Thanks Thanks:  0
Needs Pictures Needs Pictures:  0
Picture(s) thanks Picture(s) thanks:  0
Page 1 of 2 12 LastLast
Results 1 to 15 of 19
  1. #1
    Join Date
    Oct 2009
    Location
    Springfield NSW
    Age
    70
    Posts
    1,007

    Default Electricity supply question - 3 phase vs 1 phase

    Firstly , just let me saythat I have absolutely no intention of doing anything here myself ,I just want some clarification from an expert or two.

    I have recently moved into a new (actually quite old) house and was about to find an electrician to install a 15 amp circuit in my shed.I got talking to the bloke across the road and he told me that I would have no problem as I have 3 phase connection. On investigation I found that I have 3 wires coming in from the pole across the road and those 3 wires are indeed connected to3 wires on the power pole. In the meter box there is 1 single phase meter plus an off peak meter.

    I thought a single phase connection had 2 wires (phase and neutral) and a 3 phase connection had 4 wires.

    So, can any one tell me what might be going on. Do I have 3 phase connection, if so why a single phase meter? If it is single pase , what is the third wire for and where might ir go?
    ____________________________________________________________
    there are only 10 types of people in the world. Those that understand binary arithmetic and those that don't.

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by Avery View Post
    I thought a single phase connection had 2 wires (phase and neutral) and a 3 phase connection had 4 wires.
    Although most 3 phase wiring uses a neutral it is not always needed for three phase operation.
    Remember all voltages have to be relative to a reference.
    With single phase, a neutral is needed as a reference for the single phase.
    With three phases (ABC) the voltages are relative to each other AB, BC and AC

    It sounds like you have 3 phase to the meter but they decided to just wire up one phase.
    If there were no 3 phase devices used in a house and the meter needed upgrading the to save a few$ sometimes they just wire up the whole house on one of the 3 phases.

  4. #3
    Join Date
    Oct 2009
    Location
    Springfield NSW
    Age
    70
    Posts
    1,007

    Default

    Quote Originally Posted by BobL View Post
    Although some 3 phase wiring does use a neutral it is not needed for three phase operation.
    Remember all voltages have to be relative to a reference.
    With single phase, a neutral is needed as a reference for the single phase.
    With three phases (ABC) the voltages are relative to each other AB, BC and AC

    It sounds like you have 3 phase to the meter but they decided to just wire up one phase.
    If there were no 3 phase devices used in a house and the meter needed upgrading the to save a few$ sometimes they just wire up the whole house on one of the 3 phases.

    Thanks you for your quick reply.

    So if the whole house is connected to one phase and the other two are simply left dangling, does that mean that all the neutrals are just tied to ground at the meter box? To connect 3 phases I would need to upgrade the meter?
    ____________________________________________________________
    there are only 10 types of people in the world. Those that understand binary arithmetic and those that don't.

  5. #4
    Join Date
    Jun 2006
    Location
    East Warburton, Vic
    Age
    54
    Posts
    14,189

    Default

    Quote Originally Posted by Avery View Post
    So if the whole house is connected to one phase and the other two are simply left dangling, does that mean that all the neutrals are just tied to ground at the meter box? To connect 3 phases I would need to upgrade the meter?
    Seeing that you're getting a 15amp p/point installed, raise the question with him, when you call, a sparky is really the only person who'll be able to answer the question, as he will be able to see what has been done.
    Cheers

    DJ


    ADMIN

  6. #5
    Join Date
    Jul 2006
    Location
    Port Huon
    Posts
    2,685

    Default

    FWIW I have 3 phase into the shed and it's definitely 4 wires. 3 wires have fuses on the entry and one doesn't (neutral)

    Lights and power run from a single phase and there's a single 4 wire 3phase socket. 4 wire means 3 phases and earth, no neutral.
    Attached Images Attached Images

  7. #6
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by Avery View Post
    Thanks you for your quick reply.

    So if the whole house is connected to one phase and the other two are simply left dangling, does that mean that all the neutrals are just tied to ground at the meter box? To connect 3 phases I would need to upgrade the meter?
    Essentially yes, have a read of this. Ground and neutral - Wikipedia, the free encyclopedia

    It is very important not to let DIYers think that they can do this themselves - wiring up neutrals and earthing can be a tricky business that can kill and best left to qualified people.

  8. #7
    Join Date
    Oct 2009
    Location
    Springfield NSW
    Age
    70
    Posts
    1,007

    Default

    Quote Originally Posted by DJ's Timber View Post
    Seeing that you're getting a 15amp p/point installed, raise the question with him, when you call, a sparky is really the only person who'll be able to answer the question, as he will be able to see what has been done.


    That is probably what will happen. If three phase is available I will want to use it. I have a couple of 3phase machines that I was goiing to run off single phase with electronic controllers.
    I reallyjust like to know what is going on before i call the professionals in - just so I know what questions to ask.
    ____________________________________________________________
    there are only 10 types of people in the world. Those that understand binary arithmetic and those that don't.

  9. #8
    Join Date
    Oct 2009
    Location
    Springfield NSW
    Age
    70
    Posts
    1,007

    Default

    Quote Originally Posted by snowyskiesau View Post
    FWIW I have 3 phase into the shed and it's definitely 4 wires. 3 wires have fuses on the entry and one doesn't (neutral)

    Lights and power run from a single phase and there's a single 4 wire 3phase socket. 4 wire means 3 phases and earth, no neutral.


    Looks just like mine except I don't have the 4th wire.
    ____________________________________________________________
    there are only 10 types of people in the world. Those that understand binary arithmetic and those that don't.

  10. #9
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    53
    Posts
    1,938

    Default

    I have 3 wires coming onto my property and it's what it known as split phase - 2 x 240 (180 deg out of phase) and neutral. The phase to phase voltage is 480V, and not 415V like proper 3 phase.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  11. #10
    Join Date
    Jul 2008
    Location
    Bungendore
    Posts
    33

    Default

    It was quite common back I the 60's and 70's in NSW to bring 2 phases into houses. 1 phase was used general supply to the house and the second phase was a dedicated off peak supply for hot water. The three wires are probably 2 active and 1 neutral. If you can post a picture of the switchboard it should be fairly easy to tell.

    Andyd

  12. #11
    Join Date
    Feb 2006
    Location
    Perth
    Posts
    27,793

    Default

    Quote Originally Posted by andyd View Post
    It was quite common back I the 60's and 70's in NSW to bring 2 phases into houses. 1 phase was used general supply to the house and the second phase was a dedicated off peak supply for hot water. The three wires are probably 2 active and 1 neutral. If you can post a picture of the switchboard it should be fairly easy to tell.

    Andyd
    I see a number of domestic electric ovens are designed to run with two phases.

  13. #12
    Join Date
    Jan 2009
    Location
    Adelaide
    Posts
    289

    Default

    Quote Originally Posted by andyd View Post
    It was quite common back I the 60's and 70's in NSW to bring 2 phases into houses. 1 phase was used general supply to the house and the second phase was a dedicated off peak supply for hot water. The three wires are probably 2 active and 1 neutral. If you can post a picture of the switchboard it should be fairly easy to tell.

    Andyd
    What Andy and BobL said. Vernon, I think is in the country on a SWER or similar.

    In SA in the 60s it was commonish to run the house on single phase and oven across two phases. Effectively a 240V house and a "single phase" 415V oven.
    With three wires and an old house I would bet that this is what you have. A clue, but not definite, to look for is are they two covered wires and one bare (two phases and neutral respectively) however, they could be all covered or all bare.

    After the original stove or HWS died and was replaced with a new single phase one the other active would have been left unconnected to anything (except maybe the meter, the meter would be a two phase one and you should be able to tell if it wasn't changed subsequently).

    Also the 3 wires you can see (and the rating of the service fuse) would be quite small compared to a modern service, probably only good for 50A or so (maybe need to get them checked)
    .

