    Bob. I have attempted to attach 2 photos regarding power to a 3 phase motor. the motor is on an old metal lathe and we wish to convert to 240v.
    I have listened to your most informative video on VFD Mens Shed (3 times at least) and have obviously heard what you said but probably not all you meant.
    From the pic displaying the name plate it refers to STAR but the box is not ticked.
    The pic of wire connections, to my mind, could indicate motor is wired in DELTA format, and not suitable for easy conversion using VFD 240v single phase to 3 phase.
    If, when I hit “submit’ and the pics really do show up, could you please comment on whether this motor maybe able to be converted from its present 3 phase to single phase.

    yours respectfully
    Dick
    Attached Images Attached Images

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,785

    Default

    With old motors one can never be sure what they are.

    The wiring does look like a Delta connection but given it is a biggish lathe it could also be a "415V Delta" which is different from a "240V Delta".

    If it is a "415V Delta" and you connect that to a 240V SP-3P VFD, it should still run BUT will generate less than half the power.
    This will mean if you try and load the motor up by trying to take deep cuts with the lathe it will damage the motor and possibly the VFD although they usually take care of themselves.

    This is what I would do.
    Get a sparky to connect up a 240V Sp-3P VFD. Remember this should be a 5HP rated VFD
    Careful start taking ever deeper cuts with the lathe, if it stalls, or trips the VFD then it is most likely a 415V Delta wired motor
    There is naught you can do about this except replace the motor.
    If it is a 415V Delta motor and you convert this motor to Star it will produce even less power.

    If you do not intend to ever use the lathe to take deep cuts you can derate the motor by current limiting the VFD. This decision and the current limit used is best done by a sparky for your given situation.

    My preference would be to replace the motor with a new or decent second hand one.

    Remember with a VFD you have to strip out all switches including reverse between the VFD and the motor and connect the VFD directly to the motor. Figure to do this might damage the motor and VFD. A big lathe like this probably has a coolant/lube pump. f it is a 3P pump there will be issues connecting it to the same VFD - but lets leave that for another time.

  4. #3
    Join Date
    Aug 2005
    Location
    Colignan
    Posts
    11

    Default

    Thank you
    Dick

Similar Threads

  1. Thanks BobL
    By MWF FEED in forum METALWORK FORUM
    Replies: 0
    Last Post: 1st December 2019, 07:30 PM
  2. YOUR ATTENTION PLEASE, your attention.
    By Simplicity in forum FORUM GET TOGETHERS' (FGT)
    Replies: 152
    Last Post: 17th May 2019, 09:47 AM
  3. pay attention!
    By choppit in forum G'day mate - THE WELCOME WAGON -Introduce yourself
    Replies: 6
    Last Post: 12th September 2013, 12:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •