Thanks: 0
Likes: 0
Needs Pictures: 0
Picture(s) thanks: 0
Results 16 to 20 of 20
-
15th March 2011, 09:18 AM #16
I agree, it's not always straight forward. If possible go for a motor that is dual voltage name plated. However, if you find a motor that has a star/delta starter, that is a good thing. The star and delta connections are made in the starter not the motor so you will have all six motor leads brought out to the terminal box. Your correctly rated VFD will handle the startup once you connect the leads in Delta. Again, it's not always straight forward and you should check compatability of a motor with an 'expert' prior to purchase if possible. Single phase to three phase VFDs are more common in sizes up to 2.2kw or 3HP.
Those were the droids I was looking for.
https://autoblastgates.com.au
-
15th March 2011 09:18 AM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
15th March 2011, 10:15 AM #17
Cliff
That is exactly what I had at the old place in a rural area with my nearest neighbour at least a kilometre away. 35KVA with a Perkins diesel. Lovely. Not an option here.
Even there, the pacticality of starting the Genset to run a motor for even five minutes was daunting not to mention being about the worst thing possible for a diesel motor. I would normally find another way if possible and leave the genset option for bigger (longer) jobs.
Hence the quest for an alternative.
Single phase motors available as follows:
4KW 2 pole $500 plus freight, ($55)
3KW 4 pole $440 plus freight. ($48)
Eqvivalent VFDs (4KW) starting from $350 plus freight $50. VFDs sourced from Australia are nearly twice the price. It is true that it is possible to swap the VFD from one motor to another, but in practice it would be a right pain in the ####! A bit like sharing a three pin plug. Not going to happen is it?
Regards
PaulBushmiller;
"Power tends to corrupt. Absolute power corrupts, absolutely!"
-
15th March 2011, 11:20 AM #18
-
14th April 2011, 02:27 PM #19Member
- Join Date
- May 2010
- Location
- Sydney
- Posts
- 81
am i right in thinking you can run a 4 pole motor at 3000rpm by using a VFD to drive it @ 100Hz?
-
16th April 2011, 05:49 PM #20
Hi bonox,
Categorically no, for a couple of different reasons.
Firstly, induction motors rely on slip (difference between synchronous and operating speeds) to produce torque. For 100Hz input to a 4 pole motor, you would typically expect 2800 to 2850RPM for a motor providing usefull output.
Secondly, unless the motor was specifically designed for VFD drive, the iron cores in the windings would most likely not appreciate the higher frequency drive, and would respond with significant iron losses, resulting in overheating and reduced power output.
You were not specific about the motor type, but single phase and VFD are virtually mutually exclusive, due to the presence of start windings, start caps and centrifugal switches in single phase motors. They normally run at a single nominal speed and these devices are 'tuned' to suit that speed.
For the most part, a 2 pole motor would be cheaper or similar in price to a suitable VFD and more efficient.
Similar Threads
-
Hercus 3 phase lathe, single phase supply
By Pete F in forum THE HERCUS AREAReplies: 51Last Post: 16th January 2009, 10:15 AM -
replacing three phase motor with single phase
By rev in forum HAND TOOLS - POWEREDReplies: 18Last Post: 16th December 2007, 04:32 PM