    Default Can a VFD be wired with plugs?

    Hi everyone,

    Just purchased a used 3 phase Felder dust extractor (2.2 KW), which I hope to be a suitable candidate for a single-phase input VFD, allowing me to firstly operate it on single phase, but also gain some choice as to the 'power' settings of the machine depending upon the application, both for airflow and noise control. Eg - I hope to do away with my shop vac and be able to run it on a 'slow' setting when extracting from my orbital sander or biscuit cutter, then ramp it up when machining with my jointer/thicknesser etc.

    I am taking my first small steps into the world of VFDs, and want to gain a bit of background knowledge before I book in a sparky to wire things up.

    My first NOOB question is whether a VFD must be hardwired from mains then hardwired to the motor, or if it may be plugged in both the input and output leads?

    The main reason I ask is that my extractor does not have a lead, instead it has a male 3 phase plug and I expect that as Felder are known for their 'complicated' approach to things, the internal motor wiring may be a little complex, and that the plug might be the simple way to connect input 3 phase power to the motor.

    The secondary reason is I will be building an enclosure for it outside the main shed sometime down the track (ASAP hopefully), and hope to simply be able to unplug the machine from one single-phase outlet inside the shed, and plug it back in to another outlet in the 'cubby house' (I already have an outdoor plug installed out there......)

    Just for clarification, I am not hoping to utilize the 'plug in and plug out' nature of this set-up to use the same VFD for multiple machines, soley for the extractor.

    No doubt there will be more questions to come, but thought I would start with this one!

    Thanks, Steve

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    The motor and VFD should be hard wired, especially on a DC since it is under considerable load when the motor is running. Compare that to a drill press or lathe that is really only under load when drilling or turning.

    Disconnecting the motor and VFD is possible if the motor is not running (VFD can still be on), but if you forget to turn the motor off using the VFD first, you risk damaging the motor and VFD.

    My guess is you have a 3P contactor type switch on the DC. This must be removed as these usually have a current limiting device to prevent the motor burning out. If this ever activates while the motor is running (which is usually when its activated) the contactor will disconnect the DC motor from the VFD and there will be a loud BANG and smoke from the VFD.

    In practice it's just safer if all switches between the VFD and motor are removed. The VFD will automatically replace the function of the contactor's current limiting device provided the current limit parameter is set correctly in the VFD.

    If you want to retain the contactor switch the VFD must be after the contactor ie in between the contactor and motor.

    There are smart ways around all this but they require more fiddling than a 'hard wire".

    Use of a VFD for multiple machines is high impractical - sounds like you need to read the first post in the electronics forum (VFDs for Newbies)

  4. #3
    Join Date
    Nov 2006
    Location
    NSW
    Posts
    90

    Default

    Thanks for a very detailed reply, they all sound like good reasons to not do it!

  5. #4
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,774

    Default

    The 240V input to the VFD can certainly be wired with a plug but as Bob says you would need to remove or bypass whatever 3 phase controls are between the 3 phase plug and the motor.
    Definately doable but might take a bit of mucking around depending on whats there now. You would also need to check that the motor is VFD compatible without modification as you will be running it at a different voltage. Some photos of whats there will help.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  6. #5
    Join Date
    Nov 2006
    Location
    NSW
    Posts
    90

    Default

    Not sure if this helps, just a screenshot from the advert I bought it from

    Thanks everyone!

    dusty1.jpg

  7. #6
    Join Date
    Nov 2006
    Location
    NSW
    Posts
    90

  8. #7
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    That DC name plate says it requires a neutral which VFDs normally got use.
    Does that mean it has some kind of 240V SP shaker or filter cleaner built into the DC ?
    In that case that would need to be wired separately - ie outside of the VFD.

    However, are you sure it's 2.2kW, that nameplate says 7.5kW although the current rating says 5.5A which suggests a 2.2kW.
    7.5kW is equivalent to 10HP which is well above the limit of 240V SP VFDs which is about half that

  9. #8
    Join Date
    Apr 2014
    Location
    Little River
    Age
    78
    Posts
    1,205

    Default

    That label may refer to the switch that it is on. K&B make motor switchgear.

  10. #9
    Join Date
    Nov 2006
    Location
    NSW
    Posts
    90

    Default

    Hi BobL, I am very confident it is 2.2KW, here are the specs of the current machine, I doubt much has changed on mine.

    New 2016 felder AF22 2 Bag Dust Collectors in EMU PLAINS, NSW

    Thanks!

  11. #10
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    4,774

    Default

    Uberlastschutz is overload protection so it looks like it has a thermal O/L and either a load break switch or a switch and contactor but there doesn't seem to be enough room for a contactor. If there is thats why it needs the neutral. You would need to ditch all that stuff and connect the VFD to the motor but only if it can be wired in Delta or you use a 415V output VFD.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  12. #11
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,792

    Default

    Quote Originally Posted by NCArcher View Post
    . . . . . . but only if it can be wired in Delta or you use a 415V output VFD.
    To be a little more specific . . . .
    A 240V output VFD will only work if the motor is already wired as a Star and can be rewired as a Delta.
    If it's already a delta then a 415V output VFD will be required.

  13. #12
    Join Date
    Nov 2006
    Location
    NSW
    Posts
    90

    Default

    Thanks for all of your very detailed advise, was wondering if I opened up the switching/junction box and took a photo of the wiring, could that help identify a star/delta wiring? Not chasing anything definitive, but would be a helpful starting point along my VFD journey!

    Thanks again, Steve

  14. #13
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Steve, the motor data plate should have that information on it, take a photo and post it here.
    CHRIS

  15. #14
    Join Date
    Nov 2006
    Location
    NSW
    Posts
    90

    Default

    263214114_319864439959232_5550567053661672302_n.jpg

    - - - Updated - - -

    Hi found this sticker next to the motor mount, hope it might mean more to you guys than it does me!

    Ta, Steve

  16. #15
    Join Date
    Jun 2005
    Location
    Helensburgh
    Posts
    7,696

    Default

    Steve, I am not an electrician but it looks like that motor can be run off 240V three phase or 415V three phase and the choice is yours. Give me a call if you want, I have to go to Robertson MS on Saturday and we might be able to arrange something.
    CHRIS

Page 1 of 2 12 LastLast

Similar Threads

  1. Timber plugs in mortar before the days of star plugs.
    By KevinB in forum WOODWORK - GENERAL
    Replies: 5
    Last Post: 5th August 2015, 12:49 AM
  2. Kyoto lamp wired up and going
    By chuck1 in forum WOODTURNING - GENERAL
    Replies: 3
    Last Post: 1st August 2015, 09:59 PM
  3. Smart wired man cave
    By DaveTTC in forum THE SHED
    Replies: 14
    Last Post: 11th July 2015, 08:33 AM
  4. TRansformer wired incorrectly?
    By .RC. in forum METALWORK FORUM
    Replies: 4
    Last Post: 24th January 2011, 05:50 PM
  5. allowance for a wired edge?
    By techgirl in forum METALWORK FORUM
    Replies: 39
    Last Post: 10th August 2010, 06:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •