My 130A BOC inverter doesn't have a 15A plug, so I don't see why the very similar CIG would require one.
-
9th August 2011 11:33 AM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
9th August 2011, 12:20 PM #17
Yes, the specs certainly indicate that it's a 10A machine ... my comment was meant to be a little "tongue in cheek".
It is interesting however that the specs for your welder state that the maximum input current as 23A (I would assume that may occur when striking an arc). I wonder if that sort of current flow (even in short bursts) has a detrimental effect on a GPO over time ... maybe that is what contributed to the demise of your "original" GPO???Cheers.
Vernon.
__________________________________________________
Bite off more than you can chew and then chew like crazy.
-
9th August 2011, 02:16 PM #18Senior Member
- Join Date
- Jan 2008
- Location
- Vevey, Switzerland
- Posts
- 407
The electrician did say that if he replaced the cable with 4mm he could use a 20A circuit breaker so I might do that.
To be honest I've been abusing that GPO as my woodworking machines have built up over the years without really thinking about it, so this is a bit of a wake up call.Cheers, Glen
-
14th August 2011, 11:57 AM #19Senior Member
- Join Date
- Oct 2006
- Location
- perth
- Posts
- 169
my rehm 170 has a 10amp plug and my new rehm 170 tiger ac/dc tig is also 10amp
-
19th August 2011, 09:49 AM #20Senior Member
- Join Date
- Jan 2008
- Location
- Vevey, Switzerland
- Posts
- 407
Finally found the problem - would you believe too high voltage
I had a 15 amp GPO fitted next to the 'faulty' 10 amp one - completely separate circuit but same problem. The electrician checked everything, nothing wrong.
Scratched his head for a few minutes and then suddenly grabbed three of my extension leads chained them together and connected the welder to the GPO using them. Problem solved.
The meter box is just next to the shed so only about a meter of cable to the switch box and the GPO is about 20cm underneath that. The transformer is on the pole about 20 meters from the shed and only serves two houses. The substation is just up the road. He read the voltage as 247V. It is supposed to be within 10% of 230 so we are just within that.
I wouldn't have believed it but there it is. I just have to use a long extension lead to get the voltage drop!Cheers, Glen
-
19th August 2011, 10:55 AM #21Cheers.
Vernon.
__________________________________________________
Bite off more than you can chew and then chew like crazy.
-
19th August 2011, 01:50 PM #22Senior Member
- Join Date
- Jan 2008
- Location
- Vevey, Switzerland
- Posts
- 407
Thanks. The electrician said that the lead would cause a drop of about one volt, but that's apparently enough to do the trick.
But I will take care to make sure it isn't coiled tightly so it can dissipate the heat. I'm a novice doing small odd jobs so the welder is only melting metal for very short periods.Cheers, Glen
Similar Threads
-
Faulty Mig !!!
By Keepbusy in forum WELDINGReplies: 12Last Post: 25th August 2010, 10:41 AM -
Faulty CD burning
By Andy Mac in forum COMPUTERSReplies: 21Last Post: 17th August 2008, 11:07 PM -
Are my ear muffs faulty?
By Mike_R in forum TRITON / GMCReplies: 4Last Post: 15th December 2006, 03:44 PM -
What would you do with a faulty TSC-10HB
By tonyjune in forum WOODWORK - GENERALReplies: 6Last Post: 11th March 2005, 03:46 PM -
Is this plane faulty ?
By Forrest in forum HAND TOOLS - UNPOWEREDReplies: 10Last Post: 21st September 2004, 11:31 PM