    Default Another stupid sparky question

    A guy on gumtree is selling "2.5mm 3C+E" cable for a good price. I need new extension cables. Online US-centric charts indicate that 2.5mm diameter cable is ~AWG 10 and under the "maximum amps for power transmission" column AWG 10 is 15A.

    Two questions:

    - given my devices are only ever going to be pushing 10A constant at full output, surely these cables are more than enough? There's a picture and they look pretty big, but nowhere near as big as my existing stupidly big extension cable that's about a 50c piece in total diameter and came with 50A Clipsal socket/plug.
    - is it disingenuous to put 32A sockets/plugs on a cable like this, even though I'm the only one using them, if the cables themselves aren't capable of 32A?


    ADDED BY ADMIN

    DISCLAIMER
    No liability is accepted by U-Beaut Enterprises or the Woodwork Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.


    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk


  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    It doesn't matter that just you will be using it, if someone was to "borrow" the extension cord and do themselves a mischief then you would be liable .

  4. #3
    Join Date
    Sep 2008
    Location
    Perth
    Posts
    363

    Default

    So you need to choose the plugs to be less than the cable rating? So if I have a 32A wall socket I can only have 32A capable cable? (I think 32A and the 10/20A size are incompatible)

    And exactly how many amps can this "2.5mm" cable carry? E.g. it looks like the cable is thicker than my welder, which came with a 32A plug on a cable about half the diameter of my current extension cable. The online tables have "maximum power transmission" and "maximum amps for chassis wiring" and "NEC copper wire ampacity" etc but all these seem very US-biased. Is there an Australian standard measurement I need to look up for flex cable size for 400V 32A three phase transmission?

    Again, I could just ask my sparky which is who will be wiring up things in the end, but if I can get classified cable at 1/10 the price I'd pay the sparky shop that's what I'm looking to do, and then they're happy to wire it up for me if it is fit for purpose. But if I choose the wrong cable and fittings then they won't and I blow my money.

  5. #4
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    1,938

    Default

    Quote Originally Posted by Legion View Post
    And exactly how many amps can this "2.5mm" cable carry? E.g. it looks like the cable is thicker than my welder, which came with a 32A plug on a cable about half the diameter of my current extension cable.
    The welder is a known load and the cable can be sized accordingly. An extension lead could have any load up to the circuit design maximum.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  6. #5
    Join Date
    Sep 2008
    Location
    Perth
    Posts
    363

    Default

    Yeah, that makes sense.

    So I need ~AWG 6 or greater? ~4mm diameter per wire? That's rated to 37A for power transmission.

  7. #6
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    1,938

    Default

    Not according to the info I found :2014-10-14_1603.png
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  8. #7
    Join Date
    Sep 2008
    Location
    Perth
    Posts
    363

    Default

    In that chart the first column is areas, I was talking diameters. Actually, according to your chart the 4.0mm^2 cable is rated to 25A and that is ~2.26mm diameter so from that chart maybe 2.5mm diameter cable is borderline 32A.

    I'd rather a 32A cable, sized big enough without being ridiculously big. If I can get away with 2 or 3 or 4mm rather than 10mm per cable that would be great. My current cable is a pig of a thing to move around. I figure 40m is probably about 50kg+.

  9. #8
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    1,938

    Default

    Quote Originally Posted by Legion View Post
    In that chart the first column is areas, I was talking diameters.
    I'd bet that the cable you are looking at is NOT 2.5mm diameter, rather 2.5mm2 CSA.

    Electrical cable in Australia (well certainly in these situations) is always quoted in CSA, not diameter.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  10. #9
    Join Date
    Sep 2008
    Location
    Perth
    Posts
    363

    Default

    Oh, good point. You're probably right. Here it is:

    http://www.gumtree.com.au/s-ad/perth...ase/1057225566

  11. #10
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    52
    Posts
    1,938

    Default

    The other thing to consider is if this cable is actually flex cord, which is what should normally be used for extension leads.

    Also looking at the info I have, flex cord only goes to 4mm (that is info from only one supplier though).
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  12. #11
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,774

    Default

    Quote Originally Posted by Legion View Post
    Oh, good point. You're probably right. Here it is:

    http://www.gumtree.com.au/s-ad/perth...ase/1057225566
    That cable is not suitable for what you want. Talk to your electrician and ask him to recommend a cable size then search for it online for the best price.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  13. #12
    Join Date
    Sep 2008
    Location
    Perth
    Posts
    363

    Default

    Thanks everyone for the help and advice! You saved me $.

  14. #13
    Join Date
    Sep 2010
    Location
    Lebrina
    Posts
    1,099

    Default

    There is a brilliant little free app for android phones, (maybe apple as well), called electro droid that has a section for calculating voltage drop for DC, AC single phase and AC three phase circuits. You input the length of the cable run, the voltage, load amperage, current type and wire gauge and it will then calculate the drop. It is my understanding that you should aim for less than 5% drop for a constant load and sub 10% for surge loads such as starting motors etc. Obviously the lower the voltage drop the better.
    Lots of other handy tools in the app as well.

  15. #14
    Join Date
    Sep 2008
    Location
    Perth
    Posts
    363

    Default

    Installed. Thanks! Looks cool.

  16. #15
    Join Date
    Apr 2002
    Location
    Brisbane
    Posts
    5,773

    Default

    Just for those that may be interested.
    There are some things that have changed with the use of extension cords according to AS standards.....how do I know...I've just coughed up about $1200...yeh that is right, one thousand two hundred dollars......( don't get me started)...for the standards I need to carry.....and I am swatting up because I am due for the 5 yearly exam to reknew my licence.

    It is not and has not ever been legal, to use anything other than flex for extension cords or cords to connect equipment to a plug...it can also be argued that flex should be used to connect machines that are permenently wired..may be moved ( even a bit) or involve vibration

    yeh I know there is a lot of orange circular out there doing jobs that should be done by flex....but that is just bad bananas.

    Now there are two matters to consider with extension cords.....current rating and voltage drop.

    If you are talking about electrical matters in Australia we work in mm2, and we work off different considerations to overseas......so talk in the manner described in the standards and use australian tables.

    In fact if the cable is marked or discribed in guage.....it will not be Australian approved.

    here is a rough regirgitation of what is in the tables in the standards..tables I can not reproduce because of copyright....(ya cant know the rules unless you pay your money..told ya not to get me started)

    Equipment like compressors, fridges anything with a motor and welders produce high start currents.

    10 amp cables...that is cables with 10 amp plugs.
    1.0mm2 is permissable up to 25meters for general use and 15 meters for equipment with high start currents.
    1.5mm2 is permissable for general use up to 35 meters and 25 meters for high start currents
    2.5mm2 is permissable for general use up to 60 meters and for high start currents up to 40 meters
    4mm2 is permissable for general use up to 100 meters and high start currents 60 meters

    15 or 16 amp cables...15 or 16 amp plugs
    1.5mm2 is permissable general up to 25meters and high start current up to 15 meters
    2.5mm2 general up to 40 meters, high start current up to 25 meters
    4mm2 general up to 65 meters, high start currents up to 45 meters

    20 amp leads..20 amp plugs
    2.5mm2 general up to 30 meters, high start current 20 meters
    4mm2 general up to 50 meters, high start current 30 meters.

    the above is worked on 5% volatge drop

    This may explain why 30 meter builders leads have shrunk to 25 meters

    AND this applies to total length between the outlet and the machine.

    There was word out that they ( whoever "they" are) where trying to make it illegal to plug one extension cord into another......and it actually may be so in some situations.

    cheers
    Any thing with sharp teeth eats meat.
    Most powertools have sharp teeth.
    People are made of meat.
    Abrasives can be just as dangerous as a blade.....and 10 times more painfull.

Page 1 of 4 1234 LastLast

Similar Threads

  1. Sparky patch lead question
    By Legion in forum WELDING
    Replies: 8
    Last Post: 19th May 2014, 09:18 PM
  2. Stupid question
    By steamjunkprops in forum WOODTURNING - PEN TURNING
    Replies: 5
    Last Post: 14th October 2013, 08:30 PM
  3. Stupid! Stupid! Stupid! Ball Screw Mayhem!
    By Zoot in forum CNC Machines
    Replies: 13
    Last Post: 14th December 2008, 11:11 AM
  4. Dust extractor sparky question
    By tonysa in forum HAND TOOLS - POWERED
    Replies: 7
    Last Post: 10th April 2006, 11:21 PM
  5. Stupid Question ... Please No Stupid Answer
    By Sir Stinkalot in forum WOODWORK - GENERAL
    Replies: 1
    Last Post: 14th January 2002, 02:47 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •