22nd December 2020, 08:24 PM #1
Lumpy motor when VFD running in vector mode drive.
Hi All,
I finally got a motor for my VFD drive and while it runs fine in V/F mode, when I put it into vector control it is very lumpy until I get over 50 Hz.
Motor
Weg W21, 1.5 kW.
Wired to Delta.
VFD
Powtran PI150, 2.2 kW.
The following parameters have been set:
F0.00 (Motor control more) = 0 (Vector)
b0.00 (Motor type) = 0 (General asynchronous motor)
b0.01 (Rated power) = 1.5 (kW)
b0.02 (Rated voltage) = 230 (V)
b0.03 (Rated current) = 5.7 (A)
b0.04 (Rated frequency) = 100 (Hz)
b0.05 (Rated speed) = 1455 (RPM)
b0.27 (Auto tune) = 2 (Asynchronous motor parameters comprehensive)
When auto tune runs, the motor operates smoothly without any issues.
Subsequent runs however are rather lUmPy.
Any thoughts would be appreciated.
20201222_193538.jpg 20201222_193506.jpg
-
22nd December 2020 08:24 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
22nd December 2020, 11:09 PM #2.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,790
Did you set all the motor parameters and perform a motor tune up cycle/sequence?
-
23rd December 2020, 06:01 AM #3
I probably should have been more specific.
The parameter values I listed are the motor parameters which I set, and then yes, I ran the auto tune function.
Just to confirm, to run the auto tune, I set the auto tune parameter then ran the VFD. It said “tune” in the display, buzzed for a little bit, spooled up the motor, ran for a bit then spooled down and stopped, and the display went back to the set frequency. I assume at this point the auto tune had completed.
-
23rd December 2020, 08:14 AM #4
I had an epiphany. What if the Rated Frequency parameter should be set to the motor's design frequency? So I set it to 50 Hz (instead of 100 Hz), ran the auto-tune again and all is well in Tasmania again.
I got confused between the Maximum Frequency to allow the VFD to run at and the motor's rated frequency. Seems obvious now.
-
23rd December 2020, 09:58 AM #5
I was just about to tell you to drop the rated freq to 50 Hz but I see you've sorted it out. Is this going on the lathe?
Those were the droids I was looking for.
https://autoblastgates.com.au
-
23rd December 2020, 12:56 PM #6
Yes on the lathe. I just need to get the spindle hole enlarged in the pulley.
-
23rd December 2020, 01:39 PM #7.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,790
Setting the base motor frequency too high will also produce lower motor power at lower frequencies.
In this test I did the reverse ie set the base frequency of a 50Hz rated motor to 29Hz.
This produced more power at lower frequencies compared to when the motor is set to the 50Hz base frequency.
The results are not complete at higher frequencies ie curves should all tip over at their peaks) but the trade off is loss of loss of power at higher frequencies.
HPVFWYE29HzBF.jpg
I believe this is not recommended as a long term solution so its better to adjust pulleys sizes to active the desired speed power combo - however for limited use its a lot faster to change the base frequency that to change the pulley.
Similar Threads
-
Calculating the cost of running a three phase motor?
By RSD in forum THE SHEDReplies: 8Last Post: 5th May 2020, 09:09 PM -
While we are all on VFD's...Vector drive recomendations.
By Ueee in forum METALWORK FORUMReplies: 37Last Post: 4th May 2014, 12:49 AM -
Lathe motor/drive conversion
By bin555 in forum METALWORK FORUMReplies: 34Last Post: 14th June 2012, 08:21 PM -
Motor running backwards?
By aussieglen in forum WOODWORK - GENERALReplies: 22Last Post: 28th May 2005, 07:57 PM