war"

    Because the supply authority did not consider that the residential area was properly equipped to service industrial loadings.

    Remember the supply authority is responsible for supplying a stable power supply.....some guy down the street kicking a 10 Hp motor in the guts at 6 pm may cause "issues" with the power supply and people may complain.

    Remember when the network was put into some of these areas, a bloke went arround, counted the houses, pulled some typical ( mrs Jones) figures out of the air, applied a peak demand equasion ( black magic), adds a little safety margin ( white magic) and comes up with the size of transformer required....that may have been back in 1960, when most houses had a single light in each room 3 power points in the kitchen, one in the laundry and a hot water system.
    Come 2014, and that system is looking a bit ..um...marginal.

    I know this is the way it is because, in the house I grew up in we had the neibourhood transformer in the corner of our back yard.....It caught on fire in the 60's, they replaced in the 80's because it seemed a good idea at the time but in all those years, it has been the same size tranny and still serves the same number of houses.


    If the supply authority thinks your installation will compromise the network..they don't have to connect you.

    cheers
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

  14. #13
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    3,277

    Default

    Airconditioner it is!…….looks a lot like a lathe but it is an Airconditioner I swear!
    …..Live a Quiet Life & Work with your Hands

  15. #14
    Join Date
    Feb 2004
    Location
    Oxley, Brisbane
    Age
    79
    Posts
    3,041

    Default

    Chuck a fan. That'll fool 'em
    Bob Willson
    The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.

  16. #15
    Join Date
    Sep 2006
    Location
    Wandong
    Age
    60
    Posts
    453

    Default

    Quite a few years ago it was pretty common to run 415V/single phase on country properties because the length of the line reduced losses at a higher voltage. Usually it was terminated at a transformer down to true 240V, but the SWER system was also pretty common.
    I've never understood the concept of 415/single phase - it makes no logical sense to have it.

    The old SECV then went to the idea of 'justifying' the phases, so if you needed, say, 25 amps, you could get 1 phase... if you needed 50 amp, you could get 2 phase... more than that and you could get the 3 phases. Again, there's no sense in it. (The actual current draw I don't recall, but there were certain amounts to the equation)
    The only logic that I can see behind 415/single phase is for oven supply (and maybe HWS's). A lot of ovens have (or at least, used to have) links in the connection block that could configure for different voltages (240 or 415), so maybe that was the thinking behind it.

    I think now, it's a lot easier to get 3 phase connected, but it probably costs a premium. When I built 15 years ago, I had 3 phase in the pit, so I ran all phases to the house and there were no questions asked. Then again, I ran 60Amp per phase, so they didn't quibble my requirements

Page 1 of 2 12 LastLast

Similar Threads

  1. 3 phase power machines
    By hellofellow in forum GENERAL & SMALL MACHINERY
    Replies: 12
    Last Post: 28th January 2014, 05:10 PM
  2. Power supply for 3-phase DE when using VFD
    By markkr in forum DUST EXTRACTION
    Replies: 27
    Last Post: 14th September 2013, 10:01 PM
  3. 3-phase power
    By metester in forum THE SHED
    Replies: 25
    Last Post: 19th September 2010, 08:33 PM
  4. 3 Phase Power
    By funkychicken in forum NOTHING AT ALL TO DO WITH WOODWORK
    Replies: 21
    Last Post: 11th January 2009, 06:39 PM
  5. 2 Phase Power ????
    By Mick4412 in forum HAND TOOLS - POWERED
    Replies: 18
    Last Post: 10th July 2006, 03:33 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •