    Default Powtran PI150 VFD Parameters for remote

    Hi all,

    I’m setting up a remote allowing me to start and stop my motor remotely, without having to use the VFD keyboard.

    The VFD is a Powtran PI150.

    For reference the manual may be found at https://www.powtran.com/upload/20201...1754258451.pdf

    Looking at the different values I can set F1.00-F1.04 (digital inputs) to:
    - 36 (park) stops the motor as expected.
    - 1 (Forward run) is not available for selection (cycling the codes goes 0,2,3,4... any ideas?
    - 2 (Reverse run) works, but only as long as the corresponding DI is pulled low. So I can’t run the VFD running with a momentary switch.

    I see my options as follows:
    - Someone points out a command which will start the VFD with a momentary switch.
    - Use code 2 (reverse run), with a latching circuit, and wire the motor to run in reverse so that it runs in reverse, in reverse (seems daft, but will work)
    - Figure out why code 1 (forward run) is not available, rectify and use a latching circuit.

    Any thoughts or ideas would be appreciated.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Mar 2008
    Location
    Hobart, Tas
    Posts
    1,211

    Default

    Ahh, I have progressed a little.

    I think what I want is three-wire control. Now trying to figure out how it is setup on the Powtran.

    Any previous experience is welcome.

  4. #3
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    PM NCarcher (Tony), he will be able to advise you. You can use the panel remotely with a CAT cable if you wish.
    CHRIS

  5. #4
    Join Date
    Mar 2008
    Location
    Hobart, Tas
    Posts
    1,211

    Default

    Chris, not with the PI150. The control panel is not removable.

  6. #5
    Join Date
    Mar 2008
    Location
    Hobart, Tas
    Posts
    1,211

    Default

    Ok, I got it all figured out.

    Code 01 can only be set on DI1.

    F1.10 needs to be set to 2 (three wire type 1).
    F1.00 set to 1 (forward run)
    F1.01 set to 3 (three wire control)

    NO start button connected to DI1.
    NC stop button connected to DI2.

  7. #6
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,756

    Default

    Quote Originally Posted by LanceC View Post
    Ok, I got it all figured out.

    Code 01 can only be set on DI1.

    F1.10 needs to be set to 2 (three wire type 1).
    F1.00 set to 1 (forward run)
    F1.01 set to 3 (three wire control)

    NO start button connected to DI1.
    NC stop button connected to DI2.
    Same as on the PI160

  8. #7
    Join Date
    Mar 2008
    Location
    Hobart, Tas
    Posts
    1,211

    Default

    Quote Originally Posted by BobL View Post
    Same as on the PI160
    I ended up finding the info in their PI500 manual. It’s a pity they don’t add it to all their manuals, unless this is just so basic everyone is expected to already know.

    None the less, a pull down resistor and harnessing the 10 V line allowed me to convert my NO stop switch to act as NC.

Similar Threads

  1. Quick question - Remote Control for Powtran driving CVMax
    By Flindersia in forum DUST EXTRACTION
    Replies: 14
    Last Post: 22nd May 2018, 11:55 PM
  2. Replies: 3
    Last Post: 20th August 2017, 05:18 PM
  3. Huanyang vfd/inverter parameters
    By rev in forum DUST EXTRACTION
    Replies: 0
    Last Post: 31st August 2015, 04:36 PM
  4. Replies: 2
    Last Post: 27th July 2013, 08:16 AM
  5. Box design parameters ?
    By tonysa in forum BOX MAKING
    Replies: 2
    Last Post: 15th May 2006, 08:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •