Proposed electrical for new shop project
Hello Brains trust, I am finally after a lifetime of living in a leaky, low roofed, dark and asbestos roofed shed, I can see the light and I am planning the
fitout of the new shed.
It will be a skillian style shed 8 X 6 metre where the low side is 3 m and the high side is nearly 4 metres.
I am handy and know my way around electrical so I have got my sparkys blessing to start the process. So I've had a go at a switchboard design
I do not want to mucked around and I don't mind the effort to do the bulk of the roughing in work, digging trenches for cables etc. I am a Broadcast Engineer by trade.
I have designed a switchboard that will give me 9 x 10Amp, 5 X 16 Amp and a RCP fitted 3 phase outlet. I plan to run LED lights throughout but
instead of hard wired get the sparky to install rows of sockets on light switches so the configuration can be changed ( Great idea BobL ) External lights switched in the shed and
exhaust fans plus ceiling fans will chew up a few circuits. I do not want to under supply it so there is plenty of circuits to go around.
I will literally put the physical board together and get the sparky to wire it. He tells me it will be faster and cheaper to buy all of the stuff myself and he will
plumb it all up.
I figure the switchboard will cost north of $750 to purchase all of the bits and the wiring/fittings a similar amount.
I am planning on at least 20 X 10 AMP doubles and at least 5 X 15 AMP sockets with a single 3 phase 32 AMP circuit should I find groovy 3 phase tools down the road.
Attached is a picture of the shed and the proposed wiring for the switchboard which will be 2 X 18 bay switch banks.
my question is a simple one - is this going overboard or am I right to futureproof it for my senior years? I will only get one shot of this as SWMBO says do it once and do it properly.
What are your thoughts, especially those who have gone big with their switchboards?
Regards ,Scott.
ADDED BY ADMIN
DISCLAIMER
No liability is accepted by U-Beaut or the Wood Working Forum's administrators
or moderators for advice offered by members posting replies
or asking questions regarding electrical work.
We strongly advise contacting a Licensed Tradesperson for all electrical work.
WARNING
Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
Members following such information do so at their own risk
-
14th August 2021 03:50 AM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Age
- 2010
- Posts
- Many
-
14th August 2021, 07:18 AM #2
Hello Scott, I am not a sparky, so I will avoid any specific electrical answers, but will go from my experience planning and roughing in my shed.
It was cheaper for my sparky mate to purchase all the bits and bobs at trade prices and quantities, then pass them onto to me to rough in to an agreed schematics. I think the only stuff I brought was the hard and flex conduit from the big green store, as I had a ute at the time. This also meant that everything was to code.
All gpo's are at 1400mm from the floor for easy access. My bench heights are about 900mm.
All wires are ran external in solid or flex conduit attached to the white melamine boards on the walls for easy access, if I ever need to.
I have 5 circuits in my 8x4 shed, 2 10amp circuits, one of which lives the beer fridge, 1 very short run for a 20amp circuit for my lathe, a light circuit and a 15 amp circuit. Is this enough for me. Yes. The most I use is a tool, be it the lathe on it's own circuit and the DC on the west side circuit or the Bandsaw/Spindle Moulder/Thicky on the 15amp circuit and the DC. The beer fridge is on the east circuit.Pat
Work is a necessary evil to be avoided. Mark Twain
-
14th August 2021, 08:41 AM #3.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,791
Im not a sparky but here is what I did in my shed which is similar size to yours (42 m^2)
- used a combined breaker/RCP units instead of separate units
- use a single 10A breaker for a single light circuit
- used 16A breakers for the 10A GPOs . I reckon you have gone OTT with the number of 10A GPO breakers. I have ~20 double 10A GPOs and have these on 3 x 16A breaker circuits. I run a lot of things at the same time and have never had a breaker trip due to loa
- 3 of my smaller 15A machines are on 16A breakers, and two of the HD 15A machines (welder and compressor) on 20A breakers - you can always swap them out later.
If you remove the unnecessary 10A breakers this will leave some space in the breaker box for other things like more 3P or 15A breakers if you need them.
-
14th August 2021, 08:12 PM #4
I would suggest looking at RCBO’s rather than separate RCD’s.
Looks a bit overkill for a home workshop, how many tools will be running at the same time? I think you can reduce the total number of circuits.
-
14th August 2021, 08:47 PM #5SENIOR MEMBER
- Join Date
- Jan 2015
- Location
- Latrobe Valley
- Posts
- 160
Sparky here SWR - I would say complete overkill & old way of doing things, akin to when RCD's were expensive.
Price of RCBO's has become so cheap, I would be surprised if any sparky would say that it's cheaper for you to purchase and install yourself.
-
14th August 2021, 09:30 PM #6.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,791
-
15th August 2021, 02:25 AM #7
-
15th August 2021, 10:07 AM #8
-
15th August 2021, 10:52 AM #9Member
- Join Date
- Oct 2016
- Location
- QLD
- Posts
- 54
G'day SWR,
You can drop the rating of your 3P RCBO to 32A and do away with the redundant downstream CB - the RCBO provides overcurrent protection as well as as earth leakage detection.
Not sure if cost is the main driver for your layout having one RCBO feeding multiple MCBs, but by the same token you could do away with the other three 1P RCBOs if you swap all your 16A & 20A MCBs for RCBOs. Remember, most devices will have a 'normal' amount of earth leakage. The more circuits you put on a single RCD the more likely you are to get nuiscance tripping
You should be able to drop your DB size down to a single 18 way and still have plenty of space for expansion if you ever need it.
-
16th August 2021, 03:16 AM #10
-
16th August 2021, 07:17 AM #11.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,791
Starting to look more reasonable.
-
16th August 2021, 08:29 AM #12SENIOR MEMBER
- Join Date
- Jan 2015
- Location
- Latrobe Valley
- Posts
- 160
3ph RCBO are not 4 pole - don't mistake the current rating on a 3ph RCD as being a circuit breaker rating.
Get your sparky to wire your board. There are still plenty of things wrong with your diagram.
-
16th August 2021, 09:42 AM #13GOLD MEMBER
- Join Date
- Apr 2018
- Location
- Nsw
- Age
- 64
- Posts
- 1,362
IMO the biggest mistake you are making is that you are designing the system yourself and I would question the suitability of your “ electrician” for the project for entertaining the idea in the first place.
This is basic bread and butter type work for a tradie who is well versed in day to day domestic electrical work. I suspect at a guess that your electrician whilst having the appropriate accreditation is not in the game as such?
By all means do all the hack work of running cabling and conduit work if that takes your fancy but being involved in the design process as you can see by the comments to date can easily be false economy
Not trying to have a go at you but I see this all the time with DIY and owner builders who think they are saving money but through their lack of knowledge and experience ultimately spend more than getting professional assistance.
I am just seeing it again in the last few weeks with an owner builder down the road, he hasn’t even poured a footing yet and I can see he has spend at least $30,000 too much in how he has gone about his earthworks, not to mention the extra weeks lost in the process. Of course he will probably never realise that and is thinking how much he has saved by arranging it all himself direct with the contractors.
You don’t know what you don’t know.
-
16th August 2021, 09:53 AM #14Senior Member
- Join Date
- Aug 2016
- Location
- Hervey Bay
- Age
- 46
- Posts
- 230
I would consider changing some or all of the 15amp outlets to 20amp, my 3 large tools ( table saw, bandsaw , planer/thicknesser ) all have 20amp plugs and appropriate cable fitted as specced by the manufacturers. You can always plug a 15 or 10amp into a 20amp flat pin socket.
Similar Threads
-
Setting up shop from scratch - first project - Plantation Shutters