Thanks: 0
Likes: 0
Needs Pictures: 0
Picture(s) thanks: 0
Results 1 to 13 of 13
-
13th August 2007, 09:56 AM #1
Converting 3-phase compressor to single phase
There have been several threads on the forum regarding converting 3 phase
machinery to single phase.
In some cases the suggestion was that this was easy, just replace the
3-phase motor with a single phase motor.
However, there are traps for the unwary, as my son has just found out and I
would be interested in suggestions/comments from the engineers/electrical
engineers/electricians among you.
My son was give a compressor with a 3-phase motor but does not have 3-phase
power in his shed.
He then investigated the possibility of converting to a single phase motor and
one of the engineers at his work came up with some calculations to indicate
that this was possible ( see below ).
He then went out and bought the single phase motor, fitted the new pulleys,
and everything worked.
Yippee I hear you say.
Well not quite, when he ran the compressor with the lights on in his shed (6x2
4ft fluoros) the lights "pulsed", ie dimmed and brightened, in time with the
compressor stroke!
I'll let him tell the story from here:
Anyway calcs as folows.
Base Formula:
Power (HP) = Torque (ftlb) x RPM / 5252
Therefore
Torque = Power x 5252 / RPM
In the case of the Copressor at standard - Fitted motor is 5.5HP, 2865RPM
with a 85 od pulley
Copressor pump has a 290 od pulley
So using Dia*RPM=Dia*RPM to determine Pump speed = 85*2865=290*RPM,
RPM=85*2865/290 = 839.75RPM
So Torque at the drive shaft = 5.5x5252/2865 = 10.08ftlb
Torque at the driven shaft or pump = 5.5*5252/839.75 = 34.39ftlb
All good so far?
Converted to single phase motor 3HP, 1400RPM
Torque at the drive shaft = 3*5252/1400 = 11.25ftlb
If I was to matain the same pulley ratios I would have 85*1400/290 = 410RPM
at the pump. This is below the minimum RPM of 460RPM listed on the spec
sheet and would only give me 10.86 FAD (Free Air Delivery) With that in Mind
I thought I would alter to give myself around thee 15CFM FAD.
How Did I work this out?
Comressor has FAD of 22CFM at 830 RPM according to the spec sheet. Therefore
22/830*410 = 10.86CFM FAD
So I went to a 118 OD Pulley on the Drive giving me 118*1400/290 = 569.65RPM
at the pump. Therefore 22/830*569.65 = 15.1CFM
With all that in mind, back to the torque:
3*5252/569.65 = 27.65ftlb (this may be my issue, but considering I still
have flickering at nil pressure start I think all is in vain anyway.)
To maintain original torque at the pump I would need as follows
3*5252/34.39 = 458.15RPM (Say 460 Minimum) which would give me 22/830*460 =
12.19CFM FAD.
Hows your head so far??
Now the electrics:
3HP motor has a rating of 12.4 Full load amps.
When I put the Clamp Meter on the active lead, nominal readings ranged from
about 5amps at nil pressure start to about 11.4 at 110PSI add to that the
the motor showed no signs of struggle at either nill pressure or 100PSI
start (Adjusted the pressure swith to test to 100PSI rather than 75PSI
start).
All was great I thought! so I forged ahead with the final fitment, taking me
in to the early evening. That's where all went pear shaped. Lights pulsed in
time with the compressor. Faint at nil pressure start encreasing intensity
as pressure and load increased. You wouldn't want to be epileptic!!!
Free run, Motor runs at about 3.6 amps.
As the pulsing was in time with the compressor My guess is that the motor
load is mini spiking with each compression stroke. This I believe is
confirmed by activating the peak hold on the clamp meter. Readings gained
now range from 9 to 17+ amps nil to 110PSI.
I understand the mechanics without a problem, it's the electrics where I
fall behind. If there are any electrical engineers on the forum that could
explain where I went wrong, it would be great, even if to put my brain to
rest!!!
Shed is powered by a 32amp circuit from the house board
using a 25m run of 6mmsq orange circ cable.
At no point did the 20amp breaker for the compressor circuit trip, nor did
the motor thermal protection. While testing yesterday, I had the compressor
cycling over and over for about 1/2-3/4 of an hour. Motor got warm enough to
be uncomfortanble to put hand on but not burning hot.
If you are still with us this far, he would appreciate any comments suggestions as to either what causes this "pulsing" or how to overcome it.
-
13th August 2007 09:56 AM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Age
- 2010
- Posts
- Many
-
13th August 2007, 04:51 PM #2Senior Member
- Join Date
- Jan 2005
- Location
- Brisbane
- Age
- 52
- Posts
- 468
Fred, glad to help out but I have a question about the above.....
You have a sub board in the shed? So a 32 amp circuit in the house board that goes to a sub board that includes multiple circuits?
With how many circuits?
Is the light circuit on its own 10 amp breaker? From the text above you are drawing about 2AMPs for the fluros....
Or is it a mixed circuit?
-
13th August 2007, 07:36 PM #3
Warren, sorry for delayed reply, have been out all afternoon.
Here is my son's reply:
Circuit as follows 32amp breaker at house board
Sub board in shed contains:
All power fed through 63Amp / 30mA RCD to:
1 x 10A Breaker - Internal Lighting (4 x triple fluro & 2 x single fluro)
1 x 10A Breaker - External Lighting (None connected at this point)
1 x 16A Breaker - 4 double 10A Outlets
1 x 16A Breaker - 2 x double 10A Outlets
1 x 20A Breaker - 1 x single 15A Outlet (Welder)
1 x 20A Breaker - 1 x single 15A Outlet (Compressor)
Just in case, all internal shed wiring is 2.5mmsq braided white flat.
Length of run to 15A outlets less than 1m as they are mounted on the sub board.
Not being an electrician or electrical engineer, it has us baffled!
Thanks for your help
Fred
-
13th August 2007, 08:57 PM #4SENIOR MEMBER
- Join Date
- Jan 2007
- Location
- Brisbane
- Posts
- 699
Flicker rate problem
Big Shed,
Any chance of getting a measurement of the voltage at the shed board without the compressor running and at the house board for the same condition? Also need the same measurements but for the compressor running?
I want to see if the problem is with excessive voltage drop in the cable between the house and the shed or combined with the voltage drop at the house. It may be a problem that requires running an independant cable from the house for this circuit. My knowledge on the operation of fluorescent lights is limited but I will try to ask some of the guys in my home office if there is something about these lights that could be part of the problem and could be resolved with changes to them. This may take a couple of days with our holiday on Wednesday.
I do design large power systems and have to carryout calculations to avoid these sorts of problems but it is typically at startup and not during operation of the motors.
Cheers,
-
13th August 2007, 10:20 PM #5
I know it is a bit different but what about a heavy fly wheel on the motor / compressor to smooth out the load surges?
-
13th August 2007, 10:39 PM #6Intermediate Member
- Join Date
- Nov 2006
- Location
- Frenchs Forest NSW
- Age
- 74
- Posts
- 43
Hi Big Shed,
I'm not an electrician but I've been in the air compressor repair business for 34 years.Just a few weeks ago I had a spare pump (Swan ,exactly the same as yours) left over and I figured this would make a nice compressor to use in my woodworking shop at home.The only problem was that I only had a 1.75 Hp motor left over from another job.No problem..I just have to slow it down so I don't overload the motor.So I did some calculations,fitted a smaller pulley to the motor and ran the compressor at a much slower speed. Beauty I thought...nice and quiet. Just what you want at home.But...when I run the compressor in my shop the lights are flickering very badly. And I think this is the problem: Running the compressor too slow. To fix the problem I fitted a 3Hp motor and I'm running the compressor at the speed it was designed for. And the lights??? No more flickering. Or at least it happens so fast you can't see it.
-
13th August 2007, 11:11 PM #7
Thanks Walro, that seems to mirror my sons' experience. His problem would be that he can't go to a bigger size motor!
-
13th August 2007, 11:13 PM #8
-
13th August 2007, 11:16 PM #9
-
13th August 2007, 11:46 PM #10
If you can not put the fly wheel on the same motor put it on another one which you have running at the same time.
It will idle along until the voltage tries to drop, then it will generate and carry the load.
Last straw but that is what the snowy scheme does on the grid.
Apart from that you can use a 50hz tuned cct to electronically do the same thing. Big and expensive choke and capacitors.
Or change the lights to incandescent.
Or run the lights from a filtered supply.
Or run the lights from a battery supply with a charger.
-
14th August 2007, 06:46 PM #11
Here is some fuel to the compressor fire, this is a reply received from an electronics engineer in response to my sons' question.
Firstly, I don't think the peak reading that your getting with the clamp meter is a problem, because the nominal rating for the motor will be an rms (root mean square) value. The peak of an rms value, is root 2 (1.41) times the rms value. Therefore 12.4 * 1.41 = 17.5 amps peak at Full Load should be OK.I also don't think it will be a voltage drop problem, because they have to install cable that will not drop the voltage by more than 5% (12 Volts) at the rated current. Your well below the 32 amps, so it should be fine. (as a ROUGH guide the max current for wire is about 10 times the cross sectional area, approx 60 Amps.)But to check the voltage drop, you can use the following formulas:To determine the resistance of the wire:R = ρL/Awhereρ = resistivity of the wire material, (the resistivity of copper @ 20 deg C is approximately 1.724 x 10^-8 ohms.m)
L = length of the wire, and (25 m)
A = area of the conducting cross section of the wire. [ 6mm^2 = (6 x 10^-3)^2 = 6 x 10^-6 ]
Therefore the resistance of the wire (R) = 1.724 x 10^-8 x 25 / 6 x 10^-6 = 0.07183 ohms. And I think you need to multiply this by two to allow for the return wire so; 2 x 0.07183 = 0.1436 ohms.
Voltage Drop, V = I * R, so at the Full Load current the Voltage Drop will be: 12.4 * 0.1436 = 1.78 Volts. Hardly worth the effort really was it??
I don't think it will be a harmonics problem, because harmonics are usually only a result of distorting the supply voltage. This is more of a problem when you have switching loads, or speed control circuits for motors etc..
It could be something to do with the back emf produced by the motor?? (motor acting as a generator) As the current changes the inductance of the motor can produce some high voltages. Not sure about this, the electrical side of things is not really my forte. Have you got a meter that you can connect into a power point to check the voltage variations? (I could loan you one if you want) It would be interesting to see if the voltage is increasing or decreasing when the motor is running.
-
14th August 2007, 07:54 PM #12
This is the point I drag the oscilloscope out the cupboard.
Pity I am not closer.
-
20th November 2007, 06:06 AM #13Tool collector
- Join Date
- Nov 2004
- Location
- Santpoort-Zuid, Netherlands
- Age
- 67
- Posts
- 462
Hi Big Shed,
apart from all the calculations (which look very impressive), doesn't your compressor just need 5,5 HP since the original motor had 5,5 HP? In that case, it would stand to reason that a 3 HP motor has to strain very much at every compression stroke and the resulting high drawn single phase current (probably approaching starting or stalling Amp values, which can be six times nominal use) would show in your lighting brightness. Just a suggestion, i wasn't much in maths, you know...
Regards,
Gerhard Schreurs
Netherlands
Similar Threads
-
replacing three phase motor with single phase
By rev in forum HAND TOOLS - POWEREDReplies: 18Last Post: 16th December 2007, 04:32 PM -
More phase converter questions
By Fossil in forum METALWORK FORUMReplies: 4Last Post: 16th June 2006, 07:23 PM -
Upgrading to 3 phase motors from single phase
By boban in forum HAND TOOLS - POWEREDReplies: 7Last Post: 28th March 2005, 03:28 PM