    Regards
    SWK

  14. #13
    Join Date
    Aug 2003
    Location
    Conder, ACT
    Age
    77
    Posts
    6,051

    Default

    DISCLAIMER

    No liability is accepted by UBeaut or the Wood Working Forum's administrators
    or moderators for advice offered by members posting replies
    or asking questions regarding electrical work.
    We strongly advise contacting a Licensed Tradeperson for all electrical work.
    WARNING

    Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
    Members following such information do so at their own risk

  15. #14
    Join Date
    Apr 2005
    Location
    Japan。
    Age
    49
    Posts
    1,622

    Default

    You have a single phase connection, the additional live wire is old-school off peak supply, and will only be functional when 'off peak' is on. The newer systems use a single live wire and send a signal pulse down the line so the meter knows that it's billing 'off peak'. Those old 'off peak' supplies are somewhat dangerous, as they check out as dead, but can become live at any time. Stupid sparkys get zapped off them all the time.

    Your sparky will have no trouble running a 15A line to wherever you want it to be. You don't 'need' to be able to supply the full supply current to every single point, so adding in a circuit shouldn't be a problem at all. You might get some trouble if your supply coming in isn't really enough to run everything you might want to run all at the same time though, so be aware of that.

    But, get a sparky on site to sort it out.


    Stu.

    (Licensed Electrical Mechanic.)
    The Tools from Japan Blog (about Japanese tools and such)
    &
    The Tools from Japan Store.

  16. #15
    Join Date
    Jan 2009
    Location
    Adelaide
    Posts
    289

    Default

    Stu.
    Avery said the three wires to his house came from across the road. So unless there was an common LV mains switchwire for off peak (like an old street light system) or the time clock was out in the street, I don't think it is an off peak arrangement. Something like that could have been used in NSW (I don't know) but arrangements like those were never used in SA.

    I still think the circumstances indicates a two phase and neutral system of some sort. If so, the wires will be small (7/18g is what was used in SA, that's equivalent to 8mm2 in metric, about 1/2 the size of a normal service these days)

    Avery,
    since the house is old and things like the stove have been changed/upgraded and other circuits added over time, get your electrician to do a "maximum demand calculation" (use those words) before he adds anything to the house. I can't see it to know for sure but I am suspicious that the old service is too small for modern day use.
    It used to be in SA that a service upgrade would be provided by the distribution company at no (or minimal) cost if the load on the house had increased to justify it. You may find that if the single (or two) phase service has to be upgraded there might be a discounted price to go one more step and get a three phase one if you really wanted one (it used to be like that in SA). Of course there would need to be some mods done on your switchboard and a new 3 phase run out to the shed, which will add to the cost if you do go to 3 phase. But if you haven't bought your inverters already you can weigh the cost differences of the two options.

    As the moderators noted and Stu pointed out, get someone to look at it. _If_ it is a two phase system there is a chance of giving yourself a 415V shock, obviously even more dangerous than the usual 240V of a normal house. _If_ it has a timed system as Stu believes parts of it could liven up unexpectedly when you thought you were safe. Neither Stu nor I nor anyone else on this board can tell for sure what you have without looking at it. All comments given are intended so you can deal more intelligently with an appropriately qualified person, which I understood is your intention from your original post.

    Regards
    SWK
    (SA "A" Class)

Page 1 of 2 12 LastLast

Similar Threads

  1. Power supply for 3-phase DE when using VFD
    By markkr in forum DUST EXTRACTION
    Replies: 27
    Last Post: 14th September 2013, 10:01 PM
  2. Three Phase Equipment on a Single Phase Supply
    By Chris Parks in forum GENERAL & SMALL MACHINERY
    Replies: 19
    Last Post: 16th April 2011, 05:49 PM
  3. Hercus 3 phase lathe, single phase supply
    By Pete F in forum THE HERCUS AREA
    Replies: 51
    Last Post: 16th January 2009, 10:15 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •