Thread: Do I really need a 15 AMP plug
-
31st July 2013, 01:04 PM #16.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,793
-
31st July 2013 01:04 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
31st July 2013, 02:28 PM #17GOLD MEMBER
- Join Date
- Aug 2011
- Location
- bilpin
- Posts
- 3,559
Goes without saying
-
31st July 2013, 03:16 PM #18
Hi Bob,
i last measures about a year ago. Might stick my metre in a socket tonight and take another look
-
31st July 2013, 03:30 PM #19
The safest thing to do is get an electrician in to advise you!
Some important points that haven't been made yet are...
- a "15 amp plug" is a mechanical device to ensure that it can only be plugged into a 15amp circuit. It has nothing at all to do with the plugs capacity to the job it is only to make sure that you plug into a 15amp circuit.
- calculating the current drawn by a motor is pointless if you only look at the full load current. At the time of starting, and depending on the type of motor, the current drawn can be up to 5 times the full load current
- AT THIS POINT IN TIME all Australian networks supply at 240V with a tolerance that can be +3%/-6% (225V to 248V) and the utilities in some states suffer pretty substantial penalties if supply is outside that range BUT......
- the standard voltage in Europe is now 230V (and I think subject to +3/-3%, 223V to 236V) and there are a number of utilities and regulators looking at changing our standard to match
- So, if you have calculated 6 amps at full load, at start up it COULD be 30amps and, if you start your dust collector at the same time, you can very quickly be drawing 40 amps!
The moral of the story is to get a sparky to look at it for you AND it is always good practice to NOT connect your machine and the dustcollector to the same switch and start at the same time.
flettya rock is an obsolete tool ......... until you don’t have a hammer!
-
31st July 2013, 03:49 PM #20GOLD MEMBER
- Join Date
- Aug 2004
- Location
- Perth WA
- Posts
- 2,035
Have ya got a file?
Experienced in removing the tree from the furniture
-
31st July 2013, 05:56 PM #21
Fletty, Sydney is now 230V +/-
Pat
Work is a necessary evil to be avoided. Mark Twain
-
31st July 2013, 06:50 PM #22
-
31st July 2013, 07:09 PM #23
The voltage will vary at your premises according to the load at various times of day. Just check how long a pot of water takes to boil when every one in the street is cooking and at off peak times.
RegardsHugh
Enough is enough, more than enough is too much.
-
31st July 2013, 07:58 PM #24.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,793
-
31st July 2013, 08:44 PM #25.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,793
I have current and voltage meters that I can move around and check what the start up and running currents are on with all my appliances and machines.
The most monitoring I have done are on my table saw, 2HP and 3HP DCs, A 2HP (19") BS, and a bunch of other fans and power tools,
The start up currents I can see on my monitoring gear are only small snapshots of what is going on while the devices start up and in actuality will be even higher than what I describe.
The the highest start up currents the BS and DC show for a brief period are ~35A and 25A respectively.
For both machines it takes about 3 seconds for the current to settle to a free running current of 6 A.
The BS and DC have been connected to the same 10A GPO and a 15A breaker circuit and they run fine.
They also run from an expander board with a 10A breaker without tripping.
Of course other DCs and BS may vary.
-
31st July 2013, 09:12 PM #26Senior Member
- Join Date
- Jun 2013
- Location
- Geelong
- Posts
- 428
-
31st July 2013, 10:03 PM #27
249 volts confirmed
-
31st July 2013, 10:39 PM #28.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,793
-
1st August 2013, 02:06 AM #29Retired
- Join Date
- May 2012
- Location
- Canberra
- Posts
- 1,820
Good discussion. I'm about to get in a sparky to discuss upgrading the shed. I'm popping fuses.
Time to dig out the volt-o-matic and check my peaks.
This place has old wiring, no doubt done on the cheap.
-
1st August 2013, 08:37 AM #30
I had a chat to a Sparky and as the mancave is wired with 4mm instead of the usually 2.5mm I can replace the current 20A CB with a 32A CB
This should keep me out off trouble for a while.
Similar Threads
-
Spindle plug
By warrick in forum CNC MachinesReplies: 11Last Post: 21st October 2012, 05:58 PM -
Plug-It conversion
By elanjacobs in forum FESTOOL FORUMReplies: 1Last Post: 4th June 2011, 10:44 AM -
little plug for aeg
By Farm boy in forum HAND TOOLS - POWEREDReplies: 0Last Post: 22nd December 2010, 07:31 PM -
Plug cutter
By wcarey in forum HAND TOOLS - POWEREDReplies: 1Last Post: 20th June 2000, 12:24 AM