  1. #61
    Join Date
    Oct 2007
    Location
    Sydney
    Posts
    2,340

    Default

    Stuart, I would suggest checking with the manufacture and not relying on on that information. I say that as I have never heard a manufacturer suggest switching a motor in or out of a inverter is a good idea. If you want to simply search for more information yourself via Google, the driving on numerous motors is called "group drive" in this field. Having said that, it would probably allow the second motor to come in/out just fine, since the relative size of the motors is very different (another thing a manufacturer will suggest is a no-no btw). The problem is the drive will work just fine, and then just suddenly fail. The reason is because a motor switching on/off generates large surges. Most people have seen large motors on poor quality electrical circuits dim lights and so on when the motors switch on. It's because for a split second that motor effectively is a "short-circuit" in appearance. Similarly that "stored" electricity is put back into the circuit when the motor is shut down and can sometimes be seen as arcing in the switching circuit. That's the best layman's description I can manage I'm afraid. The motors being talked about here are much smaller, but of course it's all relative.

    Bob, all switching is typically done by the VFD and it's really not a good idea to have any switches anywhere. Turning any electrical device on is, other than possibly heat, the worst thing you can do to any electronic device. Leaving the VFD on and switching the output is also a bad idea and I've never heard a manufacturer ever suggest this. The VFD should detect there is no motor there and be quite happy if, for example you just wanted to test it, but then when you drop a motor on it, it will simply crap itself. Maybe an analogy is a bit like imagine lifting a 50 kg barbell at a gym, most here could do that I'd guess. But then just imagine you're standing there minding your own business and then suddenly you turn around to find somebody has thrown a 50 kg barbell at you. My bet is you're going to drop it!

    If there's any doubt, email the actual manufacturer or local representative with precisely what you want to do ie I have an xx drive, a yy motor and want to also switch a zz motor in and out with the drive running, and see what they say. Generally the support is very good as it's an industrial device and many engineers count on good backup. Hope that helps.

    Pete

  2. # ADS
    Google Adsense Advertisement
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many





     
  3. #62
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Hi Bob,

    I think Pete has covered it pretty well already, just one point to clarify when you say...

    Is it detrimental to these devices to have them powered up but NOT driving a motor?
    By that I assume you mean powered up and connected to the motor, with start/stop control via the VFD control terminals. (in this case a foot switch) No problem.

    You can switch the output of a VFD, while it is powered up, but only if it's not running. Is that what you meant?

    Similarly that "stored" electricity is put back into the circuit when the motor is shut down and can sometimes be seen as arcing in the switching circuit. That's the best layman's description I can manage I'm afraid. The motors being talked about here are much smaller, but of course it's all relative.
    Expanding a little on Pete's description, when you break the circuit, the flux in the motor field coils doesn't drop immediately, it takes time, during that time, while the motor is spinning down it acts a generator until the flux through the field coils decays. It can be a problem with fans and pumps that can auto-rotate as well.

    In motors of the size we are talking here, it's unlikely to be a problem, just another reason not to switch the output of a VFD while it's running.

    Regards
    Ray

  4. #63
    Join Date
    Nov 2008
    Location
    Perth WA
    Age
    71
    Posts
    5,650

    Default

    Thank you for that Pete.

    All the operational switching of my VFD is done via the remote switching function ( F10 - 1). No switching occurs on any motor wiring. The motor is wired directly to the VFD.

    The Schaublin's main switch controls the mains power to the VFD via the contactor.

    BT

  5. #64
    Join Date
    Nov 2008
    Location
    Perth WA
    Age
    71
    Posts
    5,650

    Default

    "You can switch the output of a VFD, while it is powered up, but only if it's not running. Is that what you meant?"

    Ray,

    In some ways, no. What I had been initially thinking was, could I run both motors via a single VFD. The motors would be switched separately. What you are saying is that it can be done if you switch the VFD output from one non running motor to the other enabling only the running of a singular motor.

    I could never have both motors running simultaneously. Using individual VFD's will overcome that restriction.

    BT

  6. #65
    Join Date
    Oct 2007
    Location
    Sydney
    Posts
    2,340

    Default

    As long as the drive is not running the motor at the time you can do all the switching you like, no problem. Just be aware however that if you have vastly different motors the VFD isn't going to like it. In this thread we've seen the last few pages of trying to get the VFD to drive just one motor correctly, now imagine how difficult it is to say to the drive "nah mate, forget all the parameters I just told you about THAT motor, I just flicked a switch and now I want you to drive THIS motor"

  7. #66
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    In fairness to the VSD, its been used on 8 motors and it ran fine out of the box, unless you count one error running at 5Hz. Other than that its when I have been playing around with the settings that the problems started. On that subject, I've been increasing F_13 today, it sounds fine up to F_13=5, at F_13=6 I think I can hear a difference in the way it starts, it does sound different at F_13=7, it sounds nasty at F_13=8.
    Stuart

  8. #67
    Join Date
    Oct 2007
    Location
    Sydney
    Posts
    2,340

    Default

    Yes but in Bob's case he's been talking about a 2 HP motor and a 0.4 HP motor if I recall correctly. A BIG difference in frame size!

    Pete

  9. #68
    Join Date
    Jun 2008
    Location
    Victoria, Australia
    Age
    74
    Posts
    6,132

    Default

    Hi Stuart,

    I've been digging further into what F5 and F13 parameters do and how they interact.

    First, to clarify what the difference between the 50Hz settings and 60Hz settings are, the difference is that the voltage boost is calculated at 2.5Hz on the 50Hz case, and 3.0Hz in the 60Hz case. (Don't know why they just didn't say 5% of rated motor frequency?) I can't tell the difference between F5=1 and F5=4

    Anyway, back to F13, the F13 is the percentage added to the V/F curve. So selecting F5=1

    Hz Voltage%

    1.0 8% + F13
    2.5 10% + F13

    So when you pick F5=1 and F13=5 you get (10+5)=15% output at 2.5Hz, which is not quite the same as selecting F5=2, because at 1.0Hz you will have 8+5=13%, wheras F5=2 would be 10.5%

    The conclusion, is the same, I think you just have to tune the combination of F5 and F13 to give the required startup. In the case of a mill or lathe, we never start under load anyway, so the tuning isn't all that critical. F5=1 and F13=0 works just fine on the HM52.

    Still, I think it's a good argument for a vector control drive if you need the torque at low revs.

    Regards
    Ray

  10. #69
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Ray,
    Always takes me awhile to get my head around those graphs each time I look at them. Would it be fair to say that if I am mostly above 25Hz F_13 isn't going to make much differeance?
    So If I understand what you said earlier. If there was more load on the motor at start up do you think it wouldnt error with F_13=10

    F_05=1 + F_13=0 in the morning.
    Thanks
    Stuart

  11. #70
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    Noticed another strange thing with my VSD today. I was boring on the mill in lower gear at 220rpm with an irrupted cut which was giving me a lot of gear noise. So I figured I would take it out of low and run it at 660rpm and 15Hz on the VSD. Started it up and took a cut, it worked just find, then while it was sitting there spinning it shut down with a OL1 error. I tried setting F_13=5 but it ran for a minute or so and then shut down. So it was back to lower gear and 220rpm 50Hz. I *guess* increasing F_18 like the manual says would fix this.
    Stuart

  12. #71
    Dave J Guest

    Default

    Just a tip if you haven't already finished.
    It would be quicker to mill out the majority with an end mill then use the boring bar.

    Dave

  13. #72
    Join Date
    Jul 2010
    Location
    Melbourne
    Posts
    7,775

    Default

    I have. It would have but I hadn't really dicided how deep I was going until I got there. lol
    Stuart

Page 5 of 5 FirstFirst 12345

Similar Threads

  1. Fitting VFD to Craftsman Lathe
    By Col2310 in forum THE HERCUS AREA
    Replies: 31
    Last Post: 12th May 2011, 08:28 PM
  2. what do you reakon a big old craftsman lathe be worth ?
    By JDarvall in forum WOODTURNING - GENERAL
    Replies: 15
    Last Post: 25th May 2009, 09:36 AM
  3. Bent spindle on craftsman lathe, its a discountinued part
    By dirk1609 in forum WOODTURNING - GENERAL
    Replies: 14
    Last Post: 19th May 2009, 02:01 PM
  4. Need Belt for my Old Craftsman Metal Lathe
    By MrChips in forum WOODWORK - GENERAL
    Replies: 0
    Last Post: 15th February 2007, 12:16 PM