    Default 25 mtr extension cord and 2.5 hp compressor

    Are there any issues using a 2.5hp compressor on a 25 meter extension cord. This is from a domestic 240 volt power source - 10 amp.

    The extension cord is from Masters, and was described as ‘Heavy duty’.

    The motor will be running intermittently.

    Just making sure I’m not going to damage something.

    Cheers
    Arron
    Apologies for unnoticed autocomplete errors.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    "Heavy duty" doesn't mean much what you should look out for is the cross sectional area of the conductors in the cable - it should be marked on the cable itself.
    For 2.5HP I'd be using at least a 1.5mm^2 cable - this is usually what Masters and Bunnings sell as HD cable.
    If you wanted to be super sure then for a 25m long cable you may want to go to 2.5mm^2 cable.

  4. #3
    Join Date
    May 2003
    Location
    Central Coast, NSW
    Posts
    3,330

    Default

    I’m pretty sure it’s 1mm, so I won’t be using it.

    I have other shorter, genuinely heavy duty leads - just less convenient.

    Just out of interest, if you did use an underrated extension cord, what exactly would fail - the motor, the cord or the building circuits?

    And does the length of the cord make a difference (provided it’s of adequate gauge) ?

    Thanks for the reply
    Arron
    Apologies for unnoticed autocomplete errors.

  5. #4
    Join Date
    May 2003
    Location
    Central Coast, NSW
    Posts
    3,330

    Default

    Yep, found it on the cable - 1mm.

    So the 2.5hp is out.

    Would you run a 2hp compressor off it?
    Apologies for unnoticed autocomplete errors.

  6. #5
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    Quote Originally Posted by Arron View Post
    I’m pretty sure it’s 1mm, so I won’t be using it.
    I have other shorter, genuinely heavy duty leads - just less convenient.
    Just out of interest, if you did use an underrated extension cord, what exactly would fail - the motor, the cord or the building circuits?
    Building circuits should look after themselves.
    Longer/ thinner cable drops more volts cable heats up - short term it might not be that much of an issue but long term, insulation gets brittle and cracks and . . . .
    Lower V at motor means it has to draw more current to achieve work rate (power) so more overheating of motors.


    Here's a few calcs for a 25m long cable, 240V mains at GPO on a 2.5HP (1863W = 7.8A) load.

    1mm^2 conductor will drop about 13V.
    Power dissipated in cable = Volts x Amps = 13 x 7.8 so the cable is drawing 101W = that's a lot - think of an old incandescent 100W light globe - although it is spread along 25m of cable.

    1.5mm^2 cable drops ~8.3V
    Power is now 65W which is a bit better but still .

    2.5mm^2 cable drops 4.5V
    Power is now ~35W

    This is BRAND NEW cable, older twisted cable with kinks and even lightly corroded plug and socket pins will have higher resistance loads.

  7. #6
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    Quote Originally Posted by Arron View Post
    Yep, found it on the cable - 1mm.

    So the 2.5hp is out.
    .

    Would you run a 2hp compressor off it?
    Not really - 25mm x 1mm^2 is about a 1kW cable ie ~1.3HP

    Just checked the regs which allow for a 5% V drop and the above combo is 3.5% so it is within spec.

  8. #7
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    You can find the V drop calculator here
    Voltage drop calculator AS/NZS3008 | jCalc.NET

  9. #8
    Join Date
    May 2003
    Location
    Central Coast, NSW
    Posts
    3,330

    Default

    Ok, thanks for all that Bob.
    Cheers
    Arron
    Apologies for unnoticed autocomplete errors.

  10. #9
    Join Date
    Feb 2003
    Location
    back in Alberta for a while
    Age
    68
    Posts
    12,006

    Default

    In my experience, "heavy duty" typically means that the insulation is thicker than normal, so the cable can withstand a little bit of physical abuse.

    In the past Bunnings (or Mitre 10) sold a "15 Amp extension cable" which was fitted with 10 Amp plugs each end.
    regards from Alberta, Canada

    ian

  11. #10
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    Quote Originally Posted by ian View Post
    In my experience, "heavy duty" typically means that the insulation is thicker than normal, so the cable can withstand a little bit of physical abuse.
    Or is coloured red, or red and yellow.

  12. #11
    Join Date
    May 2003
    Location
    Central Coast, NSW
    Posts
    3,330

    Default

    Looking at it more closely, I think the words ‘heavy duty’ refer to the cable reel, not the extension cord.

    Seems a bit deceptive.
    Apologies for unnoticed autocomplete errors.

  13. #12
    Join Date
    Nov 2008
    Location
    Sydney
    Posts
    120

    Default

    Quote Originally Posted by BobL View Post
    Building circuits should look after themselves.
    Longer/ thinner cable drops more volts cable heats up - short term it might not be that much of an issue but long term, insulation gets brittle and cracks and . . . .
    Lower V at motor means it has to draw more current to achieve work rate (power) so more overheating of motors.


    Here's a few calcs for a 25m long cable, 240V mains at GPO on a 2.5HP (1863W = 7.8A) load.

    1mm^2 conductor will drop about 13V.
    Power dissipated in cable = Volts x Amps = 13 x 7.8 so the cable is drawing 101W = that's a lot - think of an old incandescent 100W light globe - although it is spread along 25m of cable.

    1.5mm^2 cable drops ~8.3V
    Power is now 65W which is a bit better but still .

    2.5mm^2 cable drops 4.5V
    Power is now ~35W

    This is BRAND NEW cable, older twisted cable with kinks and even lightly corroded plug and socket pins will have higher resistance loads.

    Bob, those calculations are fine if the compressor is rated at input power, but in my experience compressors are usually rated by the power delivered by the motor, not that consumed by it. I would expect a 2.5HP motor to consume an estimated 12 Amps at full load. The only way to determine the correct number for the calculation is to either look at the motor rating plate or else meter the current.

    Chas.

  14. #13
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,794

    Default

    Quote Originally Posted by Chas View Post
    Bob, those calculations are fine if the compressor is rated at input power, but in my experience compressors are usually rated by the power delivered by the motor, not that consumed by it. I would expect a 2.5HP motor to consume an estimated 12 Amps at full load. The only way to determine the correct number for the calculation is to either look at the motor rating plate or else meter the current.
    Good point but a 12A draw is not what I usually see on a well maintained 2.5HP compressor.

    Assuming the compressor motor is rated at max load, a 2.5HP (1.86kW) output power motor should be at least 80% efficient so should draw 2.235 kW or a current of 9.3A at 240V which is consistent with what I used to see on my 2.5HP that I used to permanently have a V/I meter on.

    By way of comparison my 4HP (2,98kW) compressor shows it drawing a max of 3.65kW which works out to be 82% efficient.

  15. #14
    Join Date
    Feb 2009
    Location
    moonbi nsw Aus
    Age
    69
    Posts
    2,065

    Default

    A mate wanted to do up his front gate on a hobby farm. He borrowed my 2.1 cu ft cement mixer with a half horse power motor. The gate is more than one hundred meters from the nearest power point. He assured me his extension lead could reach OK. I told him to mix at the power point in his shed then transport the mixed barrow of concrete on the carry all on his Furgy. I dropped the mixer off but had to retrieve it weeks after the job was done (Grrrrr....pet hate I hate having to retrieve tools that I loan).
    I put the mixer in its place under cover. About 9 months or so later I loaded up the mixer to do a job for a mate and guess what...... the motor died half way through the job. I am almost certain old mate with the long lead, used the mixer at the gate way instead of at the shed.
    Lesson learned.....be nasty and don't lend tools.
    I reckon the voltage drop over the 100 mts plus made the motor labour too much and was the cause of the motor's demise

    Yeah I am turning into a grumpy old man. It was only money to fix the motor....just over $200. Made the loan expensive
    Just do it!

    Kind regards Rod

  16. #15
    Join Date
    Apr 2011
    Location
    se Melbourne
    Age
    62
    Posts
    2,567

    Default

    If using a lead make sure it is fully uncoiled. If it has a cable reel, it must be fully off the reel. One of the signs of heat damage are melted reels or heat set where any twist become permanent in the lead.
    Air compressors - short or no extension leads are best, use additional air hoses instead.

Page 1 of 2 12 LastLast

Similar Threads

  1. HPM Extension Cord Recall
    By Anorak Bob in forum ANNOUNCEMENTS
    Replies: 7
    Last Post: 5th October 2012, 10:17 PM
  2. Can I run 2 hp motor off an extension cord
    By Arron in forum GENERAL & SMALL MACHINERY
    Replies: 19
    Last Post: 26th September 2012, 10:18 PM
  3. How far can you run an extension cord ?
    By masterblaster in forum SAFETY
    Replies: 27
    Last Post: 1st July 2007, 01:15 PM
  4. Extension cord tangle
    By Tiger in forum HAND TOOLS - POWERED
    Replies: 30
    Last Post: 4th September 2006, 10:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •