    Default dual voltage AC motors query

    These modern 3 phase dual voltage motors 240 / 415 are apparently made this way because different countries use different voltage standards , the manufacturers do it in order to save costs

    Question: are the stator windings (1.) tapped for the dual voltage , eg a twin set of terminals , or, (2.) is it just a case of connecting the windings in either delta ( 240 ) or star (415) .

    If my second theory is correct , So in Delta mode, the windings exhibit half the impedance of star mode..is that correct .

    MIKE

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #2
    Join Date
    Nov 2007
    Location
    melbourne australia
    Posts
    2,636

    Default

    Hi Mike, in star mode you have 2 sets of windings in series for each phase, so they can cope with the higher voltage. In delta there is one winding per phase. I'm not sure about your theory because in delta you also have the other two windings in series across the winding in question. Hard to explain. Image one winding in parallel with 2 windings in series. The impedance calculation gets a bit more complicated. Maybe one of the gurus will be along shortly to clarify.

  4. #3
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Hi Mike,

    No, they don't do it to lower costs... the cost is no different, it's just a different way of making the connections to the motor windings.

    Whether you wire it in 415v star or 240 delta the voltage across the stator windings is the same.

    For a 415v star connected motor the voltage across the stator windings to neutral (the star point) is 240v..

    The impedance of the windings is the same.

    Regards
    Ray

  5. #4
    Join Date
    Jul 2008
    Location
    near Warragul, Victoria
    Posts
    2,500

    Default Good

    Quote Originally Posted by RayG View Post
    Hi Mike,

    No, they don't do it to lower costs... the cost is no different, it's just a different way of making the connections to the motor windings.

    Whether you wire it in 415v star or 240 delta the voltage across the stator windings is the same.

    For a 415v star connected motor the voltage across the stator windings to neutral (the star point) is 240v..

    The impedance of the windings is the same.

    Regards
    Ray
    Ok got it ..... thanks

Similar Threads

  1. 220/380 Voltage
    By lockwood116 in forum WOODWORK - GENERAL
    Replies: 13
    Last Post: 16th December 2006, 11:59 PM
  2. Looking for low voltage DC motors
    By Oldblock in forum NOTHING AT ALL TO DO WITH WOODWORK
    Replies: 11
    Last Post: 30th November 2003, 06:48 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •