    Default power requirements for 2hp motor

    Hi All,

    I'm looking at a 2hp single phase lathe and the dealers says must run on a 15A circuit with a lead no longer than 1m.

    2hp is ~1500 watts, does a 2hp motor really draw more than 2400 watts on startup?

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Age
    2010
    Posts
    Many





     
  3. #2
    Join Date
    Feb 2008
    Location
    Northern Sydney
    Age
    49
    Posts
    2,764

    Default

    Sounds odd. I have plenty of devices that draw more than 1500w which don't need 15A.

    Unless that particular motor draws a lot more on startup, 1500w/240v is only 6-odd Amps.

    Cheers,
    Dave
    ...but together with the coffee civility flowed back into him
    Patrick O'Brian, Treason's Harbour

  4. #3
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    4,304

    Default

    Single phase motors draw up to something like 6 times the rated amps on startup...However it does not need a 15 amp circuit...

    How many single phase compressors do you see with 15 amp plugs and most compressors today are 2 to 3 hp..

  5. #4
    Join Date
    Sep 2009
    Location
    Sydney
    Age
    45
    Posts
    18

    Default

    cheers, thats what I thought. I can understand keeping the cord short to minimize resistance. An 1800w electric chainsaw doesn't require 15A!

  6. #5
    Join Date
    Dec 2008
    Location
    Eastern Australia
    Posts
    604

    Default

    Depends on the cable you use. If you think on it, does it make sense to only have one meter of 20A cable to the socket, then have a run of 20m from the socket to the fuse box.

  7. #6
    Join Date
    Aug 2008
    Location
    Bendigo
    Age
    51
    Posts
    663

    Default

    Single phase motors draw up to something like 6 times the rated amps on startup
    Yep I go along with that for a Direct On Line single phase motor. Thats the teachings of the sparky instructors at TAFE.

    Cant say I have used a metal lathe before. Personally I think u would be okay, however running a 2 hp motor on 15 amp instead of 10 will greatly reduce the incidences of nuisense tripping. Naturally running it as per the directions is advised.

    My 2 new Hp dusty runs a 15 amp plug and lets face it it only drives a fan.

    If u can start it with minimal load on the motor naturally that will help with the above.
    www.lockwoodcanvas.com.au

    I will never be the person who has everything, not when someone keeps inventing so much cool new stuff to buy.

    From an early age my father taught me to wear welding gloves . "Its not to protect your hands son, its to put out the fire when u set yourself alight".

  8. #7
    Join Date
    Sep 2006
    Location
    Mallacoota,VIC,Australia
    Age
    53
    Posts
    656

    Default

    HI,
    I have a 3 H.P. Ingersoll Rand Air Compressor (Bought 1995). The Plate on the Motor says it Draws 13.5 Amps. Their is a 16 Amp Fuse in the Power Board. I have never had a Fuse blow. I Personally can't see a 2 H.P. Electric Motor needing a 15 Amp Circuit.
    I just had a thought though. Does this Lathe have a Coolant Pump and a Work light. If it does, then it probably does need the 15 Amps.
    All The Best steran50 Stewart

  9. #8
    Join Date
    Aug 2008
    Location
    Adelaide
    Age
    69
    Posts
    834

    Default

    It seems a tad strange to me. If you think about it, you are talking about a 1500 watt device. Most 9" angle grinders are 2200 or 2400 watts and they all run on a 10 A circuit quite happily. Granted the grinders are intermittent duty whereas the lathe will run for longer periods but I can't see 1500 watts on a 10A breaker being an issue.

    If you do have a problem with the breaker tripping on startup you could have it replaced with a motor rated breaker which allows a greater degree of inrush current for a short period on startup.

  10. #9
    Join Date
    Jun 2006
    Location
    East Warburton, Vic
    Age
    54
    Posts
    14,258

    Default

    Quote Originally Posted by benskyring View Post
    Hi All,

    I'm looking at a 2hp single phase lathe and the dealers says must run on a 15A circuit with a lead no longer than 1m.

    2hp is ~1500 watts, does a 2hp motor really draw more than 2400 watts on startup?
    It does sound a bit unusual but have you asked them why?

    Does the manual state this as well?

    And most importantly, will they honour any warranty claims if you were to run it on a 10A circuit?
    Cheers

    DJ


    ADMIN

  11. #10
    Join Date
    Aug 2008
    Location
    near Rockhampton
    Posts
    4,304

    Default

    My Hare and Forbes AL1000C lathe with 2hp motor came standard with a 10 amp plug..

  12. #11
    Join Date
    Aug 2008
    Location
    Oatley NSW
    Age
    69
    Posts
    244

    Default

    Hi benskyring,
    I have attached an article on Horse Power Ratings, its an American article but you can see what the author is getting at. The motor being used on the Lathe may have a low efficancy hence them recomending a 15Amp Circuit. If you are running a separate Circuit Breaker for your Lathe use a "D" Curve type Breaker as they are rated for Motor Starting applications.

    Regards,
    Keith.

  13. #12
    Join Date
    Sep 2009
    Location
    Sydney
    Age
    45
    Posts
    18

    Default

    Quote Originally Posted by Keith_W View Post
    Hi benskyring,
    I have attached an article on Horse Power Ratings, its an American article but you can see what the author is getting at. The motor being used on the Lathe may have a low efficancy hence them recomending a 15Amp Circuit. If you are running a separate Circuit Breaker for your Lathe use a "D" Curve type Breaker as they are rated for Motor Starting applications.

    Regards,
    Keith.

    That's a very informative article. I'll see if I can find any info on the motor efficiency. The lathe I'm looking at is the Lux 1440G.

  14. #13
    Dave J Guest

    Default

    I would ask the dealer to look at the HM52 mill, it comes with a 2.4 mtr lead and 10 amp plug for
    2 x 2hp motors
    a transformer for the power feed and light
    and a coolant pump.
    Dave

  15. #14
    Join Date
    Nov 2009
    Location
    Australia
    Posts
    12

    Default

    hey benskyring,

    i'd say the dealer has a mate who is an electrician that installs 15A circuits for a 'good price'

    you're right though, a 1500w motor shouldn't require a 15A circuit at all. Generally circuit breakers and fuses are designed to handle short term high current loads. Different rating circuit breakers are designed for different start currents, but you shouldn't need to go into that much detail.

    Also keep in mind that though the power outlet may be rated at 10A, the circuit breaker for power circuits is generally a 16A model and the cable (if it is 2C+E PVC Flat which is the standard these days) is good for around 20A depending on cable length and whether it passes through insulation material or under the ground.

    You won't have any problems with a 10A outlet unless the motor is faulty in which case it should be returned under warranty

    Jay

  16. #15
    Join Date
    Sep 2006
    Location
    Mallacoota,VIC,Australia
    Age
    53
    Posts
    656

    Default 2H.P. Lathe Motor

    HI benskyring,
    It doesn't look like anyone has picked up what I meant by My Quote. So I thought I better explain it better. I am not trying to be better than Your other Repliers, it is just a sound theory.

    Quote I just had a thought though. Does this Lathe have a Coolant Pump and a Work light. If it does, then it probably does need the 15 Amps.
    All The Best steran50 Stewart End QUOTE

    What I meant was that if the Lathe in Question has a Coolant pump and a Work Light. If they are Wired on the same Circuit ie do not use seperate Power Plugs than the Lathe Motor. Meaning one Power Plug for the whole Unit. Then the Lathe would need the 15 Amp Circuit, otherwise it would not cope on 10 amps if everything (lathe, coolant, worklight) was going at once.
    Out of interest what is make of the Lathe. Did You actually see 15 Amps marked on the Power Plug or just take the Dealers word for it?.
    All The Best steran50 Stewart

Page 1 of 2 12 LastLast

Similar Threads

  1. Power requirements for Excalibur 21" Scroll Saw
    By Dave Lister in forum SCROLLERS FORUM
    Replies: 7
    Last Post: 19th July 2009, 07:19 PM
  2. requirements for a 15a circuit
    By 19brendan81 in forum WELDING
    Replies: 63
    Last Post: 6th June 2009, 11:36 PM
  3. Broadband Requirements !
    By 351shaker in forum COMPUTERS
    Replies: 3
    Last Post: 14th September 2007, 09:16 PM
  4. New drill press motor power - does anyone have a view please?
    By MurrayD99 in forum GENERAL & SMALL MACHINERY
    Replies: 4
    Last Post: 1st December 2005, 08:00 AM
  5. Induction motor vs brush type motor
    By Don Nethercott in forum HAND TOOLS - POWERED
    Replies: 8
    Last Post: 27th May 2005, 02:14 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •