    Default Problems with vfd

    Hi folks, I have just acquired a new (old) 3hp 3ph lathe. As I only have single phase to the property I elected to go the VFD route for the lathe. I have wired up the VFD as per instructiions, the pretty lights flash and numbers appear on the screen but the motor isn't turning!
    What have I done wrong??

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Dec 2017
    Location
    Aldinga Beach
    Posts
    478

    Default

    you need to tell us the make of the VFD. Also the code shown on the display...

  4. #3
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,756

    Default

    Quote Originally Posted by ericks2 View Post
    you need to tell us the make of the VFD. Also the code shown on the display...
    You should also post the motor name plate and the VFD power rating or model number.

    Some photos of your connections with at the VFD and the motor end would be useful

    I assume you have absolutely nothing except a hardwired 3Phase cable between the VFD and motor ?

  5. #4
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,770

    Default

    Quote Originally Posted by Tern-About View Post
    I have wired up the VFD as per instructiions,
    As per who's instructions? As stated above, we need to know exactly what you have done so we can advise what else needs to be done to get you up and running.
    I may be down that way in the next couple of weeks if we can't sort it out here.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  6. #5
    Join Date
    Aug 2017
    Location
    Oak Flats
    Age
    77
    Posts
    11

    Default VFD problems revisited

    Alright guys, thanks to all of you for offering your expertise.
    The VFD is an ISACON unit rated 2.2kw20180605_090434.jpg see label. According to the advertising blurb it is good for up to 3hp.

    My wiring is shown in the next photo20180605_085344.jpg I have the 240v on the left connected to L and N, the 3ph to the right connected to U, V and W, with both Earths going to the Earth terminal.

    The motor end panel is shown here 20180605_090310.jpg the info shown on the panel is here 20180605_085352.jpg and there is a switch twixt VFD and motor 20180605_085512.jpg and that is how it was when I bought it.

    When I press 'Run' the indicator cycles up to 400 with 'fwd' and 'panel' lights glowing. I hear a noise (fan?) with an increasing pitch.
    If I press 'rev' the indicator cycles down from 400 to 0 and then back up to 400, the noise following the numbers in terms of pitch.
    All I have done is to wire the VFD into the circuit as per the wiring diagram supplied with the VFD. Unfortunately, the majority of the "User Manual" which includes the wiring diagram is just so much 'gobbledygook', I can't make head or tail of it.
    All through the procedures above, the motor shaft does not move at all.
    Here's hoping!
    Attached Images Attached Images

  7. #6
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,756

    Default

    Quote Originally Posted by Tern-About View Post
    and there is a switch twixt VFD and motor 20180605_085512.jpg and that is how it was when I bought it.
    This is far from ideal.
    In most cases there should be nothing between the VFD and the motor.
    If you repeatedly try to start the VFD with something like that switch in between you may damage the VFD and the motor.
    Before you do anything else you should remove that switch.

    When I press 'Run' the indicator cycles up to 400 with 'fwd' and 'panel' lights glowing. I hear a noise (fan?) with an increasing pitch.
    If I press 'rev' the indicator cycles down from 400 to 0 and then back up to 400, the noise following the numbers in terms of pitch.
    Did you reset the parameters on the VFD - its sounds like the VFD is trying to run at 400Hz - The motor simply cannot do this and the VFD will shut down.
    I have learned NEVER to trust a VFD straight out of the box - someone could have played with it and you don't just don't know what the settings are
    I suggest a complete parameter reset back to factory settings - then you should know where the VFD is starting from.
    Then set the motor parameters, slowish acceleration and deceleration times and max Frequency on the VFD
    This is minimum number of parameters that need reseting BEFORE the motor is starting

    Unfortunately, the majority of the "User Manual" which includes the wiring diagram is just so much 'gobbledygook', I can't make head or tail of it.
    All through the procedures above, the motor shaft does not move at all.
    Here's hoping!
    I would be far less inclined buy a VFD unless I checked out the manual first to make sure I can read and understand most of it.

    BTW That motor is a Y connected 415V motor. As is it will develop less than half its power using a 240V VFD. To make it develop full power it has to be reconfigured as a ∆ motor.

  8. #7
    Join Date
    Aug 2017
    Location
    Oak Flats
    Age
    77
    Posts
    11

    Default

    Quote Originally Posted by BobL View Post
    This is far from ideal.
    In most cases there should be nothing between the VFD and the motor.
    If you repeatedly try to start the VFD with something like that switch in between you may damage the VFD and the motor.
    Before you do anything else you should remove that switch.



    Did you reset the parameters on the VFD - its sounds like the VFD is trying to run at 400Hz - The motor simply cannot do this and the VFD will shut down.
    I have learned NEVER to trust a VFD straight out of the box - someone could have played with it and you don't just don't know what the settings are
    I suggest a complete parameter reset back to factory settings - then you should know where the VFD is starting from.
    Then set the motor parameters, slowish acceleration and deceleration times and max Frequency on the VFD
    This is minimum number of parameters that need reseting BEFORE the motor is starting

    I would be far less inclined buy a VFD unless I checked out the manual first to make sure I can read and understand most of it.

    BTW That motor is a Y connected 415V motor. As is it will develop less than half its power using a 240V VFD. To make it develop full power it has to be reconfigured as a ∆ motor.
    OK Bob, I accept what you are saying. Bear in mind that it is very difficult to check the manual before you buy the thing!

    I will remove the switch as suggested. As to re-setting the parameters back to the factory set-up, there is no information in the manual on how to go about this.

    There is a page headed 'Parameter set method' but I have no idea what those parameters are supposed to be! If you can advise I would appreciate it.

    I will look into how I can access the motor to reconfigure it as 'Delta'.

    Tern-about

    PS: my motor has only four terminals on it and I can't figure how that can be configured for Delta.

  9. #8
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,756

    Default

    Quote Originally Posted by Tern-About View Post
    OK Bob, I accept what you are saying. Bear in mind that it is very difficult to check the manual before you buy the thing!
    A quality VFD supplier will provide the manual before you buy. A company like Powtran has all their manuals on their website or you can ask and they will email them to you.
    How much was your VFD?

    As to re-setting the parameters back to the factory set-up, there is no information in the manual on how to go about this.[
    There is a page headed 'Parameter set method' but I have no idea what those parameters are supposed to be! If you can advise I would appreciate it.
    Sorry I can't do anything with out the manual.

    I will look into how I can access the motor to reconfigure it as 'Delta'.
    I suspect the motor will need to be opened up and configured internally.
    Can you open up the motor connection box and provide a photo of the inside of the box.

  10. #9
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    DISCLAIMER

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.
    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk

  11. #10
    Join Date
    Sep 2008
    Location
    North Carolina, USA
    Posts
    2,327

    Default

    Tern-About,

    Some years ago I bought a VFD for a 3 phase motor I had. The printed instructions that came with the VFD were incomprehensible but the mini CD that came with it had much more information. You may be able to download more information from the company web site or to get specific instructions from their customer service.
    So much timber, so little time.

    Paul

  12. #11
    Join Date
    Aug 2017
    Location
    Oak Flats
    Age
    77
    Posts
    11

    Default

    Hey Bob, here's a shot inside the connection box.20180606_090452.jpg

    Which part/s of the manual do you need? Thanks for all your help.

    PS is a run-of-the-mill sparky going to know about these things or do I need a specialist?

  13. #12
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,756

    Default

    Quote Originally Posted by Tern-About View Post
    Hey Bob, here's a shot inside the connection box.20180606_090452.jpg
    It appears the motor can be converted to 240V Delta in this box.
    Based on what's happened so far I recommend getting someone qualified to do it.
    I am also not a qualified to be giving advice - I'll leave that to someone that is?

    PS is a run-of-the-mill sparky going to know about these things or do I need a specialist?
    Some will and some won't. I would take it to a motor rewinder to get it done as they will know exactly what to do.

    Which part/s of the manual do you need? Thanks for all your help.
    I realize I suggested by my previous post that I would look at the Manual, but given you don't know how to change the VFD parameters, I really don't want to go to the trouble of learning the "ins and outs" of another VFD and then run a remote VFD tutorial ping-pong on the forum. I tried giving VFD programming advice to a mens shed over the phone on a VFD that I already knew something about and it didn't work - too many things to go wrong.
    In the end I felt obliged to go to their shed and fix it for them which I did.
    Maybe you should see if there is someone local that has VFD experience that can sit down with the manual and the VFD and then work through how to change the parameters together.

  14. #13
    Join Date
    Aug 2017
    Location
    Oak Flats
    Age
    77
    Posts
    11

    Default

    Thanks anyway Bob.

  15. #14
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,770

    Default

    I will be heading down to the Gong for work in a couple of weeks. If you haven't got it sorted by then I will see if I can drop in and get it running for you.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

Similar Threads

  1. Problems?
    By Ron Rutter in forum FORUMS INFO, HELP, DISCUSSION & FEEDBACK
    Replies: 2
    Last Post: 1st January 2016, 04:54 PM
  2. Does anyone see any problems with this?
    By doug3030 in forum TRITON / GMC
    Replies: 7
    Last Post: 28th May 2012, 09:08 AM
  3. CA problems
    By Big Shed in forum WOODTURNING - PEN TURNING
    Replies: 15
    Last Post: 13th July 2008, 07:10 AM
  4. Pre-Amp Problems???
    By Bruce101 in forum NOTHING AT ALL TO DO WITH WOODWORK
    Replies: 6
    Last Post: 27th November 2006, 10:37 AM
  5. IE problems
    By Big Shed in forum FORUMS INFO, HELP, DISCUSSION & FEEDBACK
    Replies: 19
    Last Post: 7th November 2006, 09:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •