    Default portable generator

    Has anyone had experience using one of the lower end petrol generators, like the one from Bunnings or similar? What size would I require to drive a 6.5amp circular saw or a decent power drill of about 1000W? I need to drill some fenceposts and install gate hinges, too far away for extension leads. I'll probably use the thing once or twice a year, but it might come in handy to power a freezer during a blackout. thanks, Peter

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Jan 2002
    Location
    Melbourne, Aus.
    Age
    71
    Posts
    12,746

    Default

    Prob hopeful Peter.

    A 1kw drill will draw more than that on startup so you'd be looking at a 1.5 or 2kw gennie.
    Cheers, Ern

  4. #3
    Join Date
    May 2007
    Location
    Gold Coast
    Age
    70
    Posts
    2,735

    Default

    There have been some in Aldi recently. I think they were 1200w but with a higher instantaneous load rating. I can't remember the price but $299 rings a bell.

  5. #4
    Join Date
    Oct 2007
    Location
    Alexandra Vic
    Age
    69
    Posts
    2,810

    Default

    For the circular saw and drill, you should get away with something having a similar rating to the tool, say 2KVA. Start up current should not be a major issue as these two tools start without the load applied, and the load is applied one the unit is up to speed.

    As backup for a freezer, hard to guess without knowing more about the freezer. If the motor is rated at 1/2 horse (375W), 2KVA would be borderline as the compressor motor is starting under load every cycle. Start current could be up to 6 times run current, and if insufficient current is available, the compressor may not start and will draw the available current till either the comp motor, the generator, or a fuse die. Either way the freezer will thaw unless there is immediate intervention.

  6. #5
    Join Date
    May 2004
    Location
    Mooroolbark VIC
    Age
    79
    Posts
    148

    Default portable generator

    Thanks everyone for their advice, I didn't think it was as simple as it looked. I will probably buy something of a decent size now, there is nothing worse than an underpowered tool of any kind. thanks and cheers Peter