28th July 2012, 05:45 PM #1
Any sparkys here? Electrical oddity...
Not sure if this is a fault that needs to be investigated or just the way electricity "is".
My shed is on a sub circuit on it's own, about 35m from the main house switchboard. The Neutral-Earth link is just below the main switchboard and appears to have a good bond to the copper earth stake.
At the switchboard there is no potential between the earth and neutral bus that I can measure.
At the shed end, there is less than about 0.1V (smallest unit I can measure - the multimeter flickers between 0.0 and 0.1V). Incidentally, I have touched neutal and earth connections with my fingers and can't feel anything either.
I have identical potential of 238V between active and neutral, and active and earth - just as you would expect.
However, when I connect neutral and earth directly (with a wire or screw driver) the RCD trips!
That tells me that there is a current of 30mA (or whatever trips the RCD) able to flow...... Where the devil does that come from?????
We are on a 11kV SWER line - and I wonder if it's just an induced low voltage in the underground cable between the house and the shed?
According to the wiring rules, I should NOT make a second link between Neutral and Earth anywhere else on the property.
I wonder if I could put a small value resistor between them UPSTREAM of the RCD?
Advice is appreciated. If there is no obvious explanation, of course I will call a sparky to come and double check everything! So don't worry about my safety. I just don't want to call someone out here (in the bush) only to learn something obvious....
Cheers,
Joe
-
28th July 2012 05:45 PM # ADSGoogle Adsense Advertisement
- Join Date
- Always
- Location
- Advertising world
- Age
- 2010
- Posts
- Many
-
28th July 2012, 05:58 PM #2GOLD MEMBER
- Join Date
- Nov 2007
- Location
- melbourne australia
- Posts
- 2,673
Joe,
this is the best place for electrical questions:
ELECTRICAL
Some of the blokes are very helpful. Of course, there's the usual "don't risk it, call a sparky" brigade, but I've usually been able to get the info I need.
Chris
-
28th July 2012, 06:58 PM #3Philomath in training
- Join Date
- Oct 2011
- Location
- Adelaide
- Age
- 59
- Posts
- 3,149
RCDs work on balance - through electrical coils they 'compare' the current flowing in the active and the current flowing in the neutral and if they don't match, trip.
It sounds like (I'm not a sparky) that when you short to earth, a current is able to flow. The RCD is doing what it should. The real question is whether the rest of your electrical is behaving...
Michael
-
28th July 2012, 07:12 PM #4
Hi,
It is nothing to worry about. The RCD works on the current in the A and N being = to within the rating (30ma in your case) ie what comes in in one leg must go out the other. If either goes to earth it will trip. it takes very little diference in potential to get a flow of 30ma and that will come from the difference in resistance and or impedance of the earth conductor / path to that of the neutral conductor in a N to E short.
If this does not make sense it doesn't matter the first sentence is the important one "It is nothing to worry about."
RegardsHugh
Enough is enough, more than enough is too much.
-
28th July 2012, 07:44 PM #5
Thanks all. That's exactly what I understood and believed to be the case.
Hugh, the earth conductor in the main cable is 2.5mm sq and the N&A are 6 or 10 (can't remember). Would that account for the difference? Other than that, the length and path to my shed are identical.
Is there any relevance in my SWER connection to this issue?
Michael, yes, everything is working correctly and safely.
Cheers,
Joe
-
29th July 2012, 12:54 AM #6
Hi,
No the SWER is on the high tension side of your transformer and should have no effect on the secondary circuit. The different size of the conductor and if there is other load on the way to where the short happens will help account for the slight current flow.
RegardsHugh
Enough is enough, more than enough is too much.
-
29th July 2012, 07:37 AM #7Senior Member
- Join Date
- Oct 2011
- Location
- Brisbane
- Posts
- 104
I think the SWER can produce this effect. Since the ground is the return conductor for the SWER transformer, there could be a potential difference between the transformer and the shed sizeable enough to activate the RCD when the connection is made.
Anyway, why are you doing this?
-
29th July 2012, 02:21 PM #8
Tool4me,
I'm not doing anything. I happened to accidentally touched the netral with my screw driver (in a switched off circuit) while tighterning the earth terminal when I swapped a single GPO for a double and heard the RDC trip.
I'm only looking for an explanation.
JoeLast edited by jhovel; 29th July 2012 at 04:43 PM. Reason: added that I touched it with a screw driver, not my fingers
-
29th July 2012, 02:48 PM #9GOLD MEMBER
- Join Date
- Aug 2007
- Location
- Brisbane
- Posts
- 1,156
Um. You were fooling around with a GPO with power applied to it? Braver man than me, that's for sure.
The other day I described to my daughter how to find something in the garage by saying "It's right near my big saw". A few minutes later she came back to ask: "Do you mean the black one, the green one, or the blue one?".
-
29th July 2012, 04:09 PM #10GOLD MEMBER
- Join Date
- Sep 2010
- Location
- Lebrina
- Posts
- 1,099
-
29th July 2012, 04:41 PM #11
Thanks Karl - no, Peter, I'm not at all brave - nor foolish , you jumped to a conclusion without reading my post.....
Joe
-
29th July 2012, 04:59 PM #12
Anyway, I think I might have got an understandable answer from the Resto forum sparkies: the fact that thewe are on a SWER line means that there is a ground path back to the transformer neutral. Since the shed is about the same distance or closer to the transformer than the main earth stake - and the shed is well grounded in this wet weather, it is possible that a small current form any user can go back via the gound, thereby making the currents in active and neutral wires unbalanced - tripping the RCD.
Makes sense to me....
The other suggestion was that the earth cable to the shed is a lot smaller that the active and neutral. That would change the impedance over that distance and could also imbalance the current sufficently.
In any case, nothing trips form any equipment and when it does, there is a good reason (I've had a build up of dust in the bandsaw motor a couple of times tripping it). So all is goos and my curiosity is satisfied.
Cheers,
Joe
PS: don't have any concerns for my electrical safety anyone - I know enough to be scared of messing with electricity, and enough to know what I can and can't do safely.
Sadly, Ihave also experienced what sort of unsafe and dumb things electricians can do if not supervised - like leaving a job at my house with the roof 'live'! I recognnised the fault myself, foudn the cause, got him to ccome back and didn't pay the bill.....
Since then, I made it my business to know the rules and understand domestic wiring properly, so I can supervise. Sparkies hate that - but I can sleep at night.
-
29th July 2012, 08:37 PM #13
I had a qualified electrician install my new switchboard and RCD switch. He is the electician at work. He deals with single and 3 phase circuits every day at work. After 2 hours of messing around he claimed that maybe my RCD switch was faulty. Then he read the instructions that came with it! Problem solved!
Dean
-
29th July 2012, 08:43 PM #14Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 4,304
Sometimes familiarity breeds contempt...
Light red, the colour of choice for the discerning man.
-
29th July 2012, 09:16 PM #15GOLD MEMBER
- Join Date
- Aug 2007
- Location
- Brisbane
- Posts
- 1,156
Woops, you are correct. I didn't properly read the thread. I can only plead bad cold which is stuffing up the thinking process. Sorry.