    Would these switches be any good for general workshop applications??


    Power Pushbutton Switch TBSP-330 3P 30A 3.7KW New $6.50 Delivered

    Power Pushbutton Switch TBSP 330 3P 30A 3 7KW NEW | eBay

    Item Description:

    ON locked
    3P 30A 3.7KW
    Contact switch : N.O. x 3 (3A, 3 termanil)
    Dimension : L90 x W45.5 x H51mm


    …..Live a Quiet Life & Work with your Hands

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Nov 2006
    Location
    Bendigo Victoria
    Age
    80
    Posts
    16,560

    Default

    Other than the fact it doesn't appear to be a No Volt Release switch, with which most new machines are now fitted, it should the job.

    Added advantage is it will work with a wireless remote control (think dust extractor) which NVR switches won't.

  4. #3
    Join Date
    Feb 2012
    Location
    Nowra, NSW, Australia
    Age
    65
    Posts
    3,003

    Default

    Good price. It appears to have been intended for 120V use, (3.7kW / 30A = 123V), but if it's only switches with no internal electronics it should be fine.

    Check this out. (The usual price in Oz?): TBSP-330
    ( GST is already included. Must be $59 GST. )
    ... Steve

    -- Monkey see, monkey do --

  5. #4
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    3,277

    Default

    Quote Originally Posted by Hermit View Post
    Good price. It appears to have been intended for 120V use, (3.7kW / 30A = 123V), but if it's only switches with no internal electronics it should be fine.

    So would that overheat on 240V or require work to use on 240V…. I basically just want something that I can splice into the flex on the back of the motor and screw to the bench. Most of my old equipment has to be turned on and off at the power point which means walking to the other side of the garage to where a long extension lead plugs into the wall.
    …..Live a Quiet Life & Work with your Hands

  6. #5
    Join Date
    Feb 2012
    Location
    Nowra, NSW, Australia
    Age
    65
    Posts
    3,003

    Default

    Quote Originally Posted by DSEL74 View Post
    So would that overheat on 240V or require work to use on 240V…. I basically just want something that I can splice into the flex on the back of the motor and screw to the bench. Most of my old equipment has to be turned on and off at the power point which means walking to the other side of the garage to where a long extension lead plugs into the wall.
    I just found another listing, with more info. It's intended for 3-phase. Hence the three sets of contacts. Just use either one or two of the pairs of contacts, depending on whether you want to wire it for double-pole or single-pole operation. (Double-pole is safer, because it disconnects both wires from the supply when off.) Leave the third pair of contacts unused.
    Quote Originally Posted by eBay
    Name of Product: Power Pushbutton Switch
    Model: TBSP-330(CBSP-330 is the same)
    Type: 3 Phase
    Current: 30A
    Power: 3.7KW
    Connection terminal: M4
    Total Size (Approx.): 90*45*50.5mm(L*W*H)
    Material of Shell: Plastic
    It should be fine on 240VAC. It's the current that's most important, so keep comfortably below 30A and it shouldn't get over hot. 30A is about 5HP, so a typical 1/2HP to 3HP motor will be no problem, I'd say.
    ... Steve

    -- Monkey see, monkey do --

  7. #6
    Join Date
    Oct 2007
    Location
    Alexandra Vic
    Age
    69
    Posts
    2,810

    Default

    Because they don't list a voltage rating for the unit I would be very wary of using them for mains switching here.

    Voltage rating is very important as it establishes the seperation between contact sets in the switch internals, the size and type of insulation barriers between the contact sets, and the open gap between contacts in a particular set. All of these factors are critical in controlling contact arcing when switching inductive loads like motors.

    It is possible on first thoughts to deduce that the contacts are rated at 120 volt from the supplied specification 3.7KW, 30 A (W = A x V so V = W/A or 3700/30). My gut feeling from the limited spec is that the unit is intended for switching a resistive load like a set of heating elements, rather than inductive loads like motors which will always cause contact arcing. It is normal practice to provide a significant safety factor for contact voltage and currrent ratings when selecting switches for motors, and to my mind, the lack of a voltage spec means that the units are not fit for the intended purpose.

    Despite the fact that the units are also being supplied locally by a wholesaler (Tobins link), I doubt that they are type approved for Australian use and could legally therefore only be incorporated into products where the designer/manufacturer will be responsible for a; establishing that the design parameters are suitable for the application and b; documenting the design and submitting the final product for type approval. In Oz we are generally well protected by our electrical type approval requirements, to the extent that we either forget that it exists, or assume that everything we want to use has type approval for our intended application.

    Hope that this helps you, even if it isn't the answer you were hoping for.
    I used to be an engineer, I'm not an engineer any more, but on the really good days I can remember when I was.

  8. #7
    Join Date
    Jan 2011
    Location
    Ormeau, Gold Coast, Australia
    Posts
    2,491

    Default

    I've bought similar from china andnyhey have been fine.
    Regards Rumnut.

    SimplyWoodwork
    Qld. Australia.

  9. #8
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    I just wanted to report that I purchased one of those switches referred to by the OP and they look reasonably robust both inside and out. In fact it looks identical in terms of the internal structure to the original switch on my Romac metal cutting bandsaw but is much more robust that the old Romac switch on the outside. I wouldn't be asking it to carry 30A but for single phase 10A it will be fine.

    The plastic surround on my Romac switch didn't like the lube/coolant/swarf being splashed around on it too much and eventually part of the plastic surround disintegrated a few weeks ago.
    I replaced the Romac switch with a Schiender 16A rated no-volt switch I found for $36 (including delivery) from RadioSpares.
    Buy Push Button Switches IP65 DP Panel Mount On-Off Push Button Switch, 16 @ 230 V ac/dcA EICHOFF 3251-20-01/67 online from RS for next day delivery.

    Normally priced at $54, at $36 it's pretty hard to beat, making it as cheap or cheaper than many of the chinese no-volt switches being sold mainly through ebay UK.

  10. #9
    Join Date
    Nov 2010
    Location
    Gippsland Victoria
    Posts
    706

    Default

    Quote Originally Posted by DSEL74 View Post
    …. I basically just want something that I can splice into the flex on the back of the motor and screw to the bench. Most of my old equipment has to be turned on and off at the power point which means walking to the other side of the garage to where a long extension lead plugs into the wall.
    Hello,

    Not what you were asking but perhaps a viable alternative ? Have a standard cradle beside each machine to house the remote.

    I bought some remote controlled power outlets from Aldi - 4 for approx $15ish. Other places will probably have similar.

    The gadget is smaller than a double adaptor, it plugs into the wall then you plug your extension cable into the gadget - It is controlled by a remote like a TV remote to switch the power on at the wall.

    Some pictures here https://www.google.com/search?q=remo...ed+power+point

    No need to walk to far end of workshop. But not a proper safety switch either.


    Bill

Similar Threads

  1. Looking for safety switches???
    By TTIT in forum GENERAL & SMALL MACHINERY
    Replies: 4
    Last Post: 4th February 2012, 12:44 AM
  2. cutout switches
    By REALOldNick in forum SAFETY
    Replies: 21
    Last Post: 14th June 2011, 11:40 PM
  3. switches
    By Tonyz in forum WOODWORK - GENERAL
    Replies: 13
    Last Post: 15th September 2007, 09:57 PM
  4. Foot Switches
    By rrich in forum SAFETY
    Replies: 6
    Last Post: 15th April 2006, 03:44 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •