    Default Interesting 3P motor

    Yesterday I picked up this interesting 3phase 3HP motor that I thought some of you might like to see.

    Its a Leroy Somer 240V ∆ / 415V Y motor with a independently powered 3P fan
    Interesting 3P motor-lsmnotor-jpg

    Nameplate
    Interesting 3P motor-lsnameplate-jpg

    The bigger terminal block is so the motor can be converted between 240V ∆ and 415V Y.
    The smaller one is so the fan can be converted between 240V ∆ and 415V Y.

    Interesting 3P motor-connections-jpg

    As you can see the fan is pretty beefy (0.12HP ) and it runs at twice the speed of the motor, so better for cooling at low RPMS when used with a VFD.

    Interesting 3P motor-lsfan-jpg

    The motor is from a very large industrial machine that was imported into WA some time ago.
    The machine had more than 20 motors on it ranging from 1/10 to ~10 HP.
    The guy that sold it to me was working for the company and he said the machine was not required and never used.
    Eventually it became outdated and although the company tried to sell the machine they could not get a buyer.
    In the end they wrote off the machine as scrap, but before it got sent off this guy took off all the motors and a lot of the control gear and has been selling these through Gum Tree.

    Most of the motors (including this one) had toothed belt pulleys with two belt positions/sizes. One of these positions was for a belt to drive a mechanical rev counter to provide feedback to control system which also controlled the motor variable frequency power supplies. He had some on the rev counters there - they looked pretty old school and I assume from all this that it was a fairly old machine.

    Most of the motors are Leroy Somer and some were ABB. Some of the bigger (5HP+) motors have large squirrel cage fans driven by 1/2HP 3P motors that ran at a constant 2850 @50Hz for max cooling at low revs.

    I'm not sure what I will do with this one. I might have a crack at replacing the 2HP SP on my 19" WW bandsaw but there is a fair bit of modding needed to get it to fit so I will have a think about it first
    Attached Images Attached Images

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Nov 2008
    Location
    Perth WA
    Age
    71
    Posts
    5,650

    Default

    So Bob,

    If you did install the motor would you use a pair of VFDs to enable the fan the run at its intended speed and the main motor at variable speeds? There have been a number of discussions regarding simultaneous running of two motors on a single VFD but in the case of this motor, I imagine there would be no advantage of its use over any other motor if a single VFD was used.

    Bob.

  4. #3
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Quote Originally Posted by Anorak Bob View Post
    So Bob,

    If you did install the motor would you use a pair of VFDs to enable the fan the run at its intended speed and the main motor at variable speeds? There have been a number of discussions regarding simultaneous running of two motors on a single VFD but in the case of this motor, I imagine there would be no advantage of its use over any other motor if a single VFD was used.

    Bob.
    Hi BT,

    I suspect that the fan is a 2 pole motor, while the main motor is a 4 pole, so even if they both ran from the one vfd, the fan will always be twice the motor speed.

    Ray

  5. #4
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,805

    Default

    Quote Originally Posted by RayG View Post
    Hi BT,

    I suspect that the fan is a 2 pole motor, while the main motor is a 4 pole, so even if they both ran from the one vfd, the fan will always be twice the motor speed.

    Ray
    I haven't tried it out yet but I also assume thats how it works.

  6. #5
    Join Date
    Aug 2007
    Location
    Melbourne
    Age
    68
    Posts
    1,417

    Default

    Quote Originally Posted by Anorak Bob View Post
    So Bob,

    If you did install the motor would you use a pair of VFDs to enable the fan the run at its intended speed and the main motor at variable speeds? There have been a number of discussions regarding simultaneous running of two motors on a single VFD but in the case of this motor, I imagine there would be no advantage of its use over any other motor if a single VFD was used.

    Bob.
    No, that is not how these are used. Only the motor is run by the VFD. The fan runs directly from 50Hz line frequency. It is supposed to provide constant cooling, no matter how slow the motor is running.

  7. #6
    Join Date
    Jun 2011
    Location
    Australia east coast
    Age
    71
    Posts
    1,469

    Default

    Quote Originally Posted by cba_melbourne View Post
    No, that is not how these are used. Only the motor is run by the VFD. The fan runs directly from 50Hz line frequency. It is supposed to provide constant cooling, no matter how slow the motor is running.
    I think that was the point AB was making. You need to run 2 VFD's if you want the fan to run at 50Hz *and* you don't have mains supplied 3 phase 415V power.....

    PDW

  8. #7
    Join Date
    Oct 2011
    Location
    Adelaide
    Age
    59
    Posts
    3,149

    Default

    There is only one cable gland into the terminal box so I think the twice as fast theory wins.
    (Before someone suggests running two sets of supply down one conduit, I suspect that would be considered bad (and unsafe) practice)

    Michael

  9. #8
    Join Date
    Aug 2007
    Location
    Melbourne
    Age
    68
    Posts
    1,417

    Default

    Quote Originally Posted by Michael G View Post
    There is only one cable gland into the terminal box so I think the twice as fast theory wins.
    (Before someone suggests running two sets of supply down one conduit, I suspect that would be considered bad (and unsafe) practice)

    Michael
    Michael, it only takes 2 minutes to drill a hole for a second gland. And its a perfectly safe practice.

    That said, that particular motor in its previous live was probably not used with a variable speed drive. The additional fan was installed to improve cooling, probably because the motor was used in an environment with elevated ambient temperature. If you look at that fan, you see that it is an axial fan. Unlike the centrifugal fan type that is normally used in TEFC motors. It likely provides a greatly increased airflow over the stock centrifugal fan, without taking up much more space.

  10. #9
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,805

    Default

    Quote Originally Posted by cba_melbourne View Post
    Michael, it only takes 2 minutes to drill a hole for a second gland. And its a perfectly safe practice..
    There was a couple of feet of old wiring still attached to the motor and there were definitely 2 sets of 3P power (one to the fan and one to the motor) in there

    That said, that particular motor in its previous live was probably not used with a variable speed drive. The additional fan was installed to improve cooling, probably because the motor was used in an environment with elevated ambient temperature. If you look at that fan, you see that it is an axial fan. Unlike the centrifugal fan type that is normally used in TEFC motors. It likely provides a greatly increased airflow over the stock centrifugal fan, without taking up much more space.
    As I said in my OP there were two toothed pulleys attached to this and on just about every motor the seller had.
    The seller was the electrical fitter that pulled the machine down and he said one pulley was to drive something and the other was to a mechanical type tacho which fed back to the VFD. He had a bunch of the old tacos with the corresponding toothed pulleys, and the original VFDs there and they look big and clunky. Very interesting to see all this and I'm glad he rescued it as the gear had never been switched on and was in very good condition

  11. #10
    Join Date
    Oct 2011
    Location
    Adelaide
    Age
    59
    Posts
    3,149

    Default

    Quote Originally Posted by cba_melbourne View Post
    Michael, it only takes 2 minutes to drill a hole for a second gland. And its a perfectly safe practice
    Not suggesting that it is not safe practice to mount a second cable gland. I was pointing out that there was only gland into the terminal box as pictured, so it was likely that only one supply was run to the motor. Looking at the terminal block photo again, it looks as if there are jumper cables between the two sets of terminals further supporting the idea.
    The reason that I suggested running two sets of cables in one conduit could possibly be considered bad practice was that it could give rise to confusion as to which conductor is in which set - if one set is made safe are you sure the other set has too, and that there has not been any cross wiring. While it has probably been done, I can't see regulators liking it.

    Michael

  12. #11
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Quote Originally Posted by Michael G View Post
    Not suggesting that it is not safe practice to mount a second cable gland. I was pointing out that there was only gland into the terminal box as pictured, so it was likely that only one supply was run to the motor. Looking at the terminal block photo again, it looks as if there are jumper cables between the two sets of terminals further supporting the idea.
    The reason that I suggested running two sets of cables in one conduit could possibly be considered bad practice was that it could give rise to confusion as to which conductor is in which set - if one set is made safe are you sure the other set has too, and that there has not been any cross wiring. While it has probably been done, I can't see regulators liking it.

    Michael
    Slightly off the topic, but I commissioned a multiple pump control system a few years back, and the electrician had run the cables, he ran the normal red, white, blue orange circ. there were three pumps, so he did three runs of cable.. and at the other end he connected all the red wires to pump 1, the white was pump 2 and the blue was pump 3... I don't think he had much experience with 3 phase stuff.. I complained, but he refused to change it...

    The question Bob asked was do you need 2 vfd's, I'm not sure we got enough information for a definitive answer..

    Ray

  13. #12
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.
    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk

  14. #13
    Join Date
    Jun 2010
    Location
    Canberra
    Posts
    769

    Default

    Quote Originally Posted by DavidG View Post
    We strongly advise contacting a Licensed Tradeperson for all electrical work.
    To be honest, I'd pay more attention to this statement if they spelled "licenced" correctly, that is, the Australian way, as opposed the the American spelling they've chosen to use.

    Although that might explain all that American-inspired flag-waving stuff they do around Australia Day.

  15. #14
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,805

    Default

    Quote Originally Posted by RustyArc View Post
    To be honest, I'd pay more attention to this statement if they spelled "licenced" correctly, that is, the Australian way, as opposed the the American spelling they've chosen to use.
    Licenced is not a word that exists in the Macquarie (Aussie) dictionary
    In the the Macquarie, "Licence" is the noun, "License" is a verb, and "Licensed" is either a verb or adjective.
    In the case in question the electrician is being described so it's the latter.

  16. #15
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    Rusty - A licensed trades person has a licence to do the work.

Page 1 of 3 123 LastLast

Similar Threads

  1. Replies: 7
    Last Post: 10th March 2014, 07:26 PM
  2. Interesting. Veeery interesting...
    By Schtoo in forum NOTHING AT ALL TO DO WITH WOODWORK
    Replies: 15
    Last Post: 8th March 2007, 12:07 AM
  3. Induction motor vs brush type motor
    By Don Nethercott in forum HAND TOOLS - POWERED
    Replies: 8
    Last Post: 27th May 2005, 02:14 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •