    I bought a K3 about a year ago and was advised by Felder to put it on a 20Amp circuit - which I did. Apparently at start-up it can pull 18 or so amps. Given the cost of the K3 versus the few hundred dollars to get a 20 Amp circuit installed it was, for me, an easy choice

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Mar 2015
    Location
    Melbourne, Vic, Australia
    Posts
    1,255

    Default

    Not sure why people worry about start up current. The start up current would only last for a few seconds and so would probably need to be 100-200 amps to trip a 15 or 20 amp breaker in that time.

  4. #18
    FenceFurniture's Avatar
    FenceFurniture is offline The prize lies beneath - hidden in full view
    Join Date
    Oct 2010
    Location
    1017m up in Katoomba, NSW
    Posts
    10,662

    Default

    Quote Originally Posted by Bohdan View Post
    When a single phase motor starts, a starter winding in the motor is energised via a capacitor. This starter current is only required for a brief time to get the motor up to speed.

    It is commonly switched off via a centrifugally activated contact in the motor but these switches are unreliable and often need maintenance.

    It appears that Hammer may be using the start button to control it. You release the button and the start winding is turned off.

    You only need to hold it in until the motor is up to full speed.
    Derek, you should be doing the same with the A3 31, and most probably the BS, given that it has the same motor.
    Regards, FenceFurniture

    COLT DRILLS GROUP BUY
    Jan-Feb 2019 Click to send me an email

  5. #19
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    I have never bothered holding the switch on my single phase A3-31 and it hasn't blown up yet and the saw is three phase. What is the experience of others?
    CHRIS

  6. #20
    Join Date
    Jan 2004
    Location
    Towradgi
    Posts
    4,839

    Default

    When I got my Hammer N4400, I was instructed by qualified electricians to run a "15 amp" dedicated circuit back to a 20 Amp circuit breaker to accommodate any fluctuation in start up amperage. I also use 32 Amp rated power cords, that I got thru my sparky mate. He checked everything before allowing me to play with then then new toy.

    Electrickery only gives you 1 chance, so I get my stuff checked by suitably qualified mates, before modifying anything. Yes I am lucky to have mates like that, but then again, my life is worth more than a couple hours/days of not being able to play.
    Pat
    Work is a necessary evil to be avoided. Mark Twain

  7. #21
    Join Date
    Jun 2017
    Location
    auckland
    Age
    49
    Posts
    21

    Default

    Hi Paul,
    Was wondering if you had one of the AR extractors? if so, how do you find it?

    Cheers
    Elliot

  8. #22
    Join Date
    Sep 2007
    Location
    Perth
    Posts
    6

    Default Dust Extractor Query

    Quote Originally Posted by ejw1234567890 View Post
    Hi Paul,
    Was wondering if you had one of the AR extractors? if so, how do you find it?

    Cheers
    Elliot
    Hi Elliot

    Still not sure how these threads are managed and whether this is where I post a reply - anyway, and assuming it was my earlier mention of a Felder Dust Extractor you are asking about, I have the Felder AF16 extractor which is one of the smaller ones they produce. It's the only one I've owned so I can't compare to anything else. Bought it as part of a package deal with the Hammer gear I bought. What can I say - it does the job. Initially I was a bit disappointed about the amount of the dust that was left suspended in the air after a workshop session. I finished up reducing that dramatically just by ensuring that at every connection was screwed down extra tight - I even ran duct tape around the junction points. All good now.

    Cheers

    Paul

  9. #23
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,791

    Default

    Quote Originally Posted by DomAU View Post
    Not sure why people worry about start up current. The start up current would only last for a few seconds and so would probably need to be 100-200 amps to trip a 15 or 20 amp breaker in that time.
    It depends on the breaker being used.
    A B rated Breaker can handle 5x its current rating for about 12s, or 100 A for a 20A breaker
    A C rated Breaker can handle 10x its current rating for about 5s, or 200 A for a 20A breaker
    A D rated Breaker can handle 20x its current rating for about 2 s, or 400 A for a 20A breaker.

    After those times the tripping currents are the same for these breakers.
    A 20 A breaker can even handle 40A for about 150s.
    This all assumes the wiring can handle it as well so the wiring must meet the maximum currents the breaker can handle.

    Starts up currents are not the same for all machines of the same power rating as it depend on initial load. My 3HP DC has about double the start up current of my 3HP TS, the difference being that a DC impeller starts having to move a full load of air whereas all the TS has to move is the blade.

  10. #24
    Join Date
    Jun 2017
    Location
    auckland
    Age
    49
    Posts
    21

    Default

    thanks paul

  11. #25
    Join Date
    May 2011
    Location
    Dicky Beach Qld
    Posts
    6

    Default Hammer K3 Winner will not stop.

    Our club has a Hammer K3 winner which we love. Many members use it but I'm sure not all hold the ON button for any length of time. May have bearing on my next statement however. Just to swap the thread completely around, our saw won't stop . We can try each of the stop buttons (the main switch, the 2 emergency switches or the slider switch) but only the wall switch will stop it. We're currently seeking advice as noone in the club can read Austrian. Has anyone encountered such a problem?

  12. #26
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    I have no idea but it should be locked out if it isn't already.
    CHRIS

  13. #27
    Join Date
    Jun 2014
    Location
    Foot of the Dandenong Ranges
    Posts
    270

    Default

    You can try using Google Translate with your phone camera on the manual if you cant find an English one online. They speak German in Austria though. There is no Austrian language. Good luck.

  14. #28
    Join Date
    Sep 2009
    Location
    Newcastle
    Posts
    549

    Default

    Major issue if the emergency stop switches don't stop it

    Has someone screwed around with the wiring?

    The emergency switches should be interrupting power directly

  15. #29
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Quote Originally Posted by pippin88 View Post
    Major issue if the emergency stop switches don't stop it

    Has someone screwed around with the wiring?

    The emergency switches should be interrupting power directly
    Mine hasn't got an emergency stop on it but it does have an isolation switch to access the blade.
    CHRIS

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Replacing Segment in Hammer Silent Power Head
    By Chris Parks in forum JOINTERS, MOULDERS, THICKNESSERS, ETC
    Replies: 20
    Last Post: 15th August 2016, 06:12 PM
  2. FAO Felder and Hammer Silent Power users
    By sje-tools in forum JOINTERS, MOULDERS, THICKNESSERS, ETC
    Replies: 13
    Last Post: 8th July 2016, 07:35 PM
  3. Replies: 45
    Last Post: 21st April 2012, 04:42 PM
  4. Impact Hammer vs Rotary Hammer Drill
    By Burnsy in forum HAND TOOLS - POWERED
    Replies: 10
    Last Post: 17th October 2007, 12:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •