    Quote Originally Posted by droog View Post
    As RCD’s detect difference in the current flow between active and neutral on a circuit then to trip the RCD any differential must be on that particular circuit.
    The link provided is for an RCD protecting multiple circuits, this must not be confused with RCBO’s protecting individual circuits with separate neutral returns.
    A RCD can have a number of breakers (circuits) with a common natural busbar, if the consumer board has 2 RCD's then each RCD will need it's own common busbar, you can not share one busbar between 2 RCB's because it won't be balanced.

    So power comes in from the street passes through the RCD and out to whatever is switched on demanding power and then returns back to the street through the RCD via the neutral, however this isn't really correct because we are dealing with AC current which will flow from the street along the live and then reverse and flow from the street along the neutral.

    The job of the RCB is to make sure anything connected to it's Live & Neutral poles are balanced to within 30ma, this does not mean just one individual circuit but everything connected to both the Live & Neutral common busbars, because they are in turn connected to the RCD.

    Now with me coming from the UK we have 32 AMP ring mains, rather than a 20 AMP radials for socket outlets and on refurbishment jobs there was always additional spur outlets to be fitted and the consumer board could have 6 or more breakers under the control of one RCD which were not really labeled clearly for me to know which breaker to isolate, so I would use a jump wire to short Earth & Neutral on the socket that I was going to run the spur from, then go back the the consumer board to see which breaker had tripped, it was always the individual breaker that tripped rather than the RCD taking out say 6 circuits, therefore the breakers themselves will detect Earth & Neutral touching before the RCD trips.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #17
    Join Date
    Mar 2008
    Location
    Cairns
    Posts
    192

    Default

    out of curiosity i just took the cover off a sub board that i had done 18 months ago at my place and found neutral bar not used, only earth. and the neutrals goto the rcd's
    Attached Images Attached Images

  4. #18
    Join Date
    Nov 2021
    Location
    Sunshine Coast, QLD
    Posts
    780

    Default

    Quote Originally Posted by wozzzzza View Post
    out of curiosity i just took the cover off a sub board that i had done 18 months ago at my place and found neutral bar not used, only earth. and the neutrals goto the rcd's
    There is a Neutral busbar at the top right but it's not being used because you have individual RCBO fitted.

    There aren't many videos showing Australian boards, here's one with 2 RCD's with 3 breakers on one of them used for Lights the other RCD having 2 breakers used for Power, under that cover should be 2 Neutral busbars being used.

    https://www.youtube.com/watch?v=ieIVhHgsF1A

  5. #19
    Join Date
    Sep 2005
    Location
    Bendigo
    Age
    60
    Posts
    242

    Default

    Quote Originally Posted by Camelot View Post
    it was always the individual breaker that tripped rather than the RCD taking out say 6 circuits, therefore the breakers themselves will detect Earth & Neutral touching before the RCD trips.
    Without any experience in UK electrics it sounds like there are some basic but significant differences.
    Australian circuit breakers will not detect or trip with Earth / Neutral interconnects as there is no connection to the breakers in any form.
    Note: RCBO’s are totally different and not the same as circuit breakers.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Replies: 0
    Last Post: 5th January 2023, 03:20 AM
  2. Replies: 1
    Last Post: 19th August 2012, 05:49 PM
  3. How long can (should) you leave a fingerboard taped up for?
    By pjpalfi in forum MUSICAL INSTRUMENTS
    Replies: 5
    Last Post: 19th July 2010, 10:30 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •