    Quote Originally Posted by cba_melbourne View Post
    - Put at least some sisalation under the roof, keeps cooler in summer and warmer in winter!!

    - an unflued gas heater is probably the last thing you want in a shed with machine tools in it. Burning gas releases large quantities of water vapour, which will condense overnight onto your precious lathes / mills etc.
    I'd like to emphasize these points that Chris made - Insulation is a must otherwise you spend too much money heating the great outdoors.

    Moist air and cold nights encourages the rust fairy. Unflued gas is particularly bad for putting more moisture into the air.

    Michael

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #17
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,631

    Default

    Is it possible to install sisilation to an existing tin shed without removing the roof sheets?

    I lived in Canberra for 12 years before moving to Melbourne. I found the air was so dry there that moisture/rust was never a problem. At the time I was using a gas blow heater similar to a Jetfire (ie un-flued). Would be interested to hear if Ewan suffers from moisture problems.

    I think any form of gas heating will work for the OP. I definitely would avoid reverse cycle. We had reverse cycle where I worked in Canberra and they spent a lot of the time defrosting their coils. While that's happening you get not heat from them.

    Chris

  4. #18
    Join Date
    Apr 2008
    Location
    Canberra
    Posts
    816

    Default

    Apologies for the garbled reply last night, was writing from my tablet and it was a PITA.

    Anyway, Gas isnt really appealing as I hate running out of the stuff, dont want to rent big bottles, and dont like the idea of dragging heavy cylinders around my shed....the units attached no doubt would work but they seem quite bulky too...and I feel my shed is already cluttered enough with all my toys in there.

    Fire would be cheap but as pointed out...it takes time to get cranking which defeats the purpose.

    The units linked to on ebay were electric blow heaters....theres a 3000w one on there that will cost me 60c an hour to run, and a 5000w 3 phase one that will cost me $1 an hour to run. Both have a half setting also. The 3000w one is $115 delivered, the 5000w one is $180 delivered.

    Has anyone used or seen these in action? Do you think I need the 5000w one for a 45sqm shed or could I get away with the 3000w one?

    Brendan

  5. #19
    Join Date
    Jul 2006
    Location
    Adelaide
    Posts
    2,680

    Default

    Quote Originally Posted by jack620 View Post
    I think the heat pump efficiency thing is overstated. I have 2 Daikin inverter ducted reverse cycle air conditioners in my home. They are frighteningly expensive to run.
    .
    if you calculate the heat output (to occupied space) V $'s input you will find that heatpumps are the most efficient..latest models are getting cop's of +3.00 at standard design conditions ...that means for very $ input you get over $3.00 worth of heat (when compared to electric element)

    gas (natural (ng) and not lpg) runs a close second but you only get heating...no cooling

    I think wood comes next and assumes a high efficieny combustion wood heater/stove

    electric element is basically 100% efficient..for every $ input you get $1.00 worth of heat

    can not recall where LPG fits in but its definitely very dear

    and then comes open fire pace...way way down on the list as most heat goes to atmosphere via the stack

    personally, I have a 4 panel suparay.....and for info only, these dont heat the air directly..they work by the items eg lathe, mill, and other stuff in your shed absorbing the infrared rays and then those items release that heat back into the space by convection.

  6. #20
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,631

    Default

    I would go the big one Brendan. 5000W is equivalent to 18MJ/hr. given that you have a large un-insulated tin shed in the coldest city in Oz, you will want plenty of output. Any chance you can run a mains gas pipe to the shed? How far is the shed from the nearest gas pipe on the house?

  7. #21
    Join Date
    Jul 2006
    Location
    Adelaide
    Posts
    2,680

    Default

    Quote Originally Posted by 19brendan81 View Post
    Apologies for the garbled reply last night, was writing from my tablet and it was a PITA.

    Anyway, Gas isnt really appealing as I hate running out of the stuff, dont want to rent big bottles, and dont like the idea of dragging heavy cylinders around my shed....the units attached no doubt would work but they seem quite bulky too...and I feel my shed is already cluttered enough with all my toys in there.

    Fire would be cheap but as pointed out...it takes time to get cranking which defeats the purpose.

    The units linked to on ebay were electric blow heaters....theres a 3000w one on there that will cost me 60c an hour to run, and a 5000w 3 phase one that will cost me $1 an hour to run. Both have a half setting also. The 3000w one is $115 delivered, the 5000w one is $180 delivered.

    Has anyone used or seen these in action? Do you think I need the 5000w one for a 45sqm shed or could I get away with the 3000w one?

    Brendan
    rough rule of thumb for heating a standard house is to allow 100watts / square metre...its going to be much higher for a non insulated metal shed

    If your going to use electricty as the fuel then you must consider capital cost of heatpump Versus long term fuel bill
    Insulation is important if you want to reduce fuel bill.
    If working in your shed you can always layer up and set heatpump thermostat down to say 15 to help reduce energy cost

  8. #22
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,631

    Default

    Eskimo,
    I'm no expert in the area, but my understanding is that the efficiency of heat pumps drops as ambient temperature drops. In Canberra, where it regularly gets below 0C in winter, they spend a significant amount of time and energy defrosting their coils. At what ambient temp were the figures you quoted measured?
    Chris

  9. #23
    Join Date
    Jun 2013
    Location
    Melbourne - Australia
    Posts
    13

    Default

    Interesting observation that unflued gas heaters put a lot of moisture in to the air. This would explain the problems I am having, even though I always run the heater with good ventilation.
    Maybe I should keep this Supagas heater for outdoor use only and look into a flued LPG gas heater.

  10. #24
    Join Date
    Jun 2007
    Location
    Adelaide, SA
    Posts
    478

    Default

    any one considered buying or Building one of these

    GAS_TUBE_RADIANT_HEATER.jpg



    they are the heaters... you see when you first walk in to bumblings

    looks like all you need as a blower, gas, a mixer and some length of Gal pipe ... Can't be that hard surely ...??

  11. #25
    Join Date
    Apr 2008
    Location
    Canberra
    Posts
    816

    Default

    "Any chance you can run a mains gas pipe to the shed? How far is the shed from the nearest gas pipe on the house?"

    About 1 meter...

    Re electric - Im also leaning towards the bigger one....id rather be over gunned than under gunned. For intermediate nights I have a little kerosene heater that I fired up for the first time last night...it throws out a reasonable amount of radiant heat...but pumps out water vapor in the process.

    Re layering up - yeah this is fine for most work I do, however I will only work on my lathe in short sleeves...which can be a touch nippy when its under 10 degrees in the shed, which is pretty much every night of the year for July and August, and most of June. I think it was 8 degrees when I was in there at 7.30pm last night.

    Brendan

  12. #26
    Ueee's Avatar
    Ueee is offline Blacksmith, Cabinetmaker, Machinist, Messmaker
    Join Date
    Dec 2011
    Location
    Canberra
    Age
    40
    Posts
    4,467

    Default

    Chris,
    No moisture problems here at all. Love it, I used to live down the south coast and everything rusted.

    Our house aircon stops pretty regularly to defrost, we can have ice here by 9 easily some nights. Brendan, if your planning to run it at night mostly I would not bother with heatpump tech, the cop gets pretty low once the air gets below 0.

    100w per m2 is pretty standard for heating in an insulated house. Get yourself a roll of aircell and line the whole shed, it will make a massive difference....although this morning its cold everywhere....where is that Sun?

    Cheers,
    Ew
    1915 17"x50" LeBlond heavy duty Lathe, 24" Queen city shaper, 1970's G Vernier FV.3.TO Universal Mill, 1958 Blohm HFS 6 surface grinder, 1942 Rivett 715 Lathe, 14"x40" Antrac Lathe, Startrite H225 Bandsaw, 1949 Hercus Camelback Drill press, 1947 Holbrook C10 Lathe.

  13. #27
    Join Date
    Apr 2008
    Location
    Canberra
    Posts
    816

    Default

    Re insulation - 1/3rd of the roof is currently insulated with batts and timber cladding, same with the walls....the back third of my shed used to be an office. Front two thirds is not though...I will look into putting something up there...what is the product you reccomend?

    Re sun - hours away by the look of things. Just checked BOM and it was probably more like 5 degrees when I was in my shed last night. I knew it was chilly cos my breath was starting to mist.

    Brendan

  14. #28
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Quote Originally Posted by eskimo View Post
    can not recall where LPG fits in but its definitely very dear
    At Brendans price of $0.20kWh it comes in pretty much the same. (if the gas usage rate from supgas is correct)My Shed is about 12*8 with a lot of cast iron in it, it take maybe 30 minutes to take the chill off. The owner of the heaters shed is larger but has a lot less stuff in it and in 30 minutes its heading towards t-shirt time lol. Cant say I have noticed any change in moisture problems since using the heater.

    Brendan I think it would take a fair while for 3kW to make a lot of difference to the whole shed. But the would be easy to cart about to where you are. What my heat will do in 30 minutes would take your 3kW heater 6 hours.
    Don't you have a couple of little fan heaters? I have three kicking about. As Eskimo says a W is a W as far as electric elements go. Most little fan heaters are about 2000W so try and couple and see if you notice a difference. I've tired them from time to time and while they help I wouldnt call them the answer.

    Stuart

  15. #29
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,787

    Default

    My two burner natural gas powered forge outputs 21kW which warms the shed up VERY quicklyso that I had to boost my 300 cfm ventilation to >1000 cfm ventilation and it is still not really enough. I had though about employing the 1250 cfm of my DC but that's 2.4kw of energy up the spout but I will have to do that in summer.
    Interestingly I didn't notice any problems with condensation, probably because I was using ventilation.

    Not that it gets that cold here or that we even worry about it.
    The only time we have turned on heaters inside during the last 3 years has been when we have had visitors.
    During the last couple of weeks our house has been 14º and 17º inside and we just wear a windcheater (for me its the manky one with the melted sleeves)

  16. #30
    Join Date
    Apr 2008
    Location
    Canberra
    Posts
    816

    Default

    "Most little fan heaters are about 2000W so try and couple and see if you notice a difference"

    Thats a good point Stuart....I could probably buy a couple of those dirt cheap locally and at least have them at either end of the garage or something. That 3 phase one is beefy, but an extension cord for it so that I can move it around the shed would double the cost.

Page 2 of 5 FirstFirst 12345 LastLast

Similar Threads

  1. Shed heating ornament
    By Gerbilsquasher in forum METALWORK FORUM
    Replies: 71
    Last Post: 21st June 2013, 09:46 PM
  2. Over heating 4x4
    By Gaza in forum MOTOR VEHICLES
    Replies: 14
    Last Post: 11th November 2010, 07:46 PM
  3. Shelving options for my shed
    By Ashes in forum WOODWORK - GENERAL
    Replies: 6
    Last Post: 22nd October 2008, 06:44 PM
  4. Heating jig
    By Tiger in forum METALWORK FORUM
    Replies: 10
    Last Post: 2nd March 2006, 08:16 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •