    Quote Originally Posted by RayG View Post
    Hi Marc,

    The VFD inputs are all active low ( current sinking ) and are pulled up to 24V DC inside the drive, so if the drive is powered and you measure an unconnected input as zero volts, then the only conclusion is that the internal 24V supply inside the drive has failed or is shorted out somewhere....

    Regards
    Ray


    I just double checked and it seem like i didn't measure the right pins. You were right, the voltage between DCM and FOR is 23.2V.

    Marc

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Quote Originally Posted by dubdzine View Post
    I just double checked and it seem like i didn't measure the right pins. You were right, the voltage between DCM and FOR is 23.2V.

    Marc
    Hi Marc,

    Ok, that sounds more like it, you could double check that it goes to zero volts when the switch operates..

    A few posts back I asked about PD002?

    I notice that you've selected comms as the source of the operating frequency ( PD002=2 ) but you've wired it up for analog input frequency control? Shouldn't PD002 be set to 1?

    I've finished up here for the time being, ( it's late! ) so I'll leave you to check that, and maybe see how you've got on tomorrow.


    Regards
    Ray





  4. #18
    Join Date
    Jun 2013
    Location
    United States
    Posts
    12

    Default

    Quote Originally Posted by RayG View Post
    Hi Marc,

    Ok, that sounds more like it, you could double check that it goes to zero volts when the switch operates..

    A few posts back I asked about PD002?

    I notice that you've selected comms as the source of the operating frequency ( PD002=2 ) but you've wired it up for analog input frequency control? Shouldn't PD002 be set to 1?

    I've finished up here for the time being, ( it's late! ) so I'll leave you to check that, and maybe see how you've got on tomorrow.


    Regards
    Ray

    THANK YOU RAY, have a great night. the vfd can now be fully controlled trough mach 3. A wire going to the relay had a bad connection!
    The VFD speed is not consistent with Mach 3. It spins at 23160rpm when entered M3 S24000 and 7200rpm at M3 S6000.
    The highest rated motor current that can be set is 7A in PD142 when it needs 13.6 A at 110V (1.5kW)

    Marc

  5. #19
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Quote Originally Posted by dubdzine View Post
    THANK YOU RAY, have a great night. the vfd can now be fully controlled trough mach 3. A wire going to the relay had a bad connection!
    The VFD speed is not consistent with Mach 3. It spins at 23160rpm when entered M3 S24000 and 7200rpm at M3 S6000.
    The highest rated motor current that can be set is 7A in PD142 when it needs 13.6 A at 110V (1.5kW)

    Marc
    Congratulations on finding the problem.


    7A is the maximum rated output current for the 240V 1.5KW version. So I'd say that's what you've got...

    Maybe you can find someone else with a 110V version and do a comparison?


    Regards
    Ray

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Replies: 1
    Last Post: 24th June 2013, 01:22 PM
  2. G540 Help, old dog new trick.
    By pkowal in forum CNC Machines
    Replies: 11
    Last Post: 29th August 2011, 11:09 PM
  3. 24 volt proximity switches
    By wbleeker in forum CNC Machines
    Replies: 24
    Last Post: 19th July 2011, 05:55 PM
  4. Treated Pine In Close Proximity To Ground
    By bryce_k in forum TIMBER
    Replies: 1
    Last Post: 29th April 2010, 06:32 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •