Thread: My shed leaks

  1. #31
    Join Date
    Jul 2011
    Location
    In between houses
    Posts
    1,784

    Default

    Quote Originally Posted by DTH1 View Post
    Hi Guys,
    Having built many sheds over the years, I would suggest the simplest and most cost effective solution is to use a proper folded flashing.
    Have a talk with a steel supplier and see about having the flashing folded to suit about a 20° pitch. The photo below is with a 90° fold (arrow).
    The flashing cost should be around $15/m.

    Unscrew the bottom 2 rows of screws on the upper roof, slide the flashing up underneath the sheeting. Then mark where the trimdeck rises and cut out the sections with tin snips. Don't just cut each side and fold flat, this just invites corrosion between the flashing and the trimdeck.
    Lay everything back in place and pop-rivet the flashing to the trimdeck. Silicon and rivet the flashing joins (150mm overlap) as you go. Re-screw the upper roof sheeting back in place. Finally, silicon the rivet heads. Don't use any silicon in the tray of the trimdeck as this will stop any water that may find it's way in from getting out.

    Attachment 474863
    Im pretty sure a previous reply from someone suggested this very exact same and sure fire method to fix this issue. This is the best and would be the only way I, as a licensed builder, would make it good if asked.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #32
    Join Date
    Aug 2004
    Location
    Perth WA
    Posts
    2,035

    Default

    Well fix it Dear Henry! Dear Henry fix it!
    Experienced in removing the tree from the furniture

  4. #33
    Join Date
    Oct 2015
    Location
    Ringwood, VIC
    Posts
    575

    Default

    I'm confused.
    How can I fit a flat sheet between the top sheet and the verandah sheet? There is at most 10mm gap between the two, following the profile. I could loosen the top sheets to get it in, but can't screw them down tight to the batten.
    What am I missing? Or will the bottom of the sheets just curve up?
    Edit - do I need to trim the roof sheets back so there is a gap between the verandah and the roof?

  5. #34
    Join Date
    May 2011
    Location
    Albury
    Posts
    3,019

    Default

    See post #24 Russ. That's what all the builders are describing, DTH1 has just stated it in a slightly different way and without acknowledging that his advice is the same as that previously given. No wonder you're confused! BUT you can't just use the flashing you also need to turn up , 'weather', the ends of the verandah sheets. Some people aren't too good at explaining things or providing all the details you need to know to complete the job, which is probably why riverbuilder neglected to point out this very necessary step in his reply to DTH1. The ends of the sheets have to be weathered because water can still be driven up through the gaps between the flashing and the verandah sheets.

  6. #35
    Join Date
    Oct 2015
    Location
    Ringwood, VIC
    Posts
    575

    Default

    Pretty sure I understand what is suggested. But see photos. It's not possible to slide a flat sheet between the top sheet and the verandah sheet.
    If the flashing is soft aluminium then it can be pressed down to follow the profile.



  7. #36
    Join Date
    May 2011
    Location
    Albury
    Posts
    3,019

    Default

    Yep, I hear you Russ, that's one reason I suggested you use the aluminium flashing. To use the builders method you would need to cut back the ends of the sheets on the main roof as you've suggested. As I understand it there is very little overlap between the roof sheets and the verandah sheets already without reducing it even further by cutting back the roof sheets. Regardless of what you end up doing it would be very wise to turn up a square end, 'weather', the ends of the verandah sheets. Anything has got to be better than what you've got now.

  8. #37
    Join Date
    Jun 2010
    Location
    Wimmera
    Posts
    174

    Default

    Just cut the top sheet a bit shorter so the flashing will fit up under it. Make the section that goes under the top sheet long enough to sit on the purlin. You will have to cut out the sections that sit on top of the ridges on the flatter roof so that you can fold the edge down as in post 24.
    Can't get any simpler than that.

    Hooroo.

  9. #38
    Join Date
    Oct 2015
    Location
    Ringwood, VIC
    Posts
    575

    Default

    Ok, thats clear. How long should the flat section be?

  10. #39
    Join Date
    Jun 2010
    Location
    Wimmera
    Posts
    174

    Default

    As riverbuilder suggested. 200mm.

  11. #40
    Join Date
    May 2011
    Location
    Albury
    Posts
    3,019

    Default

    Quote Originally Posted by Wimmera Jack View Post
    sit on the purlin.
    No wonder the poor guy is confused, correct terminology is important. That's not a purlin, it's a batten. I would be very surprised if that roof even has purlins.

    When Russ asks how long the 'flat section' needs to be does he mean of the verandah roof or the proposed flashing, and if the flashing is he asking about the projection onto the verandah roof or the projection up under the main roof? If you really want to help him a picture is worth a thousand words. So much knowledge here so poorly delivered to the unfortunate OP.

  12. #41
    Join Date
    Jun 2010
    Location
    Wimmera
    Posts
    174

    Default

    Sorry about that. Seems I know nothing, even though I lived amongst the industry.
    Call them what you like, but I have nothing further to say.

    Hooroo

  13. #42
    Join Date
    May 2012
    Location
    Woodstock (Cowra)
    Age
    74
    Posts
    3,372

    Default

    See attached, this is the correct method
    Shed Leak.pdf
    The person who never made a mistake never made anything

    Cheers
    Ray

  14. #43
    Join Date
    Jul 2008
    Location
    geelong
    Posts
    359

    Default

    silicon ANYWHERE where water MIGHT come in -going for a second layer -foil etc wont! be effective -have to stop the primary leak. Keep your outer shell secure and all else will be good. Again anything that MIGHT leak -seal the crap out of it. -if that is not the one it wont hurt -if it is -problem solved.

  15. #44
    Join Date
    May 2011
    Location
    Albury
    Posts
    3,019

    Default

    Quote Originally Posted by wood spirit View Post
    silicon ANYWHERE where water MIGHT come in -going for a second layer -foil etc wont! be effective -have to stop the primary leak. Keep your outer shell secure and all else will be good. Again anything that MIGHT leak -seal the crap out of it. -if that is not the one it wont hurt -if it is -problem solved.
    Is that meant to be serious advice, or are you just stirring?

  16. #45
    Join Date
    Oct 2015
    Location
    Ringwood, VIC
    Posts
    575

    Default

    A brief update...
    I made an 'upside down turn up tool', and turned the ends of the sheets a bit more than they were.
    Seems to have done the trick, at least so far, and we have had some significant rainfall.
    A couple more sheets to do.

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Plugging leaks (or how to stop blood going everywhere)
    By LanceC in forum WOODWORK - GENERAL
    Replies: 40
    Last Post: 11th March 2020, 10:21 PM
  2. new air hose leaks
    By ldwebster in forum WOODWORK - GENERAL
    Replies: 6
    Last Post: 13th January 2009, 06:28 PM
  3. Fixing leaks in caravan roof
    By applepie007 in forum MOTOR HOMES, CARAVANS & CAMPING
    Replies: 2
    Last Post: 14th November 2008, 07:12 AM
  4. Checking hull for leaks
    By csp in forum BOAT BUILDING / REPAIRING
    Replies: 5
    Last Post: 10th November 2005, 11:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •