27th October 2014, 10:07 AM #46GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
Please don't feel that you are being jumped on Normanby. I hope that you take this and prior comments as helpful information.
I haven't seen that type of 3 phase plug before, but it is definitely a 3P, N & E plug.
I would be surprised if the welder was 415 volt, (it definitely will not be 3 phase), but I do wonder if it is in fact a 240V single phase welder that was run from a 3 phase outlet using one Active terminal, the Neutral terminal and Earth. which would be perfectly kosher as far as I am aware. The only real way to find out will be to check the specs plate on your machine, (I think it's on the front panel, but I can't quite make it out in the photo). Generally speaking, welders are either built as single input voltage units, commonly 240V and 415 V either single or three phase, which are not able to be converted to other voltages and the multi voltage units which are able to be converted by altering the power cable connections internally and cover 240V, 415V and 480V. Often, the jumper positions and connection diagrams are printed inside the covers. Quite possibly yours is a multi voltage unit, but you need to be sure. As an example, the old Lincoln AC 225 "tombstone" welders were made in both single and multi voltage versions, the only external difference being the specs plate and code number, internally, they use different transformers.
As a matter of interest, when you hear someone mention two phase welders, smile to yourself. They don't exist. Two Active wires from a three phase supply only gives one phase, add the third Active and you jump to three phase immediately. Like drawing a triangle by joining dots - two dots equals a line, but three give a triangle immediately.
The "naughty lead" that you have is not kosher and while the chances of any negative outcomes are minimal when used by yourself at your home, Russian Roulette could well be played if it were ever used at another location. If, for example, the welder is set up for 240V and it were plugged in to a 415V outlet, (assuming that the wires were mixed up in the plug of course, but with dodgy leads anything is possible), then your OCV would jump from say 70VAC to 121VAC. That's more than the yanks have at their GPO and potentially fatal if you get a shock.
Your leads present a couple of issues. One being the plugs and adaptor, the other being the use of the good old orange cable which is meant only for static installation.
On the positive side, if you can drop back to a good old 15A 240V plug, then life just got cheaper and simpler as far as leads and plugs go.
-
27th October 2014 10:07 AM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
27th October 2014, 01:45 PM #47Intermediate Member
- Join Date
- Aug 2014
- Location
- North Queensland
- Posts
- 42
Thank you Marc and Karl for your comments. When I posted the original photo I expected a response but it took a while.
The instrument workshop was at a power station in Qld and the adaption connection was probably done in the 1980s and I acquired the welder in the mid 1990s. I have other welders as shown on another topic I started so I rarely use this one, only when it was the closest to where I was welding. Now I won't use until I get a proper plug and cable.
I took some photos of the only information plates on the welder, one on the front and one on the back. I will attach them for your information.
-
27th October 2014, 04:22 PM #48
Ahh yes as we suspected a straight forward single phase welder.
entirely suitable for a 15 amp circuit.
Don't let a bit of past dodgyness putt you off what was and probably still is a damn fine stick welder.
Give us some pictures of the cable that is fitted.....it may well be that it is the factory original cable..and if in good condition, may simply require the fitting of a normal 15 amp plug top.
Yanks being yanks...they may have gone overboard on the cable......have a look at the diameter....it may fit into a standard 15amp heavy duty plug top...this is the one with the standard soft plastic back cover...the HD version has a larger cable entry.
Otherwise you may have to go to the industrial style plugtop...still conventional 3 pin form but with a hard plastic backshell and a cable clamp.
If the whole cable looks a bit dodgy..and you don't want to be far from the 15 amp outlet...the chepaest option is to buy an off the shelf 15 amp caravan lead and chop the socket off....it will cost you less than the same length of 15 amp cable and a plugtop.
Don't forget to cross the T's and dot the I's and make sure it gets a good look over and Test & tag.
They simply don't build welders like that any more.
cheersAny thing with sharp teeth eats meat.
Most powertools have sharp teeth.
People are made of meat.
Abrasives can be just as dangerous as a blade.....and 10 times more painfull.
-
27th October 2014, 09:47 PM #49GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
Sorted. Made in Australia into the bargain.
The plate states 40x.076 cabling which is near 3mm, so if you use 4mm flex you will be laughing.
As an aside, I was in at my friendly welder repairer today picking up my Transpulse 350 and there in a pile were a heap of leads that were condemned after inspection. They were the good old orange 3C+E building cable.
Now if they can just catch up with the motor rewinder down the road that has 6" nails for his main supply fuses.......
For a laugh.
guide to fuse replacement.jpg
-
27th October 2014, 10:43 PM #50Senior Member
- Join Date
- Sep 2008
- Location
- Riddells Creek
- Posts
- 300
[QUOTE=Karl Robbers;1817271]
The plate states 40x.076 cabling which is near 3mm, so if you use 4mm flex you will be laughing.
The plate actually says 40 x .0076 which I assume would be inches, it works out to be quite small so 3 or 4mm would be fine.
-
27th October 2014, 11:23 PM #51
Its a 15 amp machine, so using the guidelines I posted above, standard 1.5mm2 three core flex will be just fine in shortish lengths.
From memory that is 30/0.25.mm
Its a high start current 15 amp application.
If you wanted to go beefy, you could go 2.5mm2 and that should fit in a 15 amp heavy duty plug top properly.
here is another bit of information.
as long as the cable is Australian approved flex you can establish the cross sectional area by counting the strands.
24 strands at 0.20....is 0.75mm2 or 7.5 amp flex
32 strands at 0.20...is 1mm2 or 10 amp flex
30 strands at 0.25..is 1.5mm2 or 15 amp flex
50 strands at 0.25...is 2.5mm2 or 20 amp flex
56 strands at 0.30..is 4mm2 or 25 amp flex.
To be australian approved it must conform to the stranding...the intent is that the cable can be identified by counting.
so you strip the cable back and count the strands......that was part of the trade test back when I sat for my licence.
These days though most cable has it all printed on it every foot or so.....most is moulded...though, some is printed in ink, which can come off in use and cleaning.
Note that below 1.5mm2, the current raring is 10 amps per mm2..above that there is a thermal mass issue that meand there needs to be a derating.
cheersAny thing with sharp teeth eats meat.
Most powertools have sharp teeth.
People are made of meat.
Abrasives can be just as dangerous as a blade.....and 10 times more painfull.
-
28th October 2014, 08:04 AM #52GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
-
28th October 2014, 10:54 AM #53
Sorry to harp on the matter but just to clarify.
If you look at the second spec plate in the post above.
ASC97-1964 is referenced at the top of the plate...that will be a government or military standard that predates Australian standards as we now know them...it also dates this machine to the late 60s or early seventies..in the pre metric period.
The plate gives a rated current consumption of 12 amps.....which is what it would consume averaged in normal continuous welding at the full rated output of 130 amps.
It state the Maximim short circuit current draw is 29 amps...that is how much it would draw with the dial all the way up and the rod firmly stuck.
Most electrical appliances draw considerably more than their rated input current for short periods.....this is why standard circuit breakers are specificed as holding at twice their rating for a full 60 seconds
So it is well within the 15 Amp format.....
If the guidelines I mentioned earlier in this thread are followed......( for high start current applications)15 meters or less of 1.5mm2 cable there will be less than 5% voltage drop in the cable.
Personally I would keep the mains cable on a welder under 5 meters it gives plenty of flexibility to get the machine near the job and a cable that is short enough to manage.
The biggest that is practical is 2.5mm2, because that will fit properly in standard 15 amp heavy duty plug tops.
I'd still keep the cable at 5 meters max.....remember you need to have that cable unrolled and laid out when working with the welder for heat reasons.
cheersAny thing with sharp teeth eats meat.
Most powertools have sharp teeth.
People are made of meat.
Abrasives can be just as dangerous as a blade.....and 10 times more painfull.
-
28th October 2014, 12:50 PM #54GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
-
28th October 2014, 02:00 PM #55
Yeh well I would not say that it is wise to run long runs of electrode leads much of the time.
In the past...in the days of big heavy iron bassed welders, long welding cables where pretty common because it was just not practical to drag a big heavy welder all over the job.
But these days, in the age of electronics and welders that weigh less than a lunch box.
Running 240V cabling becomes more practical.
In the past on big workshp structures and on site building welding.
The welder sat on the ground and moved very little and blokes dragged big heavy leads up the ladders and all over the scaf.
These days the tradesman has the welder slung over his shoulder and the earth and electrode leads may be as short as 2 meters.
Running the majority of the length in 240V flex will be a hell of a lot cheaper and more practical that running serioulsy heavy welding cables.
Keeping all cables as short as possible will always improve welding perfomance......but there are limits of practicality.
Almost without exception welders and all tools as manufactured have minimum length leads fitted.....purely on a cost basis.
It will be rare to see a new welder fitted with any less or any more than 1.2 meters of mains cable ( 1.5 if the factory is being generous)...because that is the absolute mimimum practical and the minumum required by the standards.
Of course many welding manufacturers and welding suppliers will recommend the use of long, big heavy welding cables.....because they will make good money selling them, where they would be unlikly to get any sale at all, if 240v flex was used.
Arround the average workshop, 5 meters of cable will allow getting the welder closer to the job without either getting in the way or hampering performance.
Longer than that and you need a good heavy extension cord.
Then we get the pretty well universal reccomendation against using extension cords with things like welders and compressors.
There is absolutly no reason why extension cords should not be used with welders, compressors and other high demand machines......AS long as those extension cords are of adequate size and properly managed from a safety point of view.
Consier those tables I posted earlier and that they are bassed on 5% maximum voltage drop.
As it stands all my welding & cutting machines have factory fitted cables, and I use a 20 amp 2.5mm extension cord to get to where I want to work.
A 5 meter cable on those machines would get me to where I want them......they may well get them when they come out of warranty and I have the time and inclination.
If I was running a stick welder on something like a trailer frame...yes I would still use long heavy earth and electrode leads, purely because it is not practical to drag the machine all over the job and I do not have a lunch box stick welder.
cheersAny thing with sharp teeth eats meat.
Most powertools have sharp teeth.
People are made of meat.
Abrasives can be just as dangerous as a blade.....and 10 times more painfull.
-
30th October 2014, 10:52 PM #56Intermediate Member
- Join Date
- Aug 2014
- Location
- North Queensland
- Posts
- 42
More Jetwelder photos
Had a bit of time recently so took the cover off the Lincoln Jetwelder featured in some earlier posts. Not a lot of welder inside the space but works ok. Removed the power supply cable but took the attached photos before. Some dust inside and quite a few mud wasp nests which is normal in this area, which means every small cavity or space in equipment has to be covered or plugged. Even a compressed air blow gun will be blocked if not used for a week or so.
Anyhow to get back to the welder I expect to get the power lead replaced with new lead with a 15A plug.
Some of the insulation around the transformer appears a bit brittle but nothing major.
Photos show general inside views including power cable connections and other end of cable that came out of the original 3 Phase plug. Also a couple of views of the welding current selector. Comments welcome.
Regards, Normanby
-
31st October 2014, 07:23 PM #57GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
Many years left in the old girl yet.
-
31st October 2014, 08:03 PM #58
Interesting..its a tap change welder rather than a reactive slug welder.
Limited settings...but that is less of a problem than some think.
There are a few things that need a bit of a clean and tidy.....but with a little attention and a new mains cable you'll get another 30 years out of it no worries
Two things that are a little concern.
I'd prefeer to see the welding cables terminated on either binding posts or moder twist connectors...easily done...this would give more options on welding cables used and be a little more robust
Note that the neutral wire is not in the terminal block with the active.......seems that this neutral wire to the transformer has broken short at some time.
Some sort of better arrangement would be nice.
a screw up gland and a P clamp would be good for the mains cable entry.....two nuts on the earth screw is the old specifcation...but that seems to have been dropped in the stsndards....still a good idea.
cheersAny thing with sharp teeth eats meat.
Most powertools have sharp teeth.
People are made of meat.
Abrasives can be just as dangerous as a blade.....and 10 times more painfull.
-
31st October 2014, 10:10 PM #59GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
I am guessing that this is the Australian made version of the Lincoln tombstone welders.
As far as I can gather, the Jetwelders were a very basic entry level machine, but as with most equipment from that era, were built to the same standards as thir flagship range.
Stud or Binzel type outputs would be a nice touch with the Binzels probably being the cheaper option, (use 35/50's in preference to the smaller 10/25's).
The duty cycle of that machine could easily be improved by the addition of a cooling fan and venting if desired as another upgrade.
Similar Threads
-
Sparky patch lead question
By Legion in forum WELDINGReplies: 8Last Post: 19th May 2014, 09:18 PM -
Stupid question
By steamjunkprops in forum WOODTURNING - PEN TURNINGReplies: 5Last Post: 14th October 2013, 08:30 PM -
Stupid! Stupid! Stupid! Ball Screw Mayhem!
By Zoot in forum CNC MachinesReplies: 13Last Post: 14th December 2008, 11:11 AM -
Dust extractor sparky question
By tonysa in forum HAND TOOLS - POWEREDReplies: 7Last Post: 10th April 2006, 11:21 PM -
Stupid Question ... Please No Stupid Answer
By Sir Stinkalot in forum WOODWORK - GENERALReplies: 1Last Post: 14th January 2002, 02:47 PM