Is a motor start relay switch needed for a 3ph 2.8kw pump motor?
It's been a while for me working on 3ph motors! I forgot most of what I learnt!
I have a 3ph 2.8 kW water pump with a start/stop relay that's on it's way out. The relay welded itself closed well before I got to this farm (4 years) which proved to be an advantage for me. I don't have to walk down to the pump to start it. I just flick the breaker at the board.
From memory and it's been a while, 3 phase motors under 5hp don't actually need a start/stop relay unless it's for (machinery) safety in a big plant. Is that correct or am I off by a mile?
This is just a small water pump on the river.
I was planning on just bypassing the start relay straight to the 3 phase switch.
I thought I should consult the brains trust first! You fellas always seem to talk some sense into me before I do something silly!
The relays are cheap but I like the convenience of starting/stopping the pump up at the workshop instead of trudging down the the river to get it going. I can't be bothered setting up a remote control but will if it's needed.
Any thoughts?
-
12th August 2015 12:30 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Posts
- Many
-
12th August 2015, 12:40 PM #2GOLD MEMBER
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 7,775
I don't kow sorry. But why not have the relay in the shed? or is that not allowed?
Stuart
-
12th August 2015, 12:45 PM #3SENIOR MEMBER
- Join Date
- Jan 2004
- Location
- Bellingen
- Posts
- 587
Good question Stu! Not sure on the rules on that one. The problem is reversed if I'm working on the pump ( not often, after floods or when their is air in the line) .. I have to start it at the workshop and walk 5mins to the pump., stop it there, adjust and walk back up to start it again.... I like the idea though... Will have a think about that one!
ADDED BY ADMIN
DISCLAIMER
No liability is accepted by UBeaut or the Wood Working Forum's administrators
or moderators for advice offered by members posting replies
or asking questions regarding electrical work.
We strongly advise contacting a Licensed Tradeperson for all electrical work.WARNING
Information supplied within posts is not to be considered as detailed formal instructions to complete a task.
Members following such information do so at their own risk
-
12th August 2015, 12:57 PM #4GOLD MEMBER
- Join Date
- Jul 2006
- Location
- Adelaide
- Posts
- 2,680
it pays to switch all 3ph motors via contactor...switch's being mechanical operation can work fast or slow depending on how quick one wants to be...the slower the more risk of damage to switch thru arcing of contacts...where as a contactor is always fast..well at least it should be else its stuffed
fit new stop start contactor at switchboard and replace old contactor at pump with isolating switch if none there.
-
12th August 2015, 01:08 PM #5.
- Join Date
- Feb 2006
- Location
- Perth
- Posts
- 27,807
By relay do you mean a just a simple "no-volt switch " or a full on "3P starter with excess current protection"?
If the latter, one setup I've seen on a situation like this is a bypass switch on the starter at the convenient operating location and another switch at the motor.
Once everything is honky dory the bypass is switched off and motor switch left on.
Excess current protection is pretty handy for things that get turned on-off often and operate unattended.
-
12th August 2015, 01:52 PM #6Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 4,304
It is only drawing 2.2 amps per phase (no doubt less when running), although no doubt more on startup..
Depending on how many times you will be flicking the switch, I would just install a 20 amp or 32 amp 3 phase switch/socket on the wall and use that...Light red, the colour of choice for the discerning man.
-
12th August 2015, 01:59 PM #7
Eskimo, is on the money. ( as always )
You can have the Start/Stop wherever you like, at the switch board if that's what you want. Then install an isolating switch at the pump end, so you can isolate it without having to walk all the way back to the other end.
Depending on the cost of a replacement pump and motor, you can get very basic pump protection, with a current monitoring relay that will detect loss of prime, by detecting that the current is too low, or a motor overload with current too high and shut down.
-
12th August 2015, 02:27 PM #8GOLD MEMBER
- Join Date
- Jul 2010
- Location
- Melbourne
- Posts
- 7,775
-
12th August 2015, 06:38 PM #9SENIOR MEMBER
- Join Date
- Jan 2004
- Location
- Bellingen
- Posts
- 587
I knew the brains trust would guide me on a better path!
I will look into it a bit more. If the relay fails between now and then, I will just bypass it.
It only gets turned on less than 20 times a year and runs for about 12 hrs each time.
Loss of prime can ruin a pump pretty fast...will look into it some more!
Thanks fellas!
-
12th August 2015, 07:53 PM #10
A 3 phase starter has Thermal Overload Protection. The TOL drops the contactor out if the motor draws too much current. If the contactor is welded closed then the TOL protection will not work.
Install a new 3 phase starter near the switchboard and as has been suggested an isolating switch at the pump. Just plugging it in to an outlet or using only a switch means that if the pump gets something caught in the impeller or a bearing heads south then the motor will continue to draw excess current until it burns out.Those were the droids I was looking for.
https://autoblastgates.com.au
-
12th August 2015, 08:13 PM #11GOLD MEMBER
- Join Date
- Jul 2006
- Location
- Adelaide
- Posts
- 2,680
that is supposedly the way they are made but for some reason you can manipulate it to switch a lot slower
My experience has been that if you dont tell an apprentice to manually operate the switch without hesitation he will get arcing....stuffing something up...definitely more noticeable on larger motors...even i have done it...not stuff anything up but the audible noise from the isolator is unmistakable
-
12th August 2015, 08:28 PM #12Philomath in training
- Join Date
- Oct 2011
- Location
- Adelaide
- Age
- 59
- Posts
- 3,149
Yes, but the other advantage of contacts is that they can be set up to have a no volt release as well as delayed or remote starting and even via PLC - so that you can run a low (or lower) voltage cable to control something and several hundred amps of start up current are not running through the switch in your hand (we have a motor at work with a steady state draw of around 230A - start up is around 850A).
I was 'mildly surprised' to discover when I first saw it that the control circuit for my lathe contactors runs at 415V...
As Ian says, isolator by the pump and remote start at the switchboard.
Michael
-
13th August 2015, 08:53 AM #13GOLD MEMBER
- Join Date
- Jul 2006
- Location
- Adelaide
- Posts
- 2,680
-
13th August 2015, 09:03 AM #14SENIOR MEMBER
- Join Date
- Jan 2004
- Location
- Bellingen
- Posts
- 587
Brains trust has done it again!
The pump is $1400 and not worth skimping on..
Will put a relay switch with a thermal overload at the board. Isolator is already next to the pump but might swap it over....it's a tired looking switch.
I was wanting to experement with a psi gauge plumbed in to the water lines to see if I can monotor the tank volume when the pump is off. I might be able to see if the pump needs priming and when it's pumping well... I could not find any info on the net about this yet. Must be looking in the wrong places.
Stu, you were on the money from the first post!
-
13th August 2015, 09:14 AM #15GOLD MEMBER
- Join Date
- Jul 2006
- Location
- Adelaide
- Posts
- 2,680
Similar Threads
-
Where to get a 240V motor switch with paddle?
By Dengue in forum GENERAL & SMALL MACHINERYReplies: 10Last Post: 16th April 2015, 12:34 AM -
Start motor reco
By Stustoys in forum METALWORK FORUMReplies: 36Last Post: 5th March 2015, 07:25 PM -
Washing Machine Motor and Pump
By ss_11000 in forum WOODWORK - GENERALReplies: 21Last Post: 21st October 2007, 10:23 PM -
Wiring up Start Switch to motor, 8" JET Jointer
By Friday in forum JOINTERS, MOULDERS, THICKNESSERS, ETCReplies: 2Last Post: 20th September 2007, 08:22 PM