    Default Some interesting air flow measurements

    Some of you may stumble across this web page on air flow measurements using a 1HP DC

    The air flows reported on this page are shown below


    These results are typical of those performed with an air speed meter where only one measurement is taken in the middle of the end of a duct. This is also what DC manufacturers do which leads to ver estimation of the capacity of the blower.

    This neglects
    a) the effect of friction at the walls of the pipe where the air speed is much lower.
    b) that air flow paths at the ends of a pipe are not the same as what is going on inside the pipe. To get an accurate results the measurements MUST be performed with a small probe inside a straight length of pipe, across the cross section of the pipe and then the results correctly mathematically integrated.
    c) related to a) how close to the bends and junctions the measurements taken. If the measurements are taken too close to junctions then turbulence can lead to measurements all over the place.

    As a result the reported results for the straight lengths of pipe are over estimated by at least 20%.
    For junctions etc the results could be even further out.

    In relative terms the results are probably correct for the straight lengths of pipe/duct, but deduct at least 20% for a more accurate result

    Thanks rusel for the link.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Aug 2008
    Location
    Shepparton *ugh*
    Age
    49
    Posts
    1,185

    Default

    Well now...those bend results are quite interesting.

  4. #3
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    The article makes the excellent recommendation that
    A reminder that dust extractors with coarse bags should be located outside the workspace or in a cabinet vented to the outside to prevent the dangerous fine air from escaping and being drawn back towards you by the vacuum created at your machine.
    but it also suggests that

    we'd like at least 350cfm in a 100mm duct system, but levels as low as 250cfm will still work for light dust. We should aim for 400cfm.
    These two recommendations are somewhat contradictory since 400 cfm is totally inadequate for grabbing fine dust at source of the dust production. Flow rates of 800 to 1000 cfm are needed to do this.

    350 cfm should be the minimum flow rate in a 4" duct since that is where the linear air speed reaches 4000 fpm, below that the dust will not easily stay in suspension and will clog ducts. At 250 cfm the linear air speed is now 2800 fpm which is now well below the 4000 fpm limit.

  5. #4
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    I contacted them and have had several email exchanges with the guy (Terry) that did the measurements. Terry is very technically minded (especially in electronics) and has been most helpful in expanding on what he did. He has tried to be as careful as possible and knows generally there are limitations with his measuring method but was not aware of the extent of his over estimation of the air flows.

    The main problem comes about because he is using a fan type air flow meter that is 3" in diameter. When the 3" fan is placed in from of a 4" duct it partially blocks the duct which increases the air speed into the duct and through the fan. This then over estimates the airflow.
    The other problem with a 3" fan is it cannot get close enough to the wall of the duct to accurately measure the air speed at these points in the duct. This also over estimates the speed of the air flow.
    He is also not using a proper test duct.

    I don't want to be critical of Terry as he clearly has done his best but these results are a common problem with DIY air flow measurements. Even worse is DIY particle measurements where variable backgrounds are not taken into consideration and can really mess up the measurements.

  6. #5
    Join Date
    May 2012
    Location
    Brisbane (Chermside)
    Age
    71
    Posts
    2,084

    Default

    This is a common problem everywhere.

    Good data is rare. Crappy data is common. Even good data have limited information content. It is necessary to understand how the data were collected so we know its shortcomings ... all data sets have shortcomings. Another trick is understanding what info is not in the data as well as that info which is in the data.

    Epistemology should have been one of the most important courses of study we took ... but most people don't take it.

Similar Threads

  1. Replies: 13
    Last Post: 28th October 2012, 06:55 PM
  2. Gas Rate Flow
    By DirtPig in forum WELDING
    Replies: 8
    Last Post: 8th November 2011, 03:26 PM
  3. air flow required for a DE
    By notenoughtoys in forum DUST EXTRACTION
    Replies: 8
    Last Post: 13th August 2010, 09:15 AM
  4. Sporadic ink flow
    By Ray153 in forum WOODTURNING - PEN TURNING
    Replies: 2
    Last Post: 21st July 2007, 06:09 PM
  5. Dusty air flow - some measurements
    By BobL in forum SAFETY
    Replies: 14
    Last Post: 25th May 2006, 02:02 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •