It depends on the distance of cable run, whether you need to get a new breaker installed etc, it's hard to give a figure that's going to be anywhere in the ball park. What you need to do ideally is find a friendly sparky who will let you do the grunt work running the cable and then he will terminate at each end and do the paperwork, labour is the expensive part so the more you can do the better.
It could be worse though, I recently upgraded my MIG to a 200A BOC unit which requires a 20A feed. The welder cost me $2200, the upgrade to the workshop wiring (including a new sub-board) cost me $1250. The round pin industrial sockets were $250 each and the matching plug was $125 - Ouch!
-
12th March 2010 03:41 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Age
- 2010
- Posts
- Many
-
12th March 2010, 09:45 PM #32SENIOR MEMBER
- Join Date
- Feb 2010
- Location
- Ballina, NSW
- Posts
- 725
Still waiting for the sparky to come and quote for a 15amp socket, but in the meantime I went and bought a 15amp extension lead (20m), cut it about 1m from the socket end and stuck a 10amp plug onto the loose end - so now I've got my short adapter cable. I put a 15amp socket on the left over 19m bit so I can use that too... if the sparky ever turns up! Total cost $37 bucks. Probably the least amount of money I'm going to be spending for a while on this project.
-
28th March 2010, 11:30 AM #33Novice
- Join Date
- Jan 2010
- Location
- wa
- Posts
- 22
-
29th March 2010, 10:01 AM #34Cheers.
Vernon.
__________________________________________________
Bite off more than you can chew and then chew like crazy.
-
29th March 2010, 03:33 PM #35
Welder from an RCD - OK
Hi all from an occasional visitor --
I have a small stick welder running off a RCD and separate circuit breakers in the shed sub-board - It works fine and has never tripped the RCD. It has tripped the 20Amp circuit breaker many times - usually after a serious session welding with 3.2mm rods.
The non-tripping of the RCD makes sense as the transformer in the old welder has an isolated secondary winding. This means that what goes in the primary, comes out the primary and hence is balanced as far as the RCD is concerned. This is not affected by me connecting one end of the secondary to earth. The only way there could be a problem is if the primary has a leak to earth or to the secondary - and then you want to know about it.
back to normal programcheers
David
------------------------------------------------
A society grows great when old men plant trees whose shade they’ll never sit in. (Greek proverb)
-
29th March 2010, 03:37 PM #36
Thanks for that David.
Cheers.
Vernon.
__________________________________________________
Bite off more than you can chew and then chew like crazy.
-
30th March 2010, 01:29 AM #37
Similar Threads
-
15amp shop vac question
By Ben from Vic. in forum DUST EXTRACTIONReplies: 4Last Post: 28th December 2008, 09:05 PM -
Install 15amp outlet
By haosiliu235 in forum WOODWORK - GENERALReplies: 15Last Post: 31st October 2007, 09:08 AM -
Where to find 10 and 15amp leads <5m
By Waldo in forum HAND TOOLS - POWEREDReplies: 22Last Post: 8th September 2005, 11:30 AM