    Quote Originally Posted by mhewitt View Post
    A cheap extension cord may be 1mm2 or even 0.75mm2 (the cross-section of the conductors within it). I have a table somewhere showing voltage drop (in effect, volts turned to heat) of various conductor sizes vs. length at nominal 240v; but it's not worth pulling out. Bottom line is that 2HP is only about 1500W. 10A at 240V is 2400W (I = W/V; Ohm's law). Any standard 10A extension cord at 3M will have no problem with 1500W. I'm not sure of the conductor size in a "heavy duty" extension lead; it can't be more than 1.5mm2 by eye - but I'd be happy to pull 10A/2400W through my ones at their maximum 25-odd meter length. Don't pull lots of power through a coiled extension lead. It'll melt. (But 1500W isn't lots of power).
    Don't forget that we are talking 2HP output - which as you say is 1500W. The input current will be a good deal greater allowing for the 70% efficiency of a single phase motor. Realistically your input will be 2150W or 9A @ 240V. Startup current can be as high as 6 times the rated input depending on machine/load type.
    I am glad you mention the no coiled lead rule particularly if wound around a reel or such, however I am not so sure that 1500W, (actually 2150), is not a lot of power - remember vacuum cleaners stipulate that their leads be unwound during use and they are a lot lower powered than we are talking here.
    General rule is that the bigger the lead the better.
    People spend mega dollars on good tools and then try to get by with the bare minimum lead wise which can then shorten machine life due to under voltage causing overheating.
    Leads really aren't that expensive these days an don't wear out if cared for.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Mar 2008
    Location
    Townsville, Nth Qld
    Posts
    4,236

    Default

    My choice of lead is the 15 amp lead with the 10 amp plugs
    I strongly agree! But get an electrician to wire up the plugs for you.

    You will be far better off with the heavier duty cable. Don't forget that for an induction motor, the starting current can be up to 6 times the normal full load current, which is why you often cannot start up more than one machine at a time.

    You don't want to run the risk of a thin cable operating at its limits - the insulation can melt, the bare cable wiring shorts and you have a fire and a big bang that causes a lot of inconvenience, if not a risk to life, depending on how often your circuit breaker earth leakage protection is checked and tested.
    regards,

    Dengy

  4. #18
    Join Date
    May 2010
    Location
    Not far enough away from Melbourne
    Posts
    4,204

    Default

    Quote Originally Posted by Dengue View Post
    Don't forget that for an induction motor, the starting current can be up to 6 times the normal full load current, which is why you often cannot start up more than one machine at a time.
    Something else that I have to be mindful of, speaking about starting or running more than one machine at a time - I have a 3hp compressor so when I am running any other large machines, I make sure the compressor is turned off. I have three other 3hp machines, a tablesaw, bandsaw and a thicknesser. There would be a 2hp dusty running at the same time as any of these machines. The last thing I would want is the compressor to decide to charge up the tank when I am already running 5hp of gear plus fans, radio etc.

    Just a little something to keep in the back of the mind; some machines like compressors can start by themselves and make an awful mess of your power consumption predictions.

    Doug
    I got sick of sitting around doing nothing - so I took up meditation.

  5. #19
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    Quote Originally Posted by Karl Robbers View Post
    . . . . however I am not so sure that 1500W, (actually 2150), is not a lot of power - remember vacuum cleaners stipulate that their leads be unwound during use and they are a lot lower powered than we are talking here.
    One significant reason that this is stated for vacuum cleaners is because the cord inside the vacuum cleaner is wound up inside the machine and has little chance of losing the heat. If the coil is covered up with anything that reduces heat loss even a small amount of heat may cause a problem but if the coil is exposed to open air the amount of heating is small for <10 A devices.

    A few years ago I did an experiment on the 15 A extension cord that I use to power my welder. I rolled up the cord on a plastic bobbin so that the cord consiste of 3 layers (each of 10 turns) hanging about 500 mm from the roof of the shed. I placed a thermocouple in between two of the turns in the middle layer and welded 4, 3 mm rods more or less continuously, and paused briefly in between each rod to see what the temperature rise would peak at.
    Recently I found the data and thought you might like to see it.,

    Starting Temp was 19º
    Turning on the welder and letting it warm up over 10 minutes - ie no arc, the temperature stabilized at 31º,
    After welding with one rod, it was 35º;
    after 2 it was 39º
    after 3, 42º
    after 4, 45º

    The reason I stopped at 4 rods was the limited duty cycle of the welder meant I could not weld more than 4 rods before it stopped working.

    Undoubtedly the temperature inside the wire would have been higher but there was no smoke.
    I did a megger test on the cord before and after this treatment and there was no change in the spec

    The temperature problem is exacerbated when
    - its a hot day
    - when the coil is covered up with something thermally insulating that prevents heat loss
    - when the cord is just old or damaged increasing its resistance.
    - when high currents are drawn for very long times.
    - roll has many layers

    I show this data because it is not quite as bad as it is sometimes made out to be - I still use that extension cord to power my welder - it's left with the same 3 roll layers hang from the roof.
    Sometime I should re-megger it to see how it is going.

    Of course I advocate unrolling long extension cords but I don't get too paranoid about leaving a couple of coils on a roll and I do make sure they are well ventilated.

  6. #20
    Join Date
    May 2010
    Location
    Not far enough away from Melbourne
    Posts
    4,204

    Default

    Quote Originally Posted by BobL View Post
    Of course I advocate unrolling long extension cords but I don't get too paranoid about leaving a couple of coils on a roll and I do make sure they are well ventilated.
    I agree with Bob. I have a number of 15amp leads with 10amp plugs of various lengths so that I can use a fully unwound lead without having excess power lead lying around the workshop, but let common sense prevail.

    Suppose I need to use a hand-held electric drill to drill a couple of holes and the only lead I had available was 30m and I was 2 metres from the power point and the drill had a 1.5m lead I would not unwind the 30 metre extention lead any more than necessary.

    At the other extreme, if I needed to use a 30m extention lead to get me a metre further from the power point for one of my 3hp machines I would unwind it fully even if it was for just one cut. And it goes without saying that I would prefer not to use a lead that long on a machine that size if there is another way of doing it, eg shorter lead.

    Doug
    I got sick of sitting around doing nothing - so I took up meditation.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Replace Cord on Saw
    By brucewil in forum HAND TOOLS - POWERED
    Replies: 10
    Last Post: 15th May 2008, 07:19 PM
  2. How far can you run an extension cord ?
    By masterblaster in forum SAFETY
    Replies: 27
    Last Post: 1st July 2007, 01:15 PM
  3. Extension cord tangle
    By Tiger in forum HAND TOOLS - POWERED
    Replies: 30
    Last Post: 4th September 2006, 10:22 AM
  4. Power saw blade + extension cord
    By Chris Duhig in forum HAND TOOLS - POWERED
    Replies: 9
    Last Post: 7th July 2002, 09:32 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •