    Default Exhaust Fan Revisited

    This is my update to this thread:


    Shed Ventilation


    Four years ago I installed a couple of hydroponics fans to provide a negative pressure in my work area, specifically to take away fine dust and paint smells.


    These work very well - usually depending on which end of the area I am working, I have only one turned on while using dust making gear and leave it on for about an hour afterwards.


    The fans were sized to give around 15 air changes per hour each, and with no means of testing other than observation and sniff, I'd say they've been a complete success. By way of example: after letting an awful lot of smoke out of one of my gadgets, the room was clear of smell in fewer than five minutes after turning on one fan.


    But it could be better.


    After four years there is a build up of dust on the fan casing and within about a square metre of the fan, yet not elsewhere in the room.

    21-03- 19 at 11-42-03.jpg 21-03- 19 at 11-41-24.jpg



    I have no real technical knowledge of this stuff, but suspect this is due in part to "blow back" from my duct installation, which isn't sealed around the fan outlet, and in part due to "spitback" because the fan itself has a barely rounded entrance and is pretty close to a square mouth.


    Here's what I think needs to change, and would welcome any input.


    1)Angle of installation.


    I don't know what to call this, but the fan is located at the rear-most corner of the room, however it is square to the side rather than the long axis, meaning air has to make a sharp right angled turn to enter the fan.


    By changing the mounting angle of the fan closer to the direction of flow, ie pointing it more down the room, some improvement should result.




    2) "Blowback" (my term)


    The fan is sold as a 250mm fan because that is the diameter of the outlet. but the reality is that the fan inlet is 165mm diameter with a central axle of 90mm. This gives a very approximate inlet area of 15,000mm2. I split the outlet into two 150 diameter pvc pipes with gravity louvres to weatherproof the outside. The net outlet area is about 15% larger than the outlet of the fan, but clearly there is some air flow disturbance caused by the louvres and the junction of the duct which reduces this and causes some back pressure and subsequent leakage.


    The duct is made from 3mm MDF which I projected manually, scored and shaped, but it is not a tight fit around the fan exit and you can clearly see the result in some places.

    21-03- 19 at 11-41-31.jpg



    3) "Spitback"


    Because there are a million references on the web, I have chosen just one - it concerns much higher air flows that we are talking about here, but the principals are the same, and I was surprised to see the parabolic bellmouth design is almost identical to the one I have been using, taken from another source.



    These diagrams are from:
    http://www.profblairandassociates.com/pdfs/RET_Bellmouth_Sept.pdf

    Screen Shot 2021-03-19 at 1.11.14 pm.jpg



    And I think show what is happening. Refer to the middle example: as the disturbed air containing dust approaches the fan "spitback' creates a pocket of still air around the fan and the dust can settle. This should be pretty much eliminated by the use of a bellmouth to the opening as in the bottom drawing.

    PROPOSED SOLUTION:

    Time to give the 3d printer another workout I think - and if I proceed, don't expect an update to this for some weeks - there will be a fair bit of lead time for this one!

    1) Increase the length of the outlet duct to give a smoother transition from 250 to two 150 diameter outlets.
    2)Angle the fan more towards the centre of the room.
    3)Make a bellmouth extension to the inlet side.
    4)Extend the centre boss for better airflow. I am flying completely blind on this one, so have assumed a similar profile to the bellmouth, and created a parabolic cap that "looks right" with no science involved - I'd love to know what the correct shape is or how to find it.
    5) A bellmouth exit would also improve things, but since we are going through a brick wall here and this is inside our house after all, the gravity louvres are going to stay in an effort to minimise intrusion by small creatures and water.

    Screen Shot 2021-03-19 at 12.57.15 pm.jpgScreen Shot 2021-03-19 at 12.57.38 pm.jpg

    As always, robust discussion, criticism and assistance will be welcome!

    By the way, these solutions are not for everyone, and the fan does work very well, it's just that refitting my shed/workspace is currently happening in the same way some guys restore cars, with ridiculous attention to detail, because for now at least my shed IS my hobby, and because I have copped such a hiding over twenty years from you lot because you thought I'd never finish my dust extraction system, I WILL have the last laugh!

    Cheers,

    P

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    I'd say the biggest elephants in the corner are the gravity louvres.
    Even when they are open they will constrain air flow so removing them and going for an unconstricted opening should produce bigger gains than anything else you have mentioned.

    One solution to preventing things from entering an open fan exit could be sliding or hopper style closure that leaves the exit completely clear when open. Automation of these would an interesting project. Closure could be gravity based via a solenoid - opening is a bit more problematic.

    I'm not sure its worth the effort of putting BMHs on those fans as their air flow rates are not that high.
    BMHs won't make a noticeable difference on a dust port connected to a small (1HP DC).
    On a 2HP DC the BMH should be is noticeable on a short 6" duct, but I suspect it's only marginal on a long 4" duct.
    The longer the ducting and the more constricted the dust pathway (multiple junctions and the ability of a machine to breath) the lower the flow and the less difference BMHs will make.

    If you send me one of your BMHs I will test its flow improvement (compared a naked duct opening) over a range of flows rates

  4. #3
    Join Date
    Nov 2003
    Location
    Australia and France
    Posts
    8,175

    Default

    Quote Originally Posted by BobL View Post
    One solution to preventing things from entering could be sliding or hopper style closure that leaves the exit completely clear when open. Automation of these would an interesting project. Closure could be gravity based via a solenoid - opening is a bit more problematic.

    OK so now I have an add-on project (for next year probably) and I don't think it's too hard to do either.

    A hopper style cover fixed to the outside wall would be fine, operated through a linear actuator - just need a rod through the wall and probably 50mm of movement if the angle is steep enough. I don't know enough about electronics (yet! ) to sort this, but a simple relay mounted on the same circuit to hold the actuator open when the power is on, and close when the power is off should be easy enough to work out - if I use a 12v actuator and electronics I might not get killed in the process either!

    Watch this space!

    Thanks!

    P

  5. #4
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,790

    Default

    Good plan on the opening and closing.

    I've been thinking about the directionality of the fans issue and once again their flow rates are probably too slow to create significant directionality.

    Most fans sucking on large volume spaces like workshop basically create small pressure differences/gradients across a room to incoming air vents into the room which then generates a flow. If the fan is slow then the pressure gradients are small and spread themselves fairly evenly across to the incoming air vents and overall air flow rates won't matter much on the direction the fans are pointed are pointed.

    To get even ventilation across a room, the positions of a fan and the incoming air vents are important for reducing dead spaces or under ventilated air. If there is only one fan and one nearby vent a preferential flow will form between the two and can leave the remainder of the room under ventilated. If only one fan is available then it helps to have numerous incoming vents spread evenly around the room. Evenly ventilation is usually more important than just trying for more air flow in subsection of the room.

Similar Threads

  1. A Pen Revisited
    By Ironwood in forum WOODTURNING - PEN TURNING
    Replies: 5
    Last Post: 16th September 2014, 09:08 PM
  2. CEO revisited ?
    By gawdelpus in forum WOODTURNING - PEN TURNING
    Replies: 2
    Last Post: 19th November 2011, 10:03 PM
  3. Exhaust Fan Help
    By LegacyGT in forum BATHROOM & TOILET
    Replies: 2
    Last Post: 15th April 2008, 03:25 PM
  4. Exhaust Fan
    By gregt in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 1
    Last Post: 14th June 2007, 08:15 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •