    Question I have $3,000 for a Table Saw. But I rent! 10Amp/15Amp??

    Hey All,

    Over the last 4 months I have been enjoying reading all the wonderful posts regarding workshops and equipment on here, so many super tips from you all! Now I have a question for you all..

    We are planning to move buy our first home in around 12 months. I will be working with local hardwood (Red gum, Mulga, Other Central Aust hardwoods) and softwoods (Cypress pine, plywood, chipboard)

    So.. What would you all recommend?

    Option 1 *Wait 12 months until we buy a house and then grab a 3HP saw 15 Amp saw, which I will have wired in appropriately.

    Option 2 *Buy a 10 amp saw which I can move around.. Actually! What size motor can I run with 10 Amps?


    Thanx for your input.

    Miko
    Last edited by Miko Zaire; 29th January 2014 at 11:40 PM. Reason: Update:

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    FenceFurniture's Avatar
    FenceFurniture is offline The prize lies beneath - hidden in full view
    Join Date
    Oct 2010
    Location
    1017m up in Katoomba, NSW
    Posts
    10,662

    Default

    Miko, I too am in a rental property, but I needed two x 20A circuits. The simple solution was to set up the electrickery so I can take it with me.

    It depends on how long the run is from the power box to the shed. You could install a 15A circuit with a GPO very close to that (to limit the length of flat cable installed by the electrician), and then run a 15A extension lead to the shed from there. Maybe have the lead inside conduit or, as I did, 40mm water drainage pipe which is significantly cheaper than conduit.

    The cost of the Sparky for this would be minimal. If it's a longish run to the shed you could use 20A flex for the extension lead, but you would need advice from a licenced Sparky on that.

    HTH
    Brett
    Regards, FenceFurniture

    COLT DRILLS GROUP BUY
    Jan-Feb 2019 Click to send me an email

  4. #3
    Join Date
    Dec 2013
    Location
    Australia
    Posts
    67

    Default

    Quote Originally Posted by FenceFurniture View Post
    Miko, I too am in a rental property, but I needed two x 20A circuits. The simple solution was to set up the electrickery so I can take it with me.

    It depends on how long the run is from the power box to the shed. You could install a 15A circuit with a GPO very close to that (to limit the length of flat cable installed by the electrician), and then run a 15A extension lead to the shed from there. Maybe have the lead inside conduit or, as I did, 40mm water drainage pipe which is significantly cheaper than conduit.

    The cost of the Sparky for this would be minimal. If it's a longish run to the shed you could use 20A flex for the extension lead, but you would need advice from a licenced Sparky on that.

    HTH
    Brett


    Thank you Brett for you rapid response! The shed is powered with 4 double plug 10Amp switches. The power box main is about 30mtrs from the shed (other side of the house, as far away as it possibly could be).

    So you would recommend getting a 20 amp socket put in at the mains and run a 15 Amp lead to the shed? Leaving the owner with a new switch? I guess if it is not over $150 but I cannot take it with me though..

    Miko

  5. #4
    Join Date
    Aug 2004
    Location
    Perth WA
    Posts
    2,035

    Default

    Buy your saw now and replace one of the 10amp GPO covers/plates with a 15amp GPO cover/plate. All that will happen is the switch in the box may trip.
    Experienced in removing the tree from the furniture

  6. #5
    Join Date
    Nov 2006
    Location
    Bendigo Victoria
    Age
    80
    Posts
    16,560

    Default

    Instead of interfering with the elecktrickery in your rented place maybe consider one of these?

    Portable RCD with 15A to 10A Mains Plug Conversion - Jaycar Electronics

  7. #6
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    It's along shot but what you need to find out is if the shed circuit has its own breaker back at the house CB box.

    If it does then you may be able to safely run a 3HP/15A saw in the shed provided you run nothing else except perhaps a light at the same time. It is unlikely for example that you would be able to run a DC on the same circuit at the same time.

    The fact that there will be a plug compatibility issue is for you to resolve.

    The main reason that 3HP saws use a 15A plug and dedicated circuit is because the start up currents can very briefly (e.g. ~2s) be as high as 50A.
    The breakers in most 10A circuits are usually something like 20A breakers but are normally designed to cope with 50A start up current for a couple of seconds, but only if there is not already something else that draws a high current, like an electric kettle or an air con, running on the same circuit.

    A 15A dedicated circuit will often use the exact same breaker (20A) as the 10A circuit

    You should be aware that a motor rated at 3HP/15A is just a nominal rating for a motor.
    My 3HP/15A TS only draws ~6A when it is free running, about 8A when doing light cuts, ~10A when doing intermediate cuts, 12A on heavy cuts and it will continue to draw current up to 17A before the motor (not the 20A breaker) trips. When I connected it to a 10A power circuit with nothing else running on that circuit it starts fine and runs fine even when doing heavy cuts, and I could not get the 20A Breaker to trip before the motor tripped.

    Edit - Just read BS post and agree that this device is by far the easiest route - but given it is rated only to 10A it may still trip on starting - I would definitely try or find out before buying.
    If the breakers in the house keep tripping you will just have to keep turning other devices off until the breakers stop tripping.
    It is unlikely that Jaycar will know what that thing does, what we need is someone that has one and has tried it out on their TS.

  8. #7
    Join Date
    Sep 2007
    Location
    Hervey Bay
    Posts
    559

    Default

    There are several ways (as above posts prove) to run a 15 amp saw on a 10 amp circuit. But you can expect that your warranty will be void if you do so and the motor fails (for any reason).

    Voice of experience.

  9. #8
    FenceFurniture's Avatar
    FenceFurniture is offline The prize lies beneath - hidden in full view
    Join Date
    Oct 2010
    Location
    1017m up in Katoomba, NSW
    Posts
    10,662

    Default

    Quote Originally Posted by Miko Zaire View Post
    So you would recommend getting a 20 amp socket put in at the mains and run a 15 Amp lead to the shed? Leaving the owner with a new switch? I guess if it is not over $150 but I cannot take it with me though..

    Miko
    Exactly, except I'll be taking the circuit board stuff with me as well.
    Regards, FenceFurniture

    COLT DRILLS GROUP BUY
    Jan-Feb 2019 Click to send me an email

  10. #9
    Join Date
    Dec 2013
    Location
    Australia
    Posts
    67

    Cool

    Thanx Guys! A lot of great ideas.

    It so happens that the shed has it's own dedicated circuit, unfortunately the lights and all switch's run off the same line. My uncle is a sparky over in Bingara NSW so I asked him today about how it would fair, he said "It would work no worries, but it is not a good idea". Just as you guys have mentioned

    -It is possible but there are added risks, I had a conversation with the wife and outlined those risks.. So now we have both agreed to hold off on the saw purchase until we get our own place, but then I have permission to rewire and deck out the shed to my desires, I can not disagree with that. I think I might be better off in the long run.

    I guess I will have to turn my focus back to milling timber with my Alaskan mill in preparation for my new work shop later this year.

    I appreciate all the good will and good ideas guys. Thanx

    Miko

    p.s Anyone want to trade for some Desert timbers? I would love some Tassie or north QLD species.


  11. #10
    Join Date
    Oct 2003
    Location
    Canberra
    Age
    48
    Posts
    1,484

    Default

    Don't write off a saw that runs off 10a. I've got a jet cabinet saw - it runs on 10a, and came complete witha 10a plug. Not sure what he power of the motor is, but it doesn't ever have any problems in practice, which is all that counts. I can run a dado stack or rip 50-60mm hardwood without trouble.

    Trav
    Some days we are the flies; some days we are the windscreen

  12. #11
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    Quote Originally Posted by Trav View Post
    Don't write off a saw that runs off 10a. I've got a jet cabinet saw - it runs on 10a, and came complete witha 10a plug. Not sure what he power of the motor is, but it doesn't ever have any problems in practice, which is all that counts. I can run a dado stack or rip 50-60mm hardwood without trouble. Trav
    It probably has a 2HP/10A motor rebranded as a 3HP/15A on other machinery.

  13. #12
    Join Date
    Nov 2007
    Location
    Dundowran Beach
    Age
    76
    Posts
    19,922

    Post

    I don't know how long it will be until you purchase your own home
    so think of this; the dollar is falling and the price of saws will rise.

    Will you be better off to buy your saw and store it until you have
    your own place?

  14. #13
    Join Date
    Dec 2013
    Location
    Australia
    Posts
    67

    Talking Guess who bought a house :)



    Yep! The money just came through and in 3 weeks we will be living in our own home! I even have an 8 x 4 mtr powered shed which I plan to upgrade the power in.. So now..


    Who has a 12 inch saw they can recommend? What seems to be the best deal or design relating to a 12 inch saw in the current market?

    My budget is now reduced to around $2,000 anyone have any recommendations?

    Woot yeah!

    Miko

  15. #14
    Join Date
    Nov 2007
    Location
    Albury Well Just Outside
    Posts
    13,315

    Default

    Quote Originally Posted by Miko Zaire View Post
    .... I even have an 8 x 4 mtr powered shed which I plan to upgrade the power in.....

  16. #15
    Join Date
    Nov 2007
    Location
    Dundowran Beach
    Age
    76
    Posts
    19,922

    Thumbs up

    Great to hear Miko!!!

    My prediction about the dollar has not been entirely accurate! Lucky you!!

    I had a look at the Laguna saws at The Bris.WWW show. Very nice units but no idea of price.

    Other than that Jet has a good reputation and I think someone here reviewed a Harvey. Have a look in the reviews forum.

    And good luck!!

Page 1 of 2 12 LastLast

Similar Threads

  1. 10amp to 15amp
    By Andrew_B in forum THE SHED
    Replies: 3
    Last Post: 28th January 2012, 11:27 PM
  2. 15amp welders on 10amp circuits
    By welding in forum WELDING
    Replies: 3
    Last Post: 26th December 2010, 02:45 PM
  3. 15amp welders on 10amp circuits
    By r_i_l_e_y in forum WELDING
    Replies: 173
    Last Post: 24th November 2010, 11:51 PM
  4. CTJ 680 on 10amp power supply
    By SpiritLevel in forum JOINTERS, MOULDERS, THICKNESSERS, ETC
    Replies: 5
    Last Post: 10th November 2008, 12:49 PM
  5. 'New'? 10amp 240v remote switch
    By bsrlee in forum GENERAL & SMALL MACHINERY
    Replies: 9
    Last Post: 23rd May 2008, 10:20 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •