    Question Electrical cable to the new shed. Sparkies?

    I want to install a sub board in a shed 120m away from domestic premises in a rural residential area.
    The cable run would be 120m from board to board.
    The supply to the house is 2phase rural. (phases are 180° apart)

    On the sub board I want to have one lighting circuit & 3 power circuits.
    The maximum on the lighting circuit, including fans would not exceed 2400watts (10amps) with everything on at once.
    The maximum on the power circuits would not exceed 6Hp in motors at once, allow 4800watts (20amps).

    The cable will be in a conduit underground for 110m.

    It would be best if we could run both phases to the shed & split/balance the load across them.

    My question is ‘what cable do I order?’

    I want to dig the trench & lay the cable & conduit & then have a registered sparky finish the job.

    If I do the dirty work, I can afford to spend more money on the cable.

    Any help would be appreciated.

    PS. I don't need a lecture about the dangers of electricity.
    I've been working with it for 28 years.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Aug 2003
    Location
    .
    Posts
    10,482

    Default

    Cliff be very careful with high voltage power, it can be very dangerous.
    Best left to a sparkie.

    Al

  4. #3
    Join Date
    Oct 2001
    Location
    Warwick, QLD
    Age
    45
    Posts
    3,462

    Default

    I would recommend organising a sparkie first, make sure that he is willing to let you lay the cable and get his recommendation on size. For a run of 120m I would reckon that the cable would have to be fairly substantial.
    Have a nice day - Cheers

  5. #4
    Join Date
    Jan 2005
    Location
    Sydney
    Posts
    1,205

    Default

    thats a lot of diging. good luck, sparky will be happy with you doing the durty work.

  6. #5
    Join Date
    Jul 2003
    Location
    On the Downs, Darling SEQld
    Posts
    1,167

    Default

    G'Day Cliff,
    The SAA Wiring Rules is at work
    can find out to-morrow
    Might I suggest you run it past the Sparkie who you are going to get to finish it.
    See what he wants$$$$$$$$$$$$$$$$$$$$$
    Over that distance some might go up the next size if things are close to the current limit.
    You can run it in Circular, in Conduit, Building wire in Conduit; what else:confused:
    Won't be Cheap.
    It will come down to whoever signs the dotted line:eek:
    Navvi

  7. #6
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    Well as I see it, Cliff just wants to dig the trench and lay the cables He didn't say any thing about connecting it up.

    Cliff

    AS3000 says that on Final Subcircuits the whole load has to be taken into consideration for the maximum concerned. The fact you are placing it over two phases means that is only half each for each phase. So you need to calculate the total wattage and allow half for each phase.

    So cable has the following maximum loadings
    2.5mm2 = 4800watts protected by a 20amp circuit breaker
    4.0mm2 = 6000watts " " " 25amp circuit breaker
    6.0mm2 = 7680watts " " " 32amp circuit breaker
    10.0mm2 = 9600watts " " " 40amp circuit breaker

    The other thing you have to allow for is voltage drop because of the distance over 25metres.

    The trouble is there is so many variables it would be better to ask the lecky what size cable and and conduit or go and buy AS3000 you cand download it from Standards Australia for about $90. Go here

    http://www.standards.com.au/catalogu...AS778112015227

  8. #7
    Join Date
    Jan 2004
    Location
    Sydney, NSW
    Age
    46
    Posts
    55

    Default

    G'day Cliff,

    As Barry said, there are a heap of variables here so I'd be hesitant to recommend a cable size in case you bury it and then the sparky refuses to connect it because he reckons it's wrong. I'd get quotes from a couple saying you'll be laying the cable yourself (believe me, most'll be more than happy not to have to do the dirty work) and get them to give you the cable size.

    When you're digging the trech, the SAA wiring rules state that you have to have at least 500mm cover to the top of the conduit, you have to use heavy duty 'orange' conduit and each supply must have 100m spacing from other services. That's a heap of digging :eek:

    Have fun

  9. #8
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    I've got the rules....
    I know the colours...
    I know the dept....
    I know the wire sizes for currents...
    I just can't figure out what I need to use over that distance.

    I got a quote, the bloke mumbled something about 35Amp cable & the prieck didn't show up when I had a ditch digger on site for plumbing work so F$%K him, he misses out.

    I'll get the ditch digger out again & I'll do it myself.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  10. #9
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    Looks like you will have to read the rules and work it out. Two runs of conduit and use building wire you may have to get some special rolls as standard is only 100 metre rolls as you can't make buried joints, although a mate of mine used to put a junction box in the middle of a run, join the cable with connectors and fill it up with silicone to keep the moisture out.

    You can get the formula to calculate the voltage loss from the rule book. Conduit comes in 4 metre lengths. You will need about 62 to 63 lengths. Going to be xxxxxxeeee.

  11. #10
    Join Date
    May 2003
    Location
    Kuranda, paradise, North Qld
    Age
    62
    Posts
    5,639

    Default

    Cliff,
    will ask sparky next door as soon as I see him. He works for Ergon now, travels around testing equipment, often gone for a few days at a time.

    Mick
    "If you need a machine today and don't buy it,

    tomorrow you will have paid for it and not have it."

    - Henry Ford 1938

  12. #11
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    The conduit is the cheap bit....
    You can get 3 bits of the new building wire down a single 25mm conduit & 5 down a 40mm no sweat so that won't be a problem. (shame about the heat )
    I was hoping for something BIGGER!
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  13. #12
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    Quote Originally Posted by journeyman Mick
    Cliff,
    will ask sparky next door as soon as I see him.....
    Ta.

    I'm coming to see you as soon as I find some good legs. :confused:

    Well, when it comes to bathroom cabinets, I'm a leg man, have you ever seen good boo..... Oooooo yeah, I remember now.... ... but they weren't permanent. (& the mirror did funny things to them )

    We want a bathroom cabinet that is up off the floor & all the legs that we have seen so far a CWrap with a capital CW.
    I'm going to try Lincoln Sentry tomorrow
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  14. #13
    Join Date
    May 2003
    Location
    Kuranda, paradise, North Qld
    Age
    62
    Posts
    5,639

    Default

    Cliff,
    didn't you like any of the legs at Wood's? (Cnr of Scott & Doyle Sts) They might also have other models they can order in. So might Lincol Sentry for that matter but I've been pretty unimpressed with their service to date. Spend a bit of money with them but they haven't got any catalogues (out of print for over a year) and don't keep much stock. I've had problems getting a partiular product as they don't always keep it in stock. Faxed an order in to them a week prior last time to find that it was still in the fax tray!:mad: They obviously don't want my business. End rant

    Mick
    "If you need a machine today and don't buy it,

    tomorrow you will have paid for it and not have it."

    - Henry Ford 1938

  15. #14
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    Quote Originally Posted by journeyman Mick
    Cliff,
    didn't you like any of the legs at Wood's?
    Nah.

    Quote Originally Posted by journeyman Mick
    ...Lincol Sentry...I've been pretty unimpressed with their service to date...
    You couldn't complain about their service, they wouldn't know what you were talking about.

    They are THE rudest people in Cairns. Full Stop. :mad:

    I looked at Bretts in Brissy when I was there & I've looked in Woods & Bunnies here in Cairns.
    Bretts & Woods have the same stuff.
    I don't know what Bunnies have 'cos whatever it was, it's out of stock.

    The reason that Lincol Sentry are on the end of the list is 'cos I've got no where else to go now.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  16. #15
    Join Date
    Jan 2005
    Location
    Newcastle/Tamworth
    Posts
    520

    Default

    Hi Cliff, Not a real easy question you have there. The first step is to determine the maximum demand.

    Lights = 3A for 1 to 20 light points
    socket outlets = 10A for 1 to 20 outlets
    motors = 100% of highest load and 50% of remainder

    Lets assume you arrive at 30A. It probably is easiest to put this on one phase only because of the small load and simple twin and earth run.

    The 3 factors determining circuit length and size are:
    1. maximum demand (ie current carrying capacity) (not likely to be limiting factor in such a long run)
    2. Voltage drop (pretty important here)
    3. Short circuit temperature

    Most of this is in AS 3008 1.1 (electrical installations - selection of cables - Australian conditions for up to 0.6kV)

    Basically 2.5mm2 buried in conduit has 31A current carrying capacity
    and 4mm2 has 40A current carrying capacity.

    The voltage drop for 120m of 2.5mm is about 29V and for 4mm is 18V (both way over the 5% limit allowed)

    I would try to accurately work out the maximum demand and then run through the calculations to see if you can get away with a single run of 4.0mm twin and earth in conduit.

    Cheers
    Pulse

    Happy to help more if needed...

Page 1 of 3 123 LastLast

Similar Threads

  1. My shed accredited shed
    By Waldo in forum WOODWORK - GENERAL
    Replies: 52
    Last Post: 24th November 2006, 03:32 PM
  2. Replies: 5
    Last Post: 10th July 2005, 09:25 PM
  3. My Non-existent Shed Story
    By RufflyRustic in forum WOODWORK - GENERAL
    Replies: 14
    Last Post: 14th June 2005, 11:28 PM
  4. Shed, Garage or Workshop?
    By bitingmidge in forum WOODWORK - GENERAL
    Replies: 36
    Last Post: 2nd July 2004, 01:09 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •