    Default Another vsd question

    I have been contemplating replacing the 50 - 60 year old motor on my so far unused macson surface grinder and adding a vsd.
    The Huanyang vsd unit so popular on this forum is listed as 220v.
    I know vsd manufacturers generally say a voltage within plus or minus 10 percent is allowable.
    Could running the vsd at 10 percent above the nominal voltage cause any complications such as overheating or tripping?
    I'm wondering if I'd be better off spending more money to buy a unit that is really meant to run on 240 volts?
    There seems to be endless questions that need to be asked and answered before taking the plunge and buying a vsd.
    Please answer this one for me.
    Mark

    Last edited by Poloris; 7th August 2015 at 10:43 PM. Reason: I forgot a bit.
    I've become a tool of my tools.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    Firstly I doubt that a 240V VFD exists. and done;t forget the +/- 10% is almost certainly just a guide.

    Here in WA, over the last few weeks I have been seeing 250+V on a regular basis. It doesn't seem to bother the VFDs at all.

    If you purchase a quality VFD that hopefully means they use components that can handle greater electrical stresses so if in doubt consider purchasing a quality brand.

  4. #3
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,774

    Default

    The nominal voltage in Australia is 230V +10% -6%.
    WA, Qld and ACT still specify 240V. I think. They may have come into line now. But it's only the official voltage level.
    Your power supply will fluctuate with changes in the load on the overall system. Hence the +/- % values.

    All that aside, a 220V rated unit will be fine for use in Australia. Most, if not all, 220V rated equipment is manufactured to withstand and operate at at higher and lower voltages and will have a similar +/- % rating.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  5. #4
    Join Date
    Aug 2004
    Location
    Perth Western Australia
    Age
    65
    Posts
    168

    Default Thanks

    Thanks for your replys I brought a quality 0.55 kw drive to power the 1/2 hp motor that will be going on the grinder. (220-240).

    Mark.
    I've become a tool of my tools.

Similar Threads

  1. Watering question....possible blonde question :D
    By Matt_M in forum MY RURAL BLOCK
    Replies: 1
    Last Post: 8th November 2013, 06:51 PM
  2. question
    By specialist in forum WOODTURNING - PEN TURNING
    Replies: 7
    Last Post: 20th July 2009, 07:42 PM
  3. Dumb question alert:- Salt and pepper question again
    By lubbing5cherubs in forum WOODTURNING - GENERAL
    Replies: 12
    Last Post: 22nd June 2008, 08:44 PM
  4. Replies: 13
    Last Post: 20th February 2007, 02:07 PM
  5. question
    By biotechy2k in forum NOTHING AT ALL TO DO WITH WOODWORK
    Replies: 4
    Last Post: 2nd October 2005, 10:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •