    Default Do I really need a 15 AMP plug

    Hi WWF

    I am looking to purchase the Hafco BP-430 bandsaw. It has. 2hp motor and comes with a 15amp plug. I forgot to look at the plate on the motor when I was in the shop so don't know the exact current it draws. However using the following
    Electrical Motor Calculator

    and using default values for efficiency and power factor I think I t needs about 6 amps. Thus a 10amp plug should be fine.


    i also have the Hafco Dust extractor which also has a 2hp motor and only a 10amp plug.


    Anyone see any major flaws in my logic?

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Nov 2007
    Location
    Dundowran Beach
    Age
    76
    Posts
    19,922

    Post

    Get yourself a 15amp circuit and plug. That way no problems.

  4. #3
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    It looks like they might have been a bit sloppy with the cutting and pasting from larger machines on the website.

  5. #4
    Join Date
    Aug 2011
    Location
    Brookfield, Brisbane
    Age
    49
    Posts
    1,128

    Default

    Quote Originally Posted by BobL View Post
    It looks like they might have been a bit sloppy with the cutting and pasting from larger machines on the website.
    Thanks for the reply Bob.

    I actually eyeballed the machine and it does actually have a 15A plug end

  6. #5
    Join Date
    May 2010
    Location
    Not far enough away from Melbourne
    Posts
    4,204

    Default

    Quote Originally Posted by Damienol View Post
    i also have the Hafco Dust extractor which also has a 2hp motor and only a 10amp plug.


    Anyone see any major flaws in my logic?
    Hi again Damienol,

    I noticed that too on H&F website when I was looking at that saw on your behalf for another post. I almost mentioned in my reply that I did not think it needed a 15 amp plug as it is only 2hp motor and single phase.

    I would be cautious, however, of running the 2hp saw and the 2hp dusty off the same circuit. Do not under any circumstances start them both on the same 10 amp circuit at the same time as start-up current is much higher than running current. Use common sense, if the circuit breaker trips more than once, try accessing another circuit for each machine even if it means running an extention lead from another circuit in the house.

    In any case, if you follow the following advice from BobL in another thread, you cant go wrong

    Quote Originally Posted by BobL View Post
    The 30A circuit breaker (CB) will be either a Stove/Oven or Aircon or HWS.
    The 15A CBs protect the standard 10 A outlets inside the house, (usually 20 or 25 A CBs are used to protect 15A outlets and standard installation is one outlet per breaker).
    The 15A designation is nominal continuous value but it can handle slightly higher currents for a brief period.

    FIRST THE DISCLAIMER ** If you are not confident of doing the following call in a sparky to tell you what is going on **

    Since there is no CBB in the shed and you cannot identify a specific shed CB in the house CBB, you need to determine which of those CBs in the house CBB, controls the shed.
    Do this by connecting an appliance (something like a desk lamp is the safest thing to use) to an outlet in the shed and turning it on and then turning the House CBs of-on systematically. Then you need to work out if that CB is for the shed alone, or if it connected to one of the house circuits by testing for power using the desk lamp on all the house outlets. If none of the house circuits are affected then that CB is for the shed alone.

    If that CB is connected to one of the house circuits then you will need to check what appliances are running on the circuit. if they are all small appliances like power adapters then you can pretty much ignore these. However if they are high current continuous devices appliances like dryers or air conditioners then you need to take these into account

    Assuming that you can identify a 15A CB that is dedicated to the shed then . . . .
    If the Ledacraft is a 1.5HP that means it will draw ~4A free running and ~6A under working load.
    This pretty much restricts you to a 2HP (~6A) since a 3HP draws about 10 A which when added to the saw will send you over the 15A limit .
    A 3HP unit requires a 15A GPO and a dedicated 20-25A CB because the start up currents can be much higher than 15A which will trip a 15A CB.

    If the line to the shed is part of one of the house circuits then the currents drawn by any large appliances in the house that use the same circuit should be included in the calculation.

    The other thing to note is that it is not just a question of changing the CBs in the house CBB. The other limit to total current is the wire diameter.
    The line running to the shed can probably only cope with a continuous max of 10 A so swapping the 15A CB on that circuit for a 20A could cause overheating on that line and lead to a fire.

    Either way it seems if you want to run a 3 HP or greater DC you would need to upgrade your connection to the shed.
    I got sick of sitting around doing nothing - so I took up meditation.

  7. #6
    Join Date
    Dec 2010
    Location
    Mornington Peninsula
    Posts
    2,743

    Default

    Typically, I like pushing the limits. However, in this case, if it came with a 15 AMP plug and was electrically approved with it - do not alter it. To do so will definitely void your insurance.

    As an aside, you could contact the electrical approval authority, to verify what rating of plug and lead can be used with the bandsaw on the approval certificate. If it was approved with an alternate 10 AMP plug, then if you wished, change it.

  8. #7
    Join Date
    Jun 2013
    Location
    Geelong
    Posts
    427

    Default

    Quote Originally Posted by doug3030 View Post
    Hi again Damienol,

    even if it means running an extention lead from another circuit in the house.
    Running an extension lead from another circuit in the house will probably mean a drop in voltage and will lead to the premature death of whatever is plugged in.

    Start Amps are often quoted as 3 to 5 times the run Amps, not accurate but a good guide, possibly 30 Amps on that circuit. The saw manufacturer or reseller should be able to answer why it has a 15 Amp plug. However it is generally 10 Amp plug on 2 hp and 15 Amp on 3 hp. If all else fails call a sparky for a quote on a 15Amp circuit, quotes are free and may come with a solution.

  9. #8
    Join Date
    Aug 2011
    Location
    Brookfield, Brisbane
    Age
    49
    Posts
    1,128

    Default Reply to doug3030

    Thanks Doug

    I have already experienced a tripped circuit when firing up my shopvac while the Dusty was booting up. Timing is key.

    The man cave is wired with 4mm 2CE so significantly larger then normal house wiring so no probs there with overheating. The old man is a sparky so might ask him if it worth changing the CB

    The old man has also suggested that if worst comes to fruition he can installed a 15Amp GPO in the CB box and I will just have to run an extension lead to the bandsaw every time I need to use it. Not ideal however significantly more palatable then forking out $1000 plus to run another circuit to the man cave.

  10. #9
    Join Date
    Aug 2011
    Location
    Brookfield, Brisbane
    Age
    49
    Posts
    1,128

    Default Reply to Wrongwayfirst

    Thanks for your response Wrongwayfirst

    Re the extension lead comment, I have 250v to the house so any drop in voltage incurred through the use of an extension lead should be palatable

  11. #10
    Join Date
    May 2010
    Location
    Not far enough away from Melbourne
    Posts
    4,204

    Default

    Quote Originally Posted by Damienol View Post
    Thanks for your response Wrongwayfirst

    Re the extension lead comment, I have 250v to the house so any drop in voltage incurred through the use of an extension lead should be palatable
    And I am sure that "the old man" will ensure that you are using a properly approved 15 amp lead and hopefully it will be no longer than 30 metres so all would be good.
    I got sick of sitting around doing nothing - so I took up meditation.

  12. #11
    Join Date
    Aug 2011
    Location
    bilpin
    Posts
    3,559

    Default

    A shed without a 15amp socket is not a real shed.

  13. #12
    Join Date
    May 1999
    Location
    Tooradin,Victoria,Australia
    Age
    73
    Posts
    11,918

    Default

    ADDED BY ADMIN

    DISCLAIMER

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.
    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk

  14. #13
    Join Date
    Aug 2011
    Location
    Brookfield, Brisbane
    Age
    49
    Posts
    1,128

    Default Looks pretty real to me

    Quote Originally Posted by rustynail View Post
    A shed without a 15amp socket is not a real shed.
    Still sticking with the line rustynail?

    image.jpgimage.jpgimage.jpgimage.jpg

  15. #14
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    Quote Originally Posted by Damienol View Post
    Thanks for your response Wrongwayfirst

    Re the extension lead comment, I have 250v to the house so any drop in voltage incurred through the use of an extension lead should be palatable
    Yikes 250V - have you actually measured it?
    We routinely get 244-245 but don recall seeing a 250 since the 1980s around here.
    A rumour I heard was the state supplier recently cranked up the voltage to put back pressure on the home photovoltaic systems?

  16. #15
    Join Date
    Dec 2010
    Location
    Melbourne
    Age
    79
    Posts
    601

    Default

    Quote Originally Posted by BobL View Post
    Yikes 250V - have you actually measured it?
    We routinely get 244-245 but don recall seeing a 250 since the 1980s around here.
    A rumour I heard was the state supplier recently cranked up the voltage to put back pressure on the home photovoltaic systems?
    Can you please explain a bit more about this,thanks

    Back pressure I mean??

Page 1 of 4 1234 LastLast

Similar Threads

  1. Spindle plug
    By warrick in forum CNC Machines
    Replies: 11
    Last Post: 21st October 2012, 05:58 PM
  2. Plug-It conversion
    By elanjacobs in forum FESTOOL FORUM
    Replies: 1
    Last Post: 4th June 2011, 10:44 AM
  3. little plug for aeg
    By Farm boy in forum HAND TOOLS - POWERED
    Replies: 0
    Last Post: 22nd December 2010, 07:31 PM
  4. Plug cutter
    By wcarey in forum HAND TOOLS - POWERED
    Replies: 1
    Last Post: 20th June 2000, 12:24 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •