28th February 2014, 05:51 PM #1
Electromagnetic switch
I have a H&F bandsaw. model number BS300
The switch that is on the machine was underwater during the floods and has never been that great since, as it hums when power is applied to the saw regardless of whether the saw is actually turned on or not.
I decided to get another switch for the saw and I ordered one on ebay from China. The switch on the saw is a KEDU KJD12 switch
I ordered a similarly spec'd switch, a JUCHE JCZ3B that is only 1/4 the price.
I got the switch, but it doesn't seem to behave properly. The KJD12 has a label on the side saying to use inputs 1 and 3 for the 230V input and then output goes through 2 and 4. The pins are clearly labeled 1, 2, 3 and 4 on the rear of the switch. It only has 4 pins.
The JCZ3B says to use pins 1 and 3 for the inputs and pins 2 and 4 for the outputs. There is a diagram on the side of the switch explaining this.
This is where the problem starts. The rear of the switch has 5 pins. they are labelled 13, 14, 23, 24 and A1 respectively. I connected the inputs to pins 13 and 23 and connected the outputs to 14 and 24 leaving A1 unconnected.
The saw starts but fails to hold the switch in the on position, so unless I physically hold the switch on, the saw stops. Not an acceptable state of affairs.
Can anybody tell me what I am doing wrong? Is it that I should not have got a momentary switch? Should I have got one of these instead?switch back.jpgSwitch sides.jpg
Thanks
ADDED BY ADMIN
DISCLAIMER
No liability is accepted by UBeaut or the Wood Working Forum's administrators
or moderators for advice offered by members posting replies
or asking questions regarding electrical work.
We strongly advise contacting a Licensed Tradeperson for all electrical work.
WARNING
Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
Members following such information do so at their own riskBob Willson
The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.
-
28th February 2014 05:51 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Age
- 2010
- Posts
- Many
-
28th February 2014, 07:06 PM #2SENIOR MEMBER
- Join Date
- Jun 2010
- Location
- Canberra
- Posts
- 769
You need to connect A1 to 24 so that the coil is energised and holds the switch on.
-
28th February 2014, 08:21 PM #3
Wonderful
Thanks for that RustyArc. I would never have managed to guess that by myself.Bob Willson
The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.
-
1st March 2014, 03:56 PM #4
The switch is all set up as per the instructions, but it still hums as loudly if not louder than the old one. Can anybody point me in the right direction for looking at causes of switch hum please?
ThanksBob Willson
The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.
-
1st March 2014, 04:12 PM #5GOLD MEMBER
- Join Date
- Jul 2006
- Location
- Port Huon
- Posts
- 2,685
The only thing that can hum in a switch of that design is the relay coil.
Hum could be from overvoltage - unlikely as the coil should be designed for use at the rated voltage. Wrong frequency could do it but again, if it's meant to be rated for 50Hz, unlikely.
A faulty switch would be my guess.
I have some similar NVR switches and there's no audible hum from them.Geoff
The view from home
-
1st March 2014, 05:15 PM #6
Dirt between the magnetic faces of the coil cores will do it or if they are not seating properly. A broken shading ring will cause a terrific chatter but is not likely.
RegardsHugh
Enough is enough, more than enough is too much.
-
1st March 2014, 06:55 PM #7
Thanks Hugh and Geoff.
As I said, the previous switch also hummed so I think that the fault is more likely to be external to the switch.
The hum didn't start until I shorted the A1 pin to pin 24, but without that connection the switch doesn't work properly.
Is it possible that a faulty capacitor could cause it to happen, because these are the same caps that went under water?Bob Willson
The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.
-
1st March 2014, 08:54 PM #8SENIOR MEMBER
- Join Date
- Jun 2010
- Location
- Canberra
- Posts
- 769
Without A1 connected, do you still get the hum if you hold the switch on manually?
-
1st March 2014, 10:29 PM #9.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,795
Have you had this or any other machine that have been underwater megger tested?
If not I would not use the machine without getting it checked out.
The hum could easily be due to a light coating of gunk inside the motor.
Pity you are not closer or I could have come around with my new IRT.
FWIW I have fitted the same switch to a metal cutting bandsaw and also to a small WW bandsaw without a problem.
-
2nd March 2014, 12:15 AM #10Bob Willson
The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.
-
2nd March 2014, 12:39 AM #11.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,795
-
2nd March 2014, 10:31 AM #12Bob Willson
The term 'grammar nazi' was invented to make people, who don't know their grammar, feel OK about being uneducated.
-
2nd March 2014, 11:20 AM #13SENIOR MEMBER
- Join Date
- Jun 2010
- Location
- Canberra
- Posts
- 769
The symbol represents the solenoid coil. If you look at the old switch, it has a very similar diagram, although in that case the coil symbol is more explicit.
The new switch has the coil on a separate pin (A1) so that it can be wired into equipment that has specific switching behaviour (machine stays on provided part x reaches a certain RPM or safety switch y is closed etc.).
-
2nd March 2014, 12:02 PM #14.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,795
That's the solenoid.
These switches are best connected with 6.3mm spade connectors. The small (A1) is a special size but I found the 4.8 mm ones available at altronics fit it nice and snuggly.
http://www.altronics.com.au/index.as...item&id=H1991A
-
30th March 2015, 07:00 AM #15
Hi all
I have just bougth a Kedu KJD 12 and installed it on a home-made linisher. It also has quite a loud buzz when energised but otherwise works OK (switches on and off and the motor runs the right direction). I wasn't quite sure which way around to connect it but if I had done it incorrectly, it wouldn't work at all...right?
Thanks
RichardCheers from NZ
Richard
Similar Threads
-
ElectroMagnetic Chuck help needed
By PenTurner in forum ELECTRONICSReplies: 5Last Post: 5th February 2013, 06:40 PM -
ElectroMagnetic Chuck help needed
By PenTurner in forum METALWORK FORUMReplies: 4Last Post: 5th February 2013, 06:04 PM -
Electromagnetic clocks
By jpb1958 in forum CLOCKSReplies: 12Last Post: 5th May 2011, 02:33 AM -
on/off switch
By andyjackson1 in forum WOODWORK - GENERALReplies: 22Last Post: 21st August 2010, 09:52 AM -
Need switch
By nadroj in forum METALWORK FORUMReplies: 1Last Post: 4th November 2009, 09:31 AM