    Default 10A / 15A confusion

    I'm a little confused by why some of the available table saws have the 15A plugs. For example a couple of the Hafco saws have 15A plugs, but are rated below 2400 watts (eg. one is 2250W). My memory of high-school physics tells me that A = P/V, so the current that this saw pulls would be 2250 / 240 = 9.375A.

    We have a portable electric heater that's rated at 2400W, yet it doesn't need to run on a special 15A circuit. A friend who knows much more about building wiring than I do suggested that it would probably be OK to run the above saw on a regular household circuit provided it was the only thing on it and it was only getting light use.

    Opinions? Anyone out there running 15A saws on regular circuits/plugs?

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    12,881

    Default

    In short, a motor draws more current at start than a heater does.

    The motor may be rated at 2400W (10A) but it will draw more current at start up.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  4. #3
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    523

    Default

    Quote Originally Posted by Zzz. View Post
    My memory of high-school physics tells me that A = P/V, so the current that this saw pulls would be 2250 / 240 = 9.375A.
    Correct for DC. For AC under what we call steady-state-sinusoidal (SSS) excitation (i.e. after all the transitions have decayed), the AC current is:

    I = P/(VxPF)

    where PF is the power factor. Typically about 0.9 for a motor.

    Quote Originally Posted by Zzz. View Post
    Anyone out there running 15A saws on regular circuits/plugs?
    I do it all the time. No problems.

  5. #4
    Join Date
    Sep 2007
    Location
    Hervey Bay
    Posts
    559

    Default

    Just be aware that if you do go this route (running something with a 15 amp plug on a 10 amp circuit) you are most likely voiding your warranty.

    I speak from experience.

  6. #5
    Join Date
    May 2007
    Location
    South Australia
    Posts
    135

    Default

    Iv run my Makita SCMS off a powerpoint shared with a light, you can see the voltage dip and thats only a 1600w motor

  7. #6
    Join Date
    Feb 2008
    Location
    Deloraine Tasmania
    Age
    59
    Posts
    1,092

    Default

    I run my 12" table saw, thicknesser & jointer off a 10A socket via a short extension lead with a 15A power cord. This is only temporary till i have my shed setup & wired in as i want. Things to remember if u choose to do this,
    1; make sure you use a good quality heavy duty power cord for the extensoin lead & make it as short as practical, preferably under 5m.
    2; Only opperate 1 major piece of machinery on the outlet at a time. I run 1 major machine & a dust extractor on the single outlet & have never yet tripped out the breaker. In your switchboard your 10amp lines should have 20amp breakers so running a 15amp unit on them is no prob long as you don't load too many things on each line.
    3; As Switt said doing so will actually void your warranty so keep the extensoin cord short to minimise voltage drops. The voltage drop is noticable, when i plugged in my table saw for the first time the only power cord i had was a 20M cord with a 15A plug i use for the caravan. when i made up a dedicated extension cord thats only 3m long the sound of the spin speed was noticably higher especally when the blade was under load.

  8. #7
    Join Date
    Nov 2008
    Location
    Canberra
    Posts
    13

    Default

    Thanks all for the replies. It sounds like it wouldn't be too great a risk provided I take some of the precautions suggested. It certainly widens the selection of saws to consider.

    Cheers.

  9. #8
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    523

    Default

    Quote Originally Posted by switt775 View Post
    Just be aware that if you do go this route (running something with a 15 amp plug on a 10 amp circuit) you are most likely voiding your warranty.

    I speak from experience.
    I can't see any technical reason why this would void the warranty. Maybe if you changed the 15A plug on the equipment to a 10A plug, they supplier may claim it was modified?

    It seems to me that the supplier was using this excuse as a convenient out.

  10. #9
    Join Date
    Feb 2008
    Location
    Deloraine Tasmania
    Age
    59
    Posts
    1,092

    Default

    ZZZ i would never recommend you do this on a perminant basis, only as a stop gap measure till you can get a dedicated 15A socket put in.
    Crisp the techincal reason is that as i mentioned you get voltage drops to the motor which can prematurely burn it out voiding your warranty so leaving the 15A plug on the unit is a good idea warranty wise.

  11. #10
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    523

    Default

    Quote Originally Posted by Rattrap View Post
    Crisp the techincal reason is that as i mentioned you get voltage drops to the motor which can prematurely burn it out voiding your warranty so leaving the 15A plug on the unit is a good idea warranty wise.
    Let's see.

    10A circuit: up to 15 outlets (or more now), 2.5mm2 cable, 16A or 20A breaker

    15A circuit: 1 outlet, 2.5mm2 cable, 16A or 20A breaker

    The only real difference is the number of items you can put on the circuit. This means the 10A outlet is more susceptible to nuisance tripping if there is anything else on the circuit at the same time. If it is the only item using the 10A circuit there is no practical difference.

    Hardly a valid technical reason to deny a warranty claim.

  12. #11
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    85
    Posts
    3,737

    Default

    As Chrisp says there is no difference in the cable that is used in a 10amp circuit to a 15amp circuit except for the number of points on the circuit. Provided there is nothing else plugged into any of the points on the circuit the 2.5mm2 cable will take the start up draw of the machine.

    The difficulty is that you have to know where all the 10amp points are to make sure nothing else is plugged in like a heater or something similar.

    I suppose we will have to watch out for all the electrical police for giving advise on electrical subjects.

  13. #12
    Join Date
    Nov 2008
    Location
    Canberra
    Posts
    13

    Default

    Quote Originally Posted by Barry_White View Post
    I suppose we will have to watch out for all the electrical police for giving advise on electrical subjects.
    Nah, the debate is good - it's helping me conduct my own assessment of the risks. Some people are placing greater emphasis on some factors than others - that's why we all reach different conclusions, because different things matter to each of us.

    In my case, it seems like low risk because the saw would only have light use and I would ensure that nothing else was being used on the circuit (16A circuit breaker) at the same time. I suspect the garage might even be on its own circuit, which would be even better.

    Cheers.

  14. #13
    Join Date
    Nov 2008
    Location
    Sydney
    Posts
    53

    Default

    What you plug in where is your own business, as is how you go about it. I know I'm going to regret this, but in case you don't know, a 15A plug is designed for a 15A plug. A 15A power point must be on its own dedicated circuit. This is the legal way. Just letting you know in case you aren't aware of it.

  15. #14
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    58
    Posts
    12,779

    Default

    There are only three ways I know of that you could run a 15a plugged saw on a 10a circuit:

    1. Replace the 15a plug with a 10a plug
    2. Make up an extension cord with a 15a socket and a 10a plug
    3. Replace a 10a power point with a 15a power point

    Option 1 would certainly void your warranty. Option 2 probably would too. If they found out that is. Option 3 is illegal. Take your pick
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  16. #15
    Join Date
    Mar 2007
    Location
    Munruben, Qld
    Age
    83
    Posts
    10,027

    Default

    Quote Originally Posted by silentC View Post
    There are only three ways I know of that you could run a 15a plugged saw on a 10a circuit:

    1. Replace the 15a plug with a 10a plug
    2. Make up an extension cord with a 15a socket and a 10a plug
    3. Replace a 10a power point with a 15a power point

    Option 1 would certainly void your warranty. Option 2 probably would too. If they found out that is. Option 3 is illegal. Take your pick
    I use method 2 and had no problems using my TS. But don't tell anyone.
    Reality is no background music.
    Cheers John

Page 1 of 2 12 LastLast

Similar Threads

  1. Transcribing Confusion
    By Rodgera in forum WOODIES JOKES
    Replies: 2
    Last Post: 24th May 2008, 03:41 PM
  2. Thicknesser Confusion
    By E. maculata in forum JOINTERS, MOULDERS, THICKNESSERS, ETC
    Replies: 7
    Last Post: 21st March 2005, 05:52 AM
  3. Router bit confusion.
    By LineLefty in forum ROUTING FORUM
    Replies: 20
    Last Post: 13th December 2004, 12:40 PM
  4. Confusion
    By craigb in forum WOODTURNING - GENERAL
    Replies: 1
    Last Post: 7th February 2004, 05:12 AM
  5. Bandsaw confusion …..
    By Sir Stinkalot in forum BANDSAWS
    Replies: 11
    Last Post: 29th July 2003, 10:08 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